Overview of Electrical Engineering Practices & Application of building Services
Topic 2 Fuses and Circuit Breakers
2.1 Fuses A fuse is defined as “a device for opening a circuit by means of a conductor designed to melt when an excessive current flows along it.”
There are three main types of fuses:
the semi-enclosed or rewirable fuse (Figure 2-1) the cartridge fuse (Figure 2-2) the HBC (High Breaking Capacity) fuse (Figure 2-3)
Figure 2-1: semi-enclosed or rewirable fuse
Figure 2-2: cartridge fuse
Topic 2- Fuses and Circuit Breakers Page 1 of 8
Overview of Electrical Engineering Practices & Application of building Services
Figure 2-3: High Breaking Capacity fuse
2.2 Circuit Breaker
The circuit breaker is a mechanical device used in a
circuit for automatic interruption of supply in the event of overload current and fault current. The circuit breaker installed in a circuit should break any fault current flowing in the circuit before such current causes danger due to thermal or mechanical effects produced in the circuit or the associated connections.
2.3 Types of Circuit Breakers
2.3.1 Miniature Circuit Breaker (MCB)
Miniature circuit breaker (MCB) is the small circuit
breaker used for the protection of final circuits at the Distribution Board (DB) of residential and small commercial and industrial installations.
It is used as an alternative to fuse, as it can be easily
reset and closed again after the fault in the circuit is cleared. It will trip on a small-sustained overcurrent, but not on a harmless transient overcurrent such as switching surge, e.g. in a fluorescent lamp circuit.
Topic 2- Fuses and Circuit Breakers Page 2 of 8
Overview of Electrical Engineering Practices & Application of building Services
The simplified diagram in Figure 2-4 shows the various
parts within an MCB. When the MCB is ON, it latches the various mechanisms within the MCB and ‘makes’ the switch contact. The toggle switch could also be used to disconnect the circuit for maintenance or isolation or to test the MCB for satisfactory operation.
Figure 2-4 A simplified diagram of a MCB
2.3.2 Moulded Case Circuit Breaker (MCCB)
A moulded case circuit breaker is a low voltage switching
and automatic protective device assembled in a moulded plastic housing. The nature of the sealed enclosure makes it a non-maintainable device.
Since inspection of contacts cannot be made,
replacement is recommended after breaking high fault current. MCCBs are basically defined as low voltage air- break circuit breakers.
MCCBs are normally used for installation that have
higher fault level (in excess of 9kA) and for protecting circuit of higher current rating (100A or more).
Topic 2- Fuses and Circuit Breakers Page 3 of 8
Overview of Electrical Engineering Practices & Application of building Services
MCCBs are available in ratings from 100A to about
2500A. They are broadly classified by the type of trip units fitted:- a. At the lower end of the range, MCCBs usually have fixed (non-adjustable) thermal trip element and magnetic trip element.
b. For breakers above 225A rating, thermal magnetic
trip units are generally interchangeable within any given breaker frame size. In such cases, the magnetic trip settings are adjustable.
MCCBs are mainly used to protect main feeder cables
for incoming supply to sub-circuits/distribution boards and for large motor circuits.
Topic 2- Fuses and Circuit Breakers Page 4 of 8
Overview of Electrical Engineering Practices & Application of building Services
2.3.3 Air Circuit Breaker (ACB)
The air circuit breaker (ACB) is one of the oldest forms of
automatic protective device. It consists of an operating mechanism, main contacts, arcing contacts, arc chute and a built-in overcurrent-tripping device. The name ACB is normally applied to large breakers that do not fall into the category of MCB or MCCB, although both are also air-break circuit breakers.
The ACBs are characterised by their sturdy construction,
ample electrical clearances, available in high current carrying, interrupting and making ratings. The tripping devices are adjustable to meet the required pick-up setting and operating time.
The air circuit breakers are intended primarily for
application in main switchboards to protect the incoming circuit fed by either a local generator or the low voltage side of a transformer, directly from the power utility.
They are also applicable for an individual branch-circuit
protection where the highest quality device is required and where special time-current characteristics are necessary for co-ordination.
Typically, an ACB manufacturer produces breakers with
current ratings in the range 800A to 5000A and a breaking capacity up to 120kA.
Topic 2- Fuses and Circuit Breakers Page 5 of 8
Overview of Electrical Engineering Practices & Application of building Services
2.3.4 Residual Current-Operated Circuit Breaker
(RCCB)
Residual current-operated circuit breaker (RCCB) is
primarily designed to protect against ‘indirect contact’ electric shock.
The term ‘indirect contact’ refers to the contact of the
supply voltage indirectly through the touching of the exposed conductive part such as the metallic enclosures of electrical appliances, the metallic conduit, trunking or cable tray.
These exposed conductive parts are insulated from the
live conductor and are connected to the earthing terminal and thus, should be at the earth potential.
However, during an earth fault, as there is an earth fault
current flowing from the live conductor through the exposed conductive parts to earth, the exposed metalwork may be at a high potential relative to earth. Touching the exposed conductive parts at this instance may cause an electric shock if its potential to earth exceeds 50V.
If it is a high impedance earth fault, the magnitude of the
earth fault current may not activate the overcurrent protective device. Thus, a current will continue to flow to earth, possibly generating heat and causing fire.
Topic 2- Fuses and Circuit Breakers Page 6 of 8
Overview of Electrical Engineering Practices & Application of building Services
RCCB is designed to detect such a residual current
(i.e. earth leakage current), compare it to a reference value and open the protected circuit when the residual current exceeds this reference value.
In this way, a RCCB provides an excellent protection
against the risk of electric shock and provides an excellent protection against the possibility of fire resulting from earth fault currents that tends to persist for lengthy periods without operating the overcurrent protective device.
The primary function of a RCCB is to give protection
against ‘indirect contact’. However, for RCCBs having operating residual currents not exceeding 30mA, there is an additional benefit, should other methods of protection fail, the RCCB will provide a high degree of protection to a user making direct contact with a live conductive part.
Figure 2-5 shows
an earth leakage current of 2A passing through the live conductor to earth, but not returning through the neutral. The difference between the phase and neutral currents is thus the earth Figure 2-5 The earth leakage current leakage current.
Topic 2- Fuses and Circuit Breakers Page 7 of 8
Overview of Electrical Engineering Practices & Application of building Services
Principle of Operation
The principle of operation of a RCCB is shown in Figure
2-6. The main contacts are closed against spring pressure and the loaded spring provides the energy to open the contacts when the retaining mechanism is tripped.
Figure 2-6 Principle of operation of RCCBs
Phase and neutral currents pass through identical coils
wound in opposite directions on a magnetic core, so each coil provide equal but opposite ampere-turns and no magnetic flux is set up when the currents are equal.
Earth leakage current increases the phase current,
which provides more ampere-turns than those from the neutral coil, and an alternating magnetic flux is set up in the core. This induces an emf in the search coil, which results in a current flowing in the trip coil and the main contacts are tripped.