You are on page 1of 18

APCPCWM_4828539:WP_0000045WP_000004

APCPCWM_4828539:WP_0000045WP_0000045

April 1 2009

Safety Concept of DSME LNG FPSO: A shipbuilders perspective

Sung Hoon Sean Kim, Ph. D. Daewoo Shipbuilding & Marine Engineering

Future Products & Business Development Institute

2009. 4.1

APCPCWM_4828539:WP_0000045WP_000004

APCPCWM_4828539:WP_0000045WP_0000045

Recent/On-going projects

Future Products & Business Development Institute

2009. 4.1

TOC DSME HSE Engineering Risk on Offshore LNG Plants


Comparison with those on Oil FPSOs

DSME LNG FPSO


Features Layout Process Safety Devices

Future Products & Business Development Institute

2009. 4.1

APCPCWM_4828539:WP_0000045WP_000004

APCPCWM_4828539:WP_0000045WP_0000045

HSE Engineering in DSME


Drilling rig & drillships FPSOs FSRU & LNG RV Cruiseship Reliability

Future Products & Business Development Institute

2009. 4.1

LNG RV
Reviewed by LRNA & ABS
FERA
Regas facilities besides trunk deck of No. 1 tank Jet fire
Fire rated walls to protect tanks

SUS Plating & Deluge at the pump bottom

CFD Explosion analysis


Leak in the STL Effect of Relief panel Ventilation condition

FRA, reproduced by DSME using Neptune


Future Products & Business Development Institute

2009. 4.1

APCPCWM_4828539:WP_0000045WP_000004

APCPCWM_4828539:WP_0000045WP_0000045

LNG FSRU
A research project FRA using Neptune Emergency relief design
Vent Flare

Toxic gas dispersion


Collision Risk Assessment

Future Products & Business Development Institute

2009. 4.1

Risk on Offshore LNG Plant, Myths & Facts


Myth
Explosion comparable to hydrogen bomb
Collision or vulnerability to terrorist attack?

Fact
Embrittlement of steel structure exposed to cryogenic spill Dangerous process

Spill on water
Rapid phase transition (RPT) blast? Vapor cloud traveling toward a center of population?

High pressure, flammable and/or cryogenic fluid Flammable refrigerant maybe Safety by distance shall be compromised

Total collapse of containment tank?


A pool fire within the full tank impounding area? Tank top fire?
Future Products & Business Development Institute

2009. 4.1

APCPCWM_4828539:WP_0000045WP_000004

APCPCWM_4828539:WP_0000045WP_0000045

Inherent Safety LR Guidance


Adequate separation / segregation of hydrocarbon inventories Reducing the level of confinement in a hazardous area Minimising the size of hydrocarbon inventories available for escalation Suitable location or protection of essential systems and equipment Use of passive systems, i.e. fire and/or blast walls and PFP, including protection against spills Use of active protection systems, i.e. fire fighting, ESD, PSD.

Future Products & Business Development Institute

2009. 4.1

Approach to Assess the Risk


Independent studies
Leak frequency Dispersion
Flammable gas evaporated from LNG release
Offsite hazard impact irrelevant on an offshore plant

LQ impairment due to exhaust or flammable gas, smoke, etc

Fire
Jet/Pool fire & the frequency of escalation Passive fire specification

CFD Explosion
Congested semi-closed modules Ductility level blast specification

Drop object Collision


Side-by-side offloading and/or tandem offloading

QRA

Not only related with the process failure but with non-hydrocarbon accidents
10 2009. 4.1

Future Products & Business Development Institute

APCPCWM_4828539:WP_0000045WP_000004

APCPCWM_4828539:WP_0000045WP_0000045

Oil FPSOs by DSME

AGBAMI

Pazflor
Future Products & Business Development Institute

11

2009. 4.1

Comparison of Risks on Oil FPSO & FLNG(1/2)


Oil FPSO Composition - Hydrocarbons mainly heavier than C3, C8, C10 and a little C1 - Larger heat radiation - High pressure gas at compressor module - Large liquid inventory along the process - Spill containment over the deck -Heavy hydrocarbons with smoke - Little evaporation when released - Process gas heavier than air - Smoke from the pool fire shall be considered FLNG - Mainly C1

Jet fire

- High pressure gas inventory would have more risk of jet fire - Liquid inventory rather limited - Liquid spill to be driven overboard - To be evaporated with energy from ambient air -Dense vapor just release from LNG process would slump over the deck - Less confined and congested topside to have better ventilation - Little smoke - Readily dispersed and having less reactivity

Pool fire

Dispersion

VCE

- Large explosion reactivity


12

Future Products & Business Development Institute

2009. 4.1

APCPCWM_4828539:WP_0000045WP_000004

APCPCWM_4828539:WP_0000045WP_0000045

Comparison of Risks on Oil FPSO & FLNG(2/2)


Cryogenic hazard - Welded stainless piping & equipment with the minimum number of flange connections - Deluge to prevent brittle fracture - Vapor cloud control - Hot wet flaring - Cold dry flaring - Cold vent Side-by-side & tandem offloading -Mainly risers through internal turret containing mainly gas - Enclosed space to be mechanically ventilated Ex. 1, Large scale FLNG, 460x75 lifting 50,000 ton topside ~ 1.45 ton/m2 Ex. 2, DSME LNG FPSO(Mid size), 330x65 lifting 20,000 ~ 0.93 ton/m2
2009. 4.1

Flare & vent - Hot wet flaring - Cold dry flaring - Cold vent Offloading Well fluid reception Tandem offloading - Two phase feed liquid - Mainly exposed riser inlets at one side of the vessel containing mainly liquid Ex. Agbami, 320x59 lifting 35,000 ton topside ~ 1.85 ton/m2

Plant congestion

Future Products & Business Development Institute

13

DSME LNG FPSO

330m x 65m, topside weight about 20,000 ton Production 2 MTA through 2 trains Process deck 6m above the hull deck Living Quarter located upwind Flare tower slanted Gas turbines located above the process deck Extended anchoring platform
Future Products & Business Development Institute

14

2009. 4.1

APCPCWM_4828539:WP_0000045WP_000004

APCPCWM_4828539:WP_0000045WP_0000045

DSME LNG FPSO


Barge type hull Two rows of storage tanks -Little risk from sloshing -Strong support for topside structures Storage of 200K LNG/20K LPG Condensate to be consumed as fuel Internal turret system with weathervaning capability 2x5MW Azimuth thrusters

Future Products & Business Development Institute

15

2009. 4.1

DSMEs Two-Row Tank/Design Evolution


Low sloshing load
Small tank width leads to less internal flow Avoid resonance with ship motion No concerns on CCS against sloshing load

Strong support for offshore topside module


Strong longi. bulkhead supports heavy topside Free from additional support for topside Small deck deflection

138K LNGC

2-row FLNG

Experimental setup
Impact Pressure Time History
1 Row Tank 2 Row Tank

Economical solution
Cost-effective and optimum solution comparing other Independent CCS

Model test

Pressure

1-row
P ressu re

2-row

1080

1082

1084

1086

1088

1090 Time [sec]

1092

1094

1096

1098

1100

Centerline bhd. for 2-Row arrangement

Future Products & Business Development Institute

16

2009. 4.1

APCPCWM_4828539:WP_0000045WP_000004

APCPCWM_4828539:WP_0000045WP_0000045

DSME LNG FPSO


Conceptual development
A competitive medium-scale model for offshore non-associated gas well (less acid & lean)
Liquefaction process
SMR technology of B&V, a renowned liquefaction technology Client-preferring technology applicable Gas turbine driven compressors to require smaller electric load

DSME design to Float, Storage, & Offloading


A barge with internal turret system and facilities for side-by-side offloading Gas treatment & utility modules design Cargo handling system Two-row arrangement of GTT NO. 96 CCS

Safety consideration
Conceptual layout review in the current stage
Major FLNG safety issues being considered

Detailed safety study planned


Future Products & Business Development Institute

17

2009. 4.1

Layout Living quarter


Separated from the process area Protected by the Fire/Blast wall
No jet fire grade Ductility level blast design

To protect the lifeboat station STL Compartment to be separated from the LQ via the lay-down area
Blast attenuation Safety against the jet fire & dispersion

Grated process deck to be extended to the LQ for easy material handling & working path
18 2009. 4.1

Future Products & Business Development Institute

APCPCWM_4828539:WP_0000045WP_000004

APCPCWM_4828539:WP_0000045WP_0000045

Layout Internal turret


Harsh sea condition to prefer the internal turret system
HP feed gas to be contained only within the turret

Location
To be located as close to the bow
For good weathervaning capability

Not to be close to LQ
Blast relief Flammable gas Machinery space in the hull to separate

Structural integrity
Longitudinal deformation Swivel movement Blast loading Mechanical ventilation No passive fire fighting on equipment & structure inside the structure

Future Products & Business Development Institute

19

2009. 4.1

Layout Gap for enhanced ventilation


Process deck
Plated within process modules
To prevent the release from the topside to slump down to the hull deck

6m above the hull deck Grated between modules to release flammable gas and explosion

Small safety gaps between modules to enhance ventilation


Effect be analysed through CFD analysis

Future Products & Business Development Institute

20

2009. 4.1

10

APCPCWM_4828539:WP_0000045WP_000004

APCPCWM_4828539:WP_0000045WP_0000045

Fire risk
Jet fire
Safety gap to prevent an escalation from the jet fire
7 or 10 minutes of direct exposure

Pool fire
For in-site layout, BS EN 1473
15 kW/m2 on the unprotected metal outer surface of an adjacent LNG tank Design spill

Dimensioning jet fire shall be identified of the frequency of 1.0E4/yr. Deluge, ineffective to mitigate the jet fire Heat up analysis
Lowesmith (2007) Gas jet fire 0.1
Length Total heat flux 5 180 0.25 0.08

For an FLNG,
Cargo tank protected within the hull Design spill from equipment would be limited

1.0
15 250 0.4 0.095

10
40 300 0.55 0.095

>30
65 350 0.7 0.095 21 2009. 4.1

f hc

Future Products & Business Development Institute

Layout Escape route


The primary on the hull deck
An alternative & material handling way on the process deck

The secondary crossway between modules Full redundancy allowing impairment of one route
Port & Starboard The secondary muster area (SMA) aft

Protection of SMA against fire, explosion and heat from the flare

Future Products & Business Development Institute

22

2009. 4.1

11

APCPCWM_4828539:WP_0000045WP_000004

APCPCWM_4828539:WP_0000045WP_0000045

Layout Clearance btn the hull & the process decks Spaces for CCS maintenance
Maintenance through liquid & gas dome Retractable main cargo pumps Favorable ventilation condition on the hull deck

Release at the hull deck


Hull deck piping of an LNG FPSO will be coarser than that of an Oil FPSO. Welded & insulated piping design of an LNG FPSO will be less susceptible to leakage.

Future Products & Business Development Institute

23

2009. 4.1

Layout Topside Pipe Rack


Running above the main material handling way
Safe from material handling over the process deck The material handling way as a ventilation alley & an alternative escape route Ladders between longitudinal modules

Future Products & Business Development Institute

24

2009. 4.1

12

APCPCWM_4828539:WP_0000045WP_000004

APCPCWM_4828539:WP_0000045WP_0000045

Explosion Risk
Release Dispersion Ignition Explosion
Release frequency & inventory to depend on detail design Dispersion depend on
Ventilation condition : Layout, confinement, congestion, buoyancy,

Ignition source shall be rated Explosion strength


Light hydrocarbon would have small explosion efficiency Controlled by layout

Design Overpressure once in 10,000 years Materials


NG Cold natural gas Propane Refrigerant
25 2009. 4.1

Future Products & Business Development Institute

Layout Mixed Refrigerant & Storage


Mixed refrigerant
Another source of flammable gas leak
C1, C2, C3, C5 & N2

Separate storage for C2, C3, & C5


Normally No Flow from the refrigerant storage to suction drum Located at a well ventilated area Away from LQ & SMA Considering re-arrange vessels longitudinally

Hazard to be considered
Heat from the flare Drop accident from crane operation

Future Products & Business Development Institute

26

2009. 4.1

13

APCPCWM_4828539:WP_0000045WP_000004

APCPCWM_4828539:WP_0000045WP_0000045

Layout Offloading platform


Side-by-side offloading of LNG only! Protection
SUS plated under the grated manifold deck Water deluges QCDC & ESD

Consequence of release
RPT on contact with the water within the gap would exert no risk Explosion on the FLNG with little impact on the LNGC
Future Products & Business Development Institute

27

2009. 4.1

Layout Flare tower


Tower slanted aft
With no condensate to be offloaded, no risk on tandem-offloading vessels

Flaring scenario (draft)


No flaring in normal condition
Normal BOG will be consumed as fuel for G/T

Operation/Emergency flaring
Start-up Process shutdown

Separate vents for topside & cargo


Topside equipment maintenance Tank purging Tank pressure relief

Tip design & tower height will be determined Heat shield on SMA Heat on the MR storage tank
28 2009. 4.1

Future Products & Business Development Institute

14

APCPCWM_4828539:WP_0000045WP_000004

APCPCWM_4828539:WP_0000045WP_0000045

Typical Liquefaction Process


Cryogenic Refrigeration System
CO2, Sulfur Refrigerant

Flash Gas

BOG/FG Compression

Fuel

Acid Gas Removal

Dehydration

Liquefaction

End Flash

Feed Stock

Inlet Separation

C5+

Fractionation

C1+C2

LNG Product

Produced Water Treatment

H20 C5+

C3+C4

BOG

LPG Storage Tank


H20

LNG Storage Tank

Condensate Storage Tank

Future Products & Business Development Institute

29

2009. 4.1

SMR Black &Veatch, PRICO

Benefits of SMR
Competitive efficiency Small equipment count Compact heat exchanger adopting aluminum plate fin

FLNG, August, 2007

A small number of drivers Limited inventory of refrigerant Simple operation


30

Future Products & Business Development Institute

2009. 4.1

15

APCPCWM_4828539:WP_0000045WP_000004

APCPCWM_4828539:WP_0000045WP_0000045

Gas Treatment

AGRU
Little CO2 content in the feed gas from non-associated gas well

Dehydrator
2x100%

Fractionation
Adjust LNG HHV & Stabilize condensate Located around the midship to minimize the motion

Future Products & Business Development Institute

31

2009. 4.1

Utility Gas Turbine


Gas turbine
For MR compressor
Located at the upper deck above the MR process Two trains configuration Well separated from LQ

For electric power generation


Right behind of the LQ at the port side Safe equipment requiring no hazard area classification

Turbine blade rotor failure as a potential risk


Rather a common practice on offshore plant

Future Products & Business Development Institute

32

2009. 4.1

16

APCPCWM_4828539:WP_0000045WP_000004

APCPCWM_4828539:WP_0000045WP_0000045

Safety Device Cryogenic spill


Piping of cryogenic flow over the deck minimized
Around the cold box and the short direct run-down LNG piping to cargo tank

Protection
Shield for HP flanges Drip trays for LP flanges Local SUS plating may be considered

Management
Deluge under the offloading station Spill overboard Evaporation by natural ventilation Closed drain system to return large spill Air blower away from the vessel

Future Products & Business Development Institute

33

2009. 4.1

Safety Device Fire fighting


Passive fire protection - Fire rating
Design fire scenario Jet fire rating
Large inventory hydrocarbon vessels including MR storage Primary structure such as module stools, columns, base of the flare tower SMA aft

Hydrocarbon fire rating


Fire wall behind the LQ

Active Fire Fighting


Water deluge on area & equipment Dry powder system Foam monitor

Details to be considered after FERA


Future Products & Business Development Institute

34

2009. 4.1

17

APCPCWM_4828539:WP_0000045WP_000004

APCPCWM_4828539:WP_0000045WP_0000045

Conclusion DSME, prepared for HSE issues on an LNG FPSO! DSME LNG FPSO
Optimum design & layout will be developed to obtain inherent safety Process risk as well those from SMR will be controlled
A compact process technology would enable a safer design FERA will be used to manage the process risk!

Non-process risk will be controlled HSE will be an independent discipline during whole process of development
Systematic risk assessment Structural design to withstand design accidental loads
Future Products & Business Development Institute

35

2009. 4.1

Thank you!
DSME
Future Products & Business Research Institute

Sung Hoon Sean Kim T. +82-2-2129-0864 E. vivlavie@dsme.co.kr

Future Products & Business Development Institute

36

2009. 4.1

18

You might also like