Some people says that "restrained" is buried piping, and unrestrained is above ground. Is it
right?
pennpiper (Mechanical) 22 Aug 18 12:55
"Is it right?"
Well yes! and no! Depending on the situation and the interpretation of the term "Restrained".
In most cases, in Piping, Restrained means there are Anchors and there are Guides involved.
Example: A long Steam line on an above ground pipe rack. There will be Expansion Loops
required to adsorb the thermal expansion. For these Loops to function properly there needs to
be Anchors, (say 50meters [+/-] away) on each side of the Loop and Pipe Guides at every
other pipe support.
These Anchors and Guides are called "Restraints".
Anchors can be Fixed Anchors, preventing (or restraining) movement in all directions. There
are also Anchors that allow movement in lateral directions but prevent movement in a lineal
directions.
Guides are most often to "Restrain" or control the growth movement in pipes caused by
thermal expansion.
I hope this is helpful.
Sometimes its possible to do all the right things and still get bad results
833.1 Restraint
(a) The restraint condition is a factor in the structural behavior of the pipeline. The degree of
restraint may be affected by aspects of pipeline construction, support design, soil properties,
and terrain. Part 833 is applicable to all steel piping within the scope of B31.8. For purposes
of design, this Code recognizes two axial restraint conditions, "restrained" and
"unrestrained". Guidance in categorizing the restraint condition is given below.
(b) Piping in which soil or supports prevent axial displacement of flexure at bends is
"restrained". Restrained piping may include the following;
(c) Piping that is freed to displace axially or flex at bends is "unrestrained". Unrestrained
piping may include the following:
(3) an unbackfilled section of otherwise buried pipeline that is sufficiently flexible to displace
laterally or which contains a bend
You need to read the entire section 833, 834 & 835 t see what difference it makes.
Basically Restrained pipe is buried pipe, where there is no thermal expansion and hence any
thermal effects results in additional axial stress. However in poor or unconsolidated soil at
bends, this is regarded as unrestrained.
Unrestrained pipe has no calculation in axial stress that includes for thermal stress, therefore
all thermal expansion is assumed to be free or it falls into the "sufficient flexibility" category
-833.7 (3)
fully restrained buried pipe is only assumed for a straight level pipe when you are 150-250m
away from a bend or end point.
Everything in between falls into the grey zone where you need to look at it carefully and see
if a more complex stress analysis including some sort of computerized analysis.