BBS CABLES” more than safety Technical Catalogue a Hl ae i First Edition January, 2011 Second Edition: June, 2012 Re-print December, 2013 Third Edition January, 2016 Fourth Edition December, 2017 Re-print July, 2078 Re-print December, 2018 BBS Cables Ltd. Configure Bepari Tower (3° Floor) 62-64, Middle Badda, Progati Swarani Dhaka-1212, Bangladesh Tel :88-02-9859915-17, 9850771-72 Fax: 88-02-9850772 Factory: Jaina Bazar Telehate,Sreepur, Gazipur Bangladesh This Technical Catslogue has ben cmd by BBS Cables Ltd to support engineers with the most common data an cables in accordance with National «and Intemotional Standards For further query elated to Cables Wits & Conductors please refer fou Technical Department. ‘This Technical Catalogue may contin some Wing or printing eros Readers are requested to consider these eros if any) oral and suggest to Improve the quali Your valuable suggestions wilbe accepted affectionate BBS Cables Ltd., a sister concern of Bangladesh Building Systems Ltd. (BBSL) which is a leading Pre-Engineered Stee! Building Manufacturers in Bangladesh, has been incorporated in 2009. BBS Cables Ltd. is looking forward to managing expertise and obtaining technology to provide better engineering solutions through supplying quality electrical Cables, Wires, Conductors and better Customer Service. Now at the eve of the 21" century globalization, electric power has become an integral part for infrastructural development. With the rapid urbanization from corner to comer worldwide, the necessity of transmitting power assumes significant for sustainable industrial growth. So, our objective is to manufacture electrical Cables, Wires and Conductors of the highest quality and provide unparallel Customer Service to contribute to our national economic growth. We strongly believe that the relentless effort to quality and continuous improvement is the only key to long term. success Our factory is located at Sreepur, Gazipur, Bangladesh which is equipped with state of the art technology machineries to manufacture and test all types of quality Cables, Wires and Conductors in conformity with the latest version of National and International Standards e.g, International Electro-technical Commission (IEC), German Standard (VDE), British Standard (BS), Bangladesh Standard (BDS), Australian Standard (AS), Indian Standard (IS) and also meet up the specific requirements of the customer, We believe in a world that is safe and sound for us and also for our next generation. frul Hassan Engr. Mohammad B Chairman Master's in Advance Engineering Management (BUET) Bachelor of Technology n Civil Engineering (LT. Kanpur India) Director, Helix Wice & Cable Industries Ltd Director, BRS Metallurgc Industries Lt Director BBS infrastructure Lt, Director Bangladesh Bulding Systems Ltd (8BSL) Director Xiamen Reflective Insulations Lt. Director, Speed Builders & Engineers Lid Managing Directo, BBS Distribution Ltd Engr. Abu Noman Howlader Managing Director BSc. in Mechanical Engineering (BUET) Managing Director, Helix Wire & Cable Industrest Lt. “Managing Ditector, 885 Metallurg Industries Ltd Managing Director, Bangladesh Building Systems Ltd. (BBSL) Managing Director, Xiamen Reflective Insulation Lt. Managing Director, Speed Builders & Engineers Ltd Director, 885 infrastructure Ltd Director, BBS Distribution Lt Engr. Hasan Morshed Chowdhury Director BSc. in CivilEngineering (BUET) Director, Helix Wire & Cable Industries Ltd ‘Chairman, Bangladesh Building Systems Ltd (BBSL) Director, BBS Metallurgic Industries Ltd Director, Xiamen Reflective Insulations Lt. Managing Director, BBS Infrastructure Ltd Director, BS Distribution Ltd Engr. Mohammad Ruhul Majid Director BSc. in Civil Engineering (BUET) Director, Helix Wice & Cable Industries Lid Director, 885 Metallurg Industries Ltd Director, Bangladesh Building Systems Ltd. (BBS) Director, Xiamen Reflective Insulations Lt. Director B85 nfrastucture Ltd Director, BS Distribution Ltd Md. Ashraf AliKhan Director Bachelor of Arts from Rajshahi University Director, Helix Wice & Cable Industries Lt Director, BBS Metallurgc Industries Ltd Director, Bangladesh Building Systems Ltd (B8SL) Director, Xiamen Reflective Insulations Lt. Director, BBS Infrastructure Lt, Director, BS Distribution Lt PVC Insulated, FRSkin Coated Copper/Aluminium House Wiing/Domestic Cables PVCX.PE Insulated, PVC Sheathed Power and Control Cables with or without Armour XLPE Insulated, PVC Sheathed Powe Cables up to 33 KV voltage Various Types of FRLFALS, Fi8-750°G LSHF Cables, HR-105°%C, House Wiring & Power Cables Various Types of PE insulated Telecommunication Cables,Co-axal Cables, Orop Wires Pre-assembled Insulated Aluminium Cables with ACS% messenger wire Bare Aluminium & Copper Conductors and Wiees with or without Annealing Insulated or Bare Aluminium Stranded Conductors (AAC) ‘Aluminium Conductor Steel Re-Inforced (ACSR) [AI Aluminium Alloy Conductors (AARC) Copper Wire Braided, ALMylar Tape Shielded Pair Shielded and Overall Shielded Cables Customized Cables, Wires,and Conductors as per Customers Requirement (Our expert team is able to design and customize cables to suit specifi customers requirement. To ensure the quality of our cables, our qualified engineers use the latest technology and equipments to test and monitor the entire production process. today’s market no product can expect sel effectively fit snot rooted in sound engineering designed. BBS CABLES are designed and manufactured with the latest national and international standards Using the latest technology and equipment BBS Cables Ltd. caries outa full range of Routine and Type Tests as per 8S, IEG VDE and ‘other National and International Standards. Inthe manufacturing process we maintain stringent quality assurance procedures to give long term reliability and peace of mind ‘To maintain health and safety standards, regular training is provided to all of our employees that covers special hazards, how to protect loneself,causes accidents at work preventing sips and falls and howto use tools and machine safety BBS Cables Ltd. uses only tied and tested materials and follow the processes in fll compliance with all relevant National and International Standards to protect and preserve the environment Installation: The area of installation whether indoor, outdoor, underground, or aerial is critical in t 1 choice of cable because the ‘exposures to various elements may affect the performance and safety of cable. This is where the characteristics of insulation play an important part Voltage Rating: Determine the size ofthe conductor and the thickness and type of insulation. Conductor Size: The current load, KVA load and kilowatt load are governed by voltage drop besides the heating and power factors “These must be known before determining the conductor siz, [Ampacity Limitation: The maximum current 2 cable can safely carry without exceeding the capacity ofthe insulation or jacketed. material External Condition: The presence of other sources of heat located in the installation, such as pipes, corrosive agents, structural ‘materials and other cables can cause increase in the temperature of cables Optimum cable performance can be obtained from a cable such as BBS CABLES, with access tothe latest developments in conductor, Insulation, and protective materials technology. Our experienced Technical staff can provide guidance on cable selection and installation and can ensure that you get the right cables for your job, Power Cables up to nominal voltage of 30 KV ae suitable for indoor outdoor direct burial in earth 2s wells in water or in concrete. The installation must be caried out careful, avoiding any impact on the properties ofthe cable & followings have to be considered, + Protection against rect sun irradiation Laying on solid, smooth and fre of stones ground or bedding in sand or stone free soil Protection against mechanical damage + Protection against chemical and thermos influence ‘The maximum permitted puling force during installation isP = SKA Where, = 50 N/m? and A= Sum ofthe cross section ofall copper conductors. Allturns of te installation line shall be well shaped and equipped with rls, ‘The bending radius of single core cables shall not be smaller than 15 X Dj for mult-care cables 12XDy, ‘The minimum installation temperature for the cables s-5°C for cables with PVC Sheath and -20°C for cables with PE Sheath. This value refers to the cable temperature, not the environmental temperature ‘The inner diameter of ducts and tubes should not be less than 1.5 X Dy, if more than ane cable per tube is installed, they should not tight each other Underground cables should be buried at least 60 cm under the surface, the depth of cables under roadways not less than 80 cm. Fixing of Cables If cables are installed horizontally on walls ceiling or trays by lamps, the distance between fixing 20 X Dy, but not more than 80cm. For vertical instalation the distance may be Increased, but not more than 150 cm. Compression of the cable must be strictly avoided Single-core cables must be fixed with non-magnetic clamps only Meter Marking ‘According to the standard cables with diameter > 10 mm must cary a meter mark The marks may have a tolerance of 1%,but they are not calibrated. Incomplete or missing marks (on shart distances) may not be claimed. For defining the delivery length only calibrated measuring equipment has to be used. As Per BDS 900 & BS 6004 (450/750 V & 300 / 500V) BYA-FRIBAYA-FR FRPVC insulated Non-Sheathed Single Core Cable BYA-FRLS/BAVA-FRLS FRLS PVC insulated Non-Sheathed Single Core Cable aan FRPVC Insulated Non-Sheathed Fire Resistant Cable FRLS PVC Insulated Non-Sheathed Fire Resistant Cable ishe LSHF Insulated Building Wires ‘As Per BDS 900 & BS 6004 (450/750 V & 300/500 V) BYA/BAYA PVC Insulated Non-sheathed Single Core Cable 'BYM/BAYM PVC Insulated & PVC Sheathed Single/Multi Cable BYFY/ BAYEY PVC Insulated & PVC Sheathed Flat Cable BYFYE PVC Insulated & PVC Sheathed Flat Cable with Earth Continuity Conductor As Per BDS 899 & BS 6500 (300/500 V) Flexible (1/7) PVC Insulated Single Core & Twisted Twin Core Flexible Cable Flexible (F/T) PVC Insulated & PVC Sheathed Flat Twin Core Flexible Cable Flexible Cable PVC insulated & PVC Sheathed 234 Core Flexible Cable As Per VDE 0271 & IEC 60502-1 (600/100 V) NYY / NAY PVC Insulated & PVC Sheathed Single Core Cable Yy/AYY, PVC Insulated & PVC Sheathed Single Core Cable NYY/ NAY PVC Insulated & PVC Sheathed Multi Core Cable yy /AYY. PVC Insulated & PVC Sheathed Multi Core Cable NYRaY/NAYRAY PVC insulated, Aluminium wire armoured & PVC sheathed Cable ‘YRaY /AYRAY PVC Insulated, Aluminium wire armoured & PVC sheathed Cable NYFGbY /NAYFGbY PVC Insulated, Fat steel wire armoured & PVC sheathed Cable YFGY / AYFGY PVC Insulated, Fat steel wire armoured & PVC sheathed Cable INYRGLY / NAYRGBY “VC Insulated, Round steel wire armoured & PVC sheathed Cable YRGY / AYRGY PVC Insulated, Round stel wire armoured & PVC sheathed Cable Nyy PVC Insulated & PVC Sheathed Multi Core Control Cable NYcY. PVC Insulated, Concentric Copper Conductor & PVC Sheathed Cable DUPLEX PVC Insulated & Two core twisted Service Drop Cable /QUADUPLEX PVC Insulated & Four core twisted Service Drop Cable ‘TELEPHONE CABLE PE insulated & PVC Sheathed Telecommunication Cable JUMPER WIRE PE Insulated Jumper Wire DROP WIRE. PE Insulated Twin Core Drop Wire ‘COAXIAL CABLE PE Insulated, CU wire braided & PVC Sheathed Coaxial Cable ‘WELDING CABLE PVC Insulated Fiexibie Welding Cable (NYAB) ‘As Per VDE 0271 (60/1000 V) NYY PVC Insulated & PVC Sheathed Flexible Cable Page iP) 54 78 si0 1114 is6 7 8 18 i820 2 2 23-26 23:26 7 7 28-30 28-30 Bee 3133 34 5 36 36 7 38 38 38 39 404i SS vl ‘As Per IEC 60502-1 (600/1000 V) xv /AaKy Loe islied VC Sheth aia ove Cable BxRay /ADHRaY TPE nslted Aluminium wre armoured &PVC seated single Coe Cale /2XFGY / A2XFGY "XLPE insulated, Flat steel wire armoured & PVC sheathed Mukti Core Cable ‘2XRGY / A2XRGY EXLPE Insulated, Round steel wire armoured & PVC sheathed Mulki Core Cable xv “XLPE Insulated & PVC Sheathed Multi Core Control Cable As PerlEC 60331, 85 6387 ‘rink “Fac Resistant inal Gove Gable AsPerlEC 607541 82 ‘she ‘LSHEinslted Single Core Cable As er EC 60502-2 6 KV to 15 KV) axis tb insted te Shih Sngle Cove Cie axnsvRay LP slated Aluminum wire armoured &PVC sheathed Single Core Cable bee “ML Ile 1 VC sheathed ul Core Cable “2XSEYFGY XLPE Insulated, steel wire armoured & PVC sheathed Multi Core Cable axsevacy {LP uated PVC Sheathed a Core Cnel Cable “A2XSEYFGY =XLPE Insulated & PVC Sheathed Aluminium Cable }DS-1036, BS-215 & IEC-207 “Al Aluminium Conductor DS-1036, BS-215 & BS-6485 Insulated All Aluminium Conductor Al Aluminium Conductor ‘As Per BDS-1037, BS-215-2 & IEC-209 ACR ‘Aluminium Conductor Steel Reinforced ‘As Per BDS-1037, ASTM-B232, 82,83 & IEC-209 D4,02,0.3,0-28 ‘Aluminium Conductor Steel Reinforced (D405 “Hard drawn & Annealed Bare Solid Aluminium Wire -6,D-7,D-8,D-9,-10 Deo obe sso Medium Hard Drawn Bare Solid & Stranded Copper Conductor ‘As Per ASTM-8231,8232 & ICEA-S-66-524 (NEMA WC7) D-11,D-12D-14D-15 pre assembled XLPE Insulated Aluminium Cable with ACSR Messenger bauoas pas D-16, 0-17, D-18, 0-19 |XLPE insulated Medium Hard Drawn Copper Cable Beas: Bsi,o-81/084 "bare Aluminum Aloy Condor D-59-D-61,0-62 “HDPE Insulated ACSR Conductor ‘Des VE Insulated Aluminium Cable with ACSR Messenger “GuyWire Earnie stance Cahaied Se ire TECHNICAL INFORMATION FOR LT POWER & HT POWER CABLES "USER'S GUIDELINE (CABLES & DRUM) Page a5 7 4850 51-53 5561 6258 6871 R78 1577 7880 31-83 35 a6 36 7 a8 8 89 9 90 6 3 oi 92 Ponaid iste MH FRIS LsHF FR Interpretation ‘According to VDE Standard According to British Standard Insulation or Sheath of Thermoplastic based on PVC ‘Aluminium Cable With Al Conductor Insulated Single Core Cable Sheathed Cable ‘Medium Hand-held Equipment Cable Intemational Colour Code Flat Cable Earth Continuity Conductor Galvanized Steel Flat wire armouring Concentric Conductor of Copper Galvanized Stee! Round wire armouring | Galvanized Stee! Tape ‘According To BS-2004 (imperial System) Heli Conductor of Single Solid wire having Circulae Cross-section Conductor of Multiple Stranded wires having Circular Cross-section Conductor of Multiple Stranded wires having Sector Shaped Cross-section CCompacted Circular Stranded Conductor Sector Shaped Solid Crosslinked Polyethylene (XLPE) Shield of Copper For Malki core Cables With Individual Screens Round Aluminium wire armoured "Non-metallic Semi-Condicting Sereen over Conductor & over Insulation Polyethylene (PE) Insulation Flame Retandant lame Retandant Low Smoke ‘ow Smoke Halogen Free Fre Resistant vl vi ‘Abbreviation aps. LEC VDE ce ‘CENELEC USA _DEMKO. DKE EN HN IE IEEE 150. fre NEC NE NEC, SAE SEV, uM UNI \VoEW Interpretation | Bangladesh Standard __Inseenational Electrotechnical Commission | Union of Serman Electrical Engineer British Standard __ American Society fr Testing and Material Insulated Cable Engineers Associana, | National Elecric Manufacturers Assocation _ Japanese Industrial Standard Standards National Indonesia _ Deutsche Industral Norms __ American National Standard institution (USA) _ Australian Standard Australia, Brtsh Standard Institution (Great Britain), | Bureau Vertas (France) Community Antenna Television (international, | Committee Elecrotecnicue Beige (Belgium) "Intemational Commission on Rules for the Approval of Electrical Equipment Commission Electrotechnique Internationa _ Committee European de Normalization Electrotechnique Canadian Standard Association (Canada) __Denmarks Electric Material Konto! __BeutschesFlectrotechnique Kommission in DIN & VDE (Germany) _ European Standards (Germany) | Harmonisation des Noemes (france) Institute of Electrical Engineers (Great Britain) _ Institute of Electrical & Flecronics Engineers (Great Britain), Ingernational Organization for Standardization __ Miltary Specification (USA) National Electrical Code (USA). Normes Francaises (France) _Notmes Francalses Class ¢ (France _ Society of Automotive Engineers __ Svenska Elektriska Kommission (Sweden) Switzerlands Electrotechnical Verein (Switzerang) _Underwniters Laboratories (USA), Unificazione National aliana (aly) | Verband Deutscher Eleckrotechniker W (Germany) — —— RR cs PVGRINSUEATED BUILDINGIWIRES) Opps canies BBS CA Flame Retardant (3) cables eit the spreading of fire in anew area by having behavior in fre under tions whichis proven by pasing the test as per IEC 60332 The uses of FR cables ate especialy impo: anttoday because modern homes with the nceaceinelecrcl product alone, presenta greater riko fre damage Inadaltionsusage ofFRcables isa component o protect the public particularly more vulnerable population inclu Ing the elders chilren in School College, Hospital ane more populated areas. 3 204 3 Construction: |. Annesied Copper/ Aluminium Conductor 2. Virgin FR PVC Insulation 3. Color Coated PVC Colour: @H COCO PHYSICAL DATA ELECTRICAL DATA CE ‘eorex? nos mm mm | mm kg/km kg/km: ohmvlen ohmvkm amps amps amas amps wo vias e723 at - 16 to | 30s mo? 25 aa Samia 16 wa yom om 0726 32 ks St ws Wie eo 28 tat ~ 16 2 wis 782m 72733 tw eo wis | aso mo 273 a atte tos) om ok 138 0g se 0S was) vies R328 am SnieZ 2% yas 7s? om 0833 4 ot ts wo | 70% om 8S 4 Som o ao 7/0as rm =k 38) 48S} asta 30208 assim 38 AT Sees yxeo 704 rm B43 82 ak 508 saw wo 7m was SR sa ae pos 732m = to 54 6S gs Steg 50g wo | 73s om we S667 sae at was 7m 10 27S wT HTB ce KEY De ee Ma. Boe Gs in “re Eee oe ee Note: 1. Current ratings are vale for cables laid under defined conditions at page no, 93.For current ratings at deviated conditions apply correction factors as ven on page no.93 ZA a Application: Flame Retardant (3) cables esis the spreading of fein anev area byhaving behavior in fre under defined conatins whichis proven by passing the tes as pe IEC 60352. The uses of FR cables ae especialy import- ant today because modern homes, with the increas in electrical product alone, present a greater riskef fre damage Inadlton usage of R cables 2 component to protect the public particularly more vulnerable population ineluc- ing the elders, chiléren in School &Colege, Hospital ane more populated areas. Construction: |. Annealed Copper/ Aluminium Conductor 2 Virgin FRPYCIncuation 3. Color Coated PYC colour @HCOS PHYSICAL DATA FLECTRICAL DATA Gorexmm! nosinm mm mm mm. agikm Kgikm: ohm ohmikm "amps amp amp amps ws m2 87 76 6 om st ge tas | omné rm 12) 80 108 ay sk) ose ome eae 90 miné. «om 1410828532216 OSK ga 136 8st 07 a0 mind m4 iad 146 raz aS ose ams ear fa ‘omnis om 18 T4171 85 Guang os 76 tad 53_ 65 te20 | mint@is om 16 186) TR nay ayaa | ass 2k ts 281s 80 mmis'S om «18732081835 S72, One O26 3327 feiss | ming0 | m=) -20 193-283 TaBT | 705 nseT 6k ae 2s 240 mna430 om 22220266 ASB NO. ODTSA ONS 432 285, a0 | min3430 im 24 | 24S 2863055 1425. OngoT a0 526 3a, 00 mins tm «26 «2753324078508 ODN ONTT8 os a6 eso mins3 m= 2830S) -369° SOB tues tes 00s 72 | 489 630 mings om. 28 380.) 411.363 2310. onmas nts BS 56 KEY Oe Bs. Be a-- © A=. Re Beew E ce Note: 1. Current ratings ae valid for cables laid under defined conditions at page no.93.For current ratings at deviated conditions IS apply correction factors as given on page no.93 02 Opps capies* DOBBS CABLES Application: Flame Retardant Low Smoke (FRLS) cables are most widely used among al cables. Law voltage FRLS cables ate used in electrical power distribution substations for industrials application, In addition, usage of FALS Cables is a component are to protect the publi, particularly more vulnerable population.Schools & Colleges, Hospitals and more populated areas. Construction: J. Annealed Copper/Aluminium Conductor. 2. Flame Retardant Low Smoke (FRLS) PVC Insulation. Colour @OO: PHYSICAL DATA FLECTRICAL DATA iA Aw Aw ‘coexmm osm mm mm | mm kgikm kg/km | chmvkm ohmvkm = amas amps | amps amps mio via eon 2s 30 at Boo we wo) Smee m7 25 8a ae wis 34m 07,26 32 aS mis MB me Or 268 2 tat 6 bw wis | 7082 om 072733 a) tt mis | 308 mo? 273 tw woo vos) om O81 38 tt tsk 2S vos | vive e852 8am Roo. we wos os) om 0838 80) ts veo) 7074 mo 8S A ao 20 wo | 705m 083k 46 STs] at 9H was) 70s) m3 AT 56 sgt eo 704m O88 52 kms] wo 7M mas asm aa ves | 732m 10 S465 gta P88 mio) 73s mt S667 swe was igs om to) 2 TS ght wie 770m 4 SST ww KEY ewes Note: 1. Current ratings ae valid for cables nic under defined conditions at page no.93. For current ratings at deviated conditions apply correction factors as given on page no 93 Z| 03 ation: Flame Retardant Low Smoke (FRLS) cables are most widely used among all ables. Law voltage FRLS cables are used in electrical power distribution substations for industrials application, In addition, usage of FRLS Cables is a component are to protect the public, particularly more vulnerable population, Schools & Colleges, Hospitals and more populated areas. Ce Se Construction: J. Annealed Copper/Aluminium Conductor. 2. Flame Retardant Low Smoke (FRLS) PVC insulation. PHYSICAL OATA ELECTRICAL DATA @ AG ‘eorex nos mm mm mm. kg/km kg/km: ohmvkm — ohmvkm amps amps amps amps as 7214 om 12 887i 0 pas ming mm 129 109 7313S oa 27a so min om 14108128 5218 ass7 oss] 138 gk 1687 a0 mini? mm) 1A RE AB 7a DAS oso sear a7 1995 min.'S om 18}. 9853209805964 25385 Wiz mings | mm | 18 186) 188 zR7 aro alse oss 2a ase 281 ae iso min te/13 mm 1873 2081535572 GAM 020s noon wes "ming m0 193) 233, tH8 70S comm a6 =a 2a aed min3a30 | om 22220-66458 810 awys4 ONS Pan 235 300 mind4a0 mm = 2A AS 29H 4055 125 OG O10 2 6 a ico "min.s3 om 26275332 4075050470077 fa | ae ys00 mins? sm «28 «30S | 369 SoH Hass omnes OHS 272 a9 Ye20, UN S328 KO AT 6868 2a games ong 88888. KEY SS ee Mos. Be @) moe We Beene tena RA cores Note: 1. Current ratings are valid for cables lid under defined conditions at page no.93.For cutent ratings at deviated conditions IS apply correction factors as given on pagena.93, CULT UAE eR Te SS Jas A % re Lua J ZA < OBBs caBies* OBBS CABLES’ ‘Applicaton: These cables are designed for emergency lighting, fie alarms and essential equipment in fre situations where an uninterrupted power supply has tobe guaranteed During fre, electric cicuts and the associated lighting may be damaged. Power and data communications may be suspended. Human safety may depend on continued operation of lighting, elevators and escaltors, fire fighting ‘water pumps fe alam and ventilation fans. The conductor is manufactured with a specially designed heat barter and fire resistant insulation which esse the fre to reach conductor surface. The cable continues to remain into ‘operation at high temperatures like 650°, 750°C & 950°C as per various conditions of operation and applications. PHYSICAL DATA " elecrmicat bata orexmn nsdn mm g/km Kalk" ohnvien rv amps amps amps amps ws nse |e o7 3% om tale » ws 7082 m7 2 mm we me as yee OB Seo ae vas jos? | m8 mm mm os | ee ao nes ms 5632 aw a2 bso 70k |B m3 aoe aka mo) asm 1D 2338s wis) 7D; om | 10 6 SDS ims 7am 12 20 13 om hw OS Ming om 12 100576158 aac aa bso Wing rm 14118 Ste 230 a3a7 set 1356 8B Tak TO wo Mina | om 14132 aS 2568 | ozs ome 78220737 ss ints rm 18187900 ou an aaa Nsw a8 pe wing's fm 8/168 y200 | ao ass 0253 28158218 miso Minlg's | om 1819804178206. 333217 1x@5 | “Mingo” om) 20210 tase | 740 onoet | et se ae a0 in3a/30_ orm | 22,241 zaps 968 omyst | _o1as 452285 yon Minsaso orm 28285 | Sams tive ota 56 3a 100 Ming orm 28301 a0 s6a. neyo. ogre 6946 "S00 | Miss | om) 28333, asso too ones 152189 nest Min S328 970s 2300. mas 0k 85S, S88 KEY B/E. / Es: Mi%«.. 6 Gesist, (meen > fa) Note: 1. Current ratings are valid for cables laid in under defined conditions at page no. 98. For current ratings ae deviated conditions apply correction factors as given on page no. 93. Z| 0s SS 06 OBBS CABLES" ‘Applicaton: These cables are designed for emergency lighting, fie alarms and essential equipment in fre situations where an uninterrupted power supply as to be guaranteed, During fre eletticcicuts and te associated lighting may be damaged. Power and data communications may be suspended. Human safety may depend on continued operation of lighting, elevators and escalators, firefighting wate: pumps, re alarm and ventilation fans. The conductor is manufactured with a specially designed heat barter land fre resistant insulation which resists the fre to teach conductor suface. The cable continues to remain into ‘operation at high temperatures lke 650°, 750°C & 950°C as pe various conditions of operation and applications. 3 204 3 1 Construction: 1 Annealed Cpper/Aluminium Conductor 2 Mia Tae SyiheislssoverConducar 3. Fame RetrdantLow Smoke LS) PUCIsulation. Colour: OOO PHYSICAL DATA " LECTRICAL Dara 2 SUE Ee rom a er a see aad ee i eal : op moro ib foc sofas ae a : um oa orm a ee a Se eee ene a Eb) amr ng anon aba a so rh a a Se a re ae Sea coe gs aes ee ae eee a ee ee Sitnjohs a nee ee ee eee Sinn mn gee rm ge egg ee eens: gn anes ae ee mines a ae key ee, Bes / Be Ee: Are i Bi. Gjeans, (mm GB) om Nn 1, Current ratings are valid for cables laid in under defined conditions at page no. 93. For current ratings ae deviated conditions apply correction factors as given on page no. 83. Gaps cantes: BUILDING WIRES LSHF / LSZH / LSOH INSULATED ‘Opps castes: Applicaton: Electrical safety is» function of five characteristic viz. smoke, hazardous gas generation, rate of heat release, fame spread and rate of buming. In case offre ina closed area, trapped people are unable to find the exit due to emission of thick lack smoke and lose consciousness due to the inhalation of toxic fumes before they can evacuate for safety. The advantage of low smoke and low acid gas generation are addtional and critical features avilable with LSHF / LSZH / LSOH wires in comparison with FR (Flame Resistant) wires which do not provide these properties J. Annealed Copper/Aluminium Conductor 2. LSHE Insulation PHYSICAL DATA ELECTRICAL DATA ee ee a ee a Se a ee) KEY es. Bee Mex. Oe See Bee Bee -- Ga Or [ele Note: {Current ratings ae valid for cables laid in under defined conditions at page no. 93. For current ratings are deviated conditions apply correction factors as given on pagerno. 83 Z| 7 Applicaton: Elecrical safety is» function of fve characteristics viz, smoke, hazardous gas generation rate of heat release, fame spread and rate of burning ln case of fre ina closed area, rapped people are unable to find the exit due to emission of thick black smoke and lose consciousness due tothe inhalation of toxic umes before ‘they can evacuate for safety. The advantage of low smoke and low acid gas generation are addtional and critical features avilable with LSHE / LSZH / LSOH wies in comparison with FR (Fame Resistant) wires which do not provide these properties ‘Construction: 1 Annealed Copper/Aluminium Conductor 2. SHE insulation Colour @C COO PHYSICAL DATA FLECTRICAL DATA w Nw A Ge exe? nox mm mm mm_—kgikm kg/km ohm ohavkm amps amps | amps _ amps as 7a om 12g Tao am gg Bs ming orm 12 90 SF SE Ose moe te ae ted ming. orm T0132 «S2_| 2160387 06K t38 gs tek tO tO mint2 rm TA DASA 782 F285 06 om ts 2077 ts minis tm 181A 17985 82019503214. 283—_— 165, Tez) mintais form | T8156 | 194 | tay | 47 ass 0258 da S828 a tals) ominigy's orm T8173 216 1535 S72 ae 0206 3 tees | "ming | orm 20) 1932411891 | 705 | acest aed Daa ae tod mingay30.= rm == 2220S 2458 510s OS 4s 235 300 | min330 | orm 24 4S 306 | 3055 | 1125 coset a0 Dae ua teed "mins? rm 26 7S 3434781505 0oH? one Teer 500 mings =m == 2830S) 382 SMB | 186s ses OnmAS Dota as 1x30 mins} rm) 28 340256632510 ocenss omnes Ts 5s6 -- anette Cg) women Bn ay Note: 1. Current ratings ae valid for cables lai in under defined conditions at page no. 92. For current ratings are deviated conditions IS Spplycomecton factors an given on page no 88 os a Te EUR TSS Application: Suitable for surface mounted or concealed stel conduits or trunking. Also 5 installation in and appfance up to 1000V ac or upto 750V to earth dc rood Construction: 1. Annealed Copper/ Aluminium Conductor. PVC Insulation. colour @@@@@ PHYSICAL DATA ELECTRICAL DATA wa Aw) Aw | ‘orexmm® nosinm =m, mms Mm—Aglkm kg/km ohmvkm ohavkm | amps amps = amps amps wo Neorg 181 Boo. mo | 36s mo? 2S Oa 181 Bl 6 wis 37am 726 32 ames ts bis 1B re or 6 tat we: | Do wis yosz om oy 2733 te) et mis) oan mm oy 27 38 et ot eo yoo yo) mk 3138 ge SS os ie mek 28am 2. wos og) mk 33 80 mts pao | 77am ok 3S 48 ao 8 ome a0 mo | yoss om Os 3848 Sts alm) mas 7st mk 39 AT 5g gs aS so osm Ok 4352 ge ata) akg wo 7m mw 4s SR sam os | N32 rm to SH Sts 2 as go) 50 gt pao 703s mt S667 sew eT was 7s rm 10 27S sg wD wie 770m BAS ASS KEY S38 Bee Me. Se Ben Oo Bae, Note: 1. Current ratings ae valid fo cables aid under defined conditions at page no, 93 For current ratings at deviated conditions apply correction factors as given on page no, 93. 09 ‘Application: Suitable for surface mounted o¢ concealed stee! conduits or trunking, Ako suitable for fd protected instalation nand appliance upto 1000 Vac or upto 750 to earth de PHYSICAL DATA ELECTRICAL DATA _eexem! nos mm mm mm —kgikm Kalam’ ohmkn ohmikm amps amps amps amps yas 7218 m1 97 6 16 om ete yasmin rm 12 80 18 G73 NSB Ose ase 50 ominé rm 141028 S32 216 aay awn 36 ak NH? 7 min m4 aT 16 Taz 28S 06H MT 2077 te omin's sm 161471985 3a? aaa tad jwi20 | mintwis | rm 16 186 1B 27 a7 Sass a1 281s teis0 | mintaiS tm 1473.28 sas S72 ame aN 333217 jries | mingd | rm) 20 193-233 Test | 705 omssT OTe 3a as 0 minaq30 om =) 22220286 SE 10 | OMSs OS 452295, 200 | min3430 rm | 24) «245-286 | 5055 1125) OnmoT | O10 52632 30) mings stm =| «26 «27S «382 7A 3308 ODKT | OUTTE os a6 y9S00 | minSB | im «28 «30S | «369 S08 1865 | 0865 aK 752488 630 mings rm 2k 40) AI 63622310 Omme nN 1855. 356 WEY Ss Gee Ble. Qe em mm Bees, B= Bie 2 fle Note: 1, Current ratings ae valid for cables lid under defined conditions at page na 93. For curtent ratings at deviated conditions IS apply correction factors as given on page na 93 OBB CABLES" ‘Application: Suitable for fied instalatons in dry or damp premises dipped direct toa surface or on a cable tay Lunenclosed and also fr us in non metalic conduit (PVO. RSCRLESBANLACESH Construction: J. Annealed Copper/ Aluminium Conductor 2PYC Insulation 3. Grey PVC outer Sheath. colour @ PHYSICAL DATA ‘ELECTRICAL DATA ‘eexrm! nos/mn mm mm mm mm -gkmkglkm ohmikm — ohmvkm | amps amas amps amps md WB | we | 06 | og ak 4s tai Bo. wa) 3085 mm 06 ok kgs 28 a1 Bw bas M3 | 3074 om 07 gk 4243 a6 MOS as St ws ise fe 207 a8 | 42 as 21 eo fo Wis 7082 Lom Fok gz 88a) wis) Sogo fm 27 ok a ae 8 tate yao 3091 om OF 86 Sk M8] tS1R aS Ws Wik fe) kk ak aS 7a po 5 os jas 7067 om «O88 48 Sk STA wD tao) 7m fm | 8 ok S161 tS) ome ja 77085 sm «O80 R 8M Aww 30a MS osm | 08 a8 56 7 3 gs nso 7/104 | m8 09 6078S 308 awa wo ng im | 08 098 6S Pw aw ngs 7932 | m | 1909 70a? SSO wl wo) 73s m | 19 09 72 Rak nas 76 | m | 1010 80982] D Me 770 fm | 19 1 BD os 2 ITS as was SS tS 721 fm) 12 1) 100s 38S 2k 58 PBS SQM tm AR NMDA RTT 08240868 TTT MEY B=. Behl. D~ Gee, FM one! o Sd 1. Current ratings are valid for cables lid under defined conditions at page no. 93.For curent ratings at deviated conditions apply correction factors as given on page no. 93. SS Application: Suitable fr fixed installations in dry or damp premises dipped direct 10 a surface or ona cable ray tunenclased and also fr use in non metallic conduit (VC). Eye") NY BSCE ACE ass A059 4 B21 4 3 2 Construction: Amal oper Aluminum Conduct 2PYCIslaton Yer Sheath. PYCot Sheath Celour usta. oma ELECTCAL OAT Gag A Ga A ne mm hain im, | ohn | ags aps amps amps Dio vig ee? 768s 2 so Bib joes moe 2 te BR b Bot Be oe oe oor oo em on ee Bb js mor 2 Poker Bs joo om oor gs elo we om goo fa in ok aS th eee Bos jor om os doe Ws em eee Re fos om ok OSS ae ts an Bene om oof ne We re fw wee a eee rd a am ne Wo gh erg ig gna 2 ee 3 Bowe me Bes ee me eee n Key B= Bees = Ge hse 4] ep GE) Te) nrneae in nose ote 1. Current ratings ae valid for cables aid under defined conditions at page no, 93 For current ratings at deviated conditions apply correction factors as given on page no. 93. Application: Suitable for fed installations in dry or damp premises clipped direct toa surface or on a cable tray ‘unenclosed and also for usen nan metallic conduit (PVC). ‘Construction: 1 Annealed Copper/ Aluminium Conductor 2.PVC Insulation 3 PVC Inner Sheath 4. Grey PVC outer Sheath colour: PHYSICAL DATA ELECTRICAL DATA Carexmm? nom mmm mmm agikenkgykm’ Gkmim —ohm/km amps amps amos amas geo as re 812g oo 2 aaa es m7 12 eis aa amma 2 Bas 3h re 07 92g tos ge atts tote aus fF 7msz fom fay 12 92 tok ta ats te BaS Hao om 892g toga tat hts tote gas | vie fre ok 12 too aoa tat as gas 1s) om 0812S 125 tag et aT Fr CT B67 8 TAS TSS 386 27S] ao 73S m= 191A 190 $90 400 ak Basa gle | 770m =| 10) 1A | DS a6 SSS) Sk aos Rm 12 18 ao 60TH ORT 1D TD gos 1st sm 1218 24S 7806S 102305 asa] S908 MEY 23 Dee Bes. S- fe peewee Blew Oe). ye Note: 1. Current ratings ae valid for cables laid under defined conditions at page no. 93 For current ratings at deviated conditions apply correction factors as given on page no. 93. ZA 3 SS Application: Suitable for xed installations in dry r damp premises dipped direct toa surface or on a cable tray Lunenclosed and also for use in non metalic conduit (PVC). BBSCRRLES BANS ACCS ec Construction: 1. Annealed Cepper/ Aluminium Conductor 2 PYC Insulation 3 PC Inner Sheath 4. Grey PYC outer Sheath Colour: PHYSICAL OATA FLECTRICAL DATA ovine rosin mm mmm TMT | Kgikm’ Kg ohrvken” ehmvien amps amps amps” ames alo VIB we 08 12 BAB ape tat i a ‘do 30s rm 0812 BOB gy ua 0 me ais) vise oe 07 12 868 NS tg Dif wr see aus) 7s2 om 0712 100g nara tw ‘is soso om 0712100120 gg nara) as ie 0812 D180 ane mo Rt Mm Rs as 7s? om 812 SBS Oe ag} ja asm Ok TA DS Ga a asa fo | 7noe om 08 te 4D F170 aes Sagal io) 73s om | 10 14 05g gas wk ais 7m 30 2008S tosis gays Suga a5 Tae om 12 18 MS 8S to som wT 8 dos ss om 126 70,320 | amgs | am oss ass ak WEY =] room OM arcs, Note: 1. Current ratings ae valid for cables laid under defined conditions at page no, 93.For current ratings at deviated conditions apply correction factors as given on page no. 83 Application: Suitable or fixed instalationsin dry or damp premises clipped direct toa surface or ona cable tray ‘unenclosed and also for use in non metalic conduit (PVC), BScrasewssE 3 2 3 2 1 Construction: 1 Annealed Copper! Aluminium Conductor2.PYC Insulation & Cores Laid in Blat For, 3. Grey PVC outer Sheath Colour: PHYSICAL DATA ELECTRICAL DATA cxearmey nos. mm mm mm gen’ Kg/kmohmvrn ohmvkm amps amps amps amps mio Wise 08 sma get : 15 2d | wos om | 06 08 Has Set 5 15 M13 HOM sm «OF 08 sg 2140s 9 yon bis | Wiss fe | 07 | 08 sas 2 tz T8106 Boi 5 7082 m= 0708 basa 77 | ae 1210181018 Boe as iS | MOHD rm 0708 BSA 77 as 1210 TRI 16 Boom os 220 os! m=O Boo GS STB 20 wo 6 mas Wie we O81 9D 0 KD das 708) tm =O 8x82 oe ga 1210 we 2% | 0 pao | rome fom | 08 | 10 67 aay go 599 sak kd dao | 7088 rm «081032 182. tr asl =A) DS pas | 7st rm) 08 10S 165 TOR a gst 2x60 TNO m8 T1380 205130, oe as aS WEY = Bee Bs. nee mom Fo] vom ER acces Tews 5622 Ben ole Note: 1. Current ratings ae valid for cables laid under defined conditions at page no. 93. For current ratings at deviated conditions apply correction factors as given on page no, 93. ZA 15 CABLES* Application: Suitable or fixed installations in cry or damp premises clipped direct toa surface or ona cable tray ‘unenclosed and aso fr use in non metalic conduit (PVC) BOSCH acs Biscrasem cess ‘Construction: Annealed Copper/ Aluminium Conductor 2.PYC Insulation & Cores Lldin Flat Form 3. Grey PYC outer Sheath, Colour: PHYSICAL OATA "ELECTRICAL DATA SUE EEE Se ee eae os anay nnn " aa a i a Te ee aes nog eo oi ee as Sc si iat a SE ee a a ne nee ee oe ee ee wer SS. Dems Bee. 24 GBBS CABLES" Application: Suitable for indoor ovtdoorunderground and in water for continuous permissible service voltage of magn200 Volt. I I 4 32 4 B20 Construction: 1.Anneaied Copper /Aluminium Conductor 2. PVC Insulation 3. PVC inner Sheath 4, Black PVC outer Sheath, come SS PHYSICAL DATA ELECTRICAL DATA ee GA a GA om remy Tye il chs |etnhn | wees | ante | acs ees ‘ase nme mim 121270 gto armis guns) Mo 76 ms i assis mime. umm TP T8242 sap | 20 0sIS puwist WO To) 12) tne ul ses me. imme te 1974S 2 | imo OWA pei20 SO ISO 16 mae u S005 MND ami Td ZO als") sto | s05 onunsu pawwoase 1 Ma i le aa a 655 Som Nd MO 950 |r cine (aszn6 ose ys s/n us mine i Muni mits umm 1823 Wh ssa. 290 oI90M" b2sI0aK) 2 I-70 vn ua $5071 min iWAs _omim= 1824480” goo 230 010020 200044) 795 930827 vin u sis minse smi 20 26 395” 7650 asia aupiainbiewos0 0257 3s0 77 mats ut errors? an OC aT mats i omiist MeaHoo, smim Le 3063021 swe sogreinpronnme 0s ame IW L : i KEY coon aces, pam rr... deaaait SRM cerns =. es. wm [eo b Bex ta FG] neem @)” © tee - ote 1, Curent ratings ate valid fr cables aid under defined conditions at page no. 94 For current ratings at deviated consitions apply correction factors as given on pageno, 95.99 q 25 Application: Suitable for indoor outdoor underground and in water for continuous permissible service vokage of maonizo0Vets Construction: Annealed Copper/ Aluminium Conductor 2 PVC Insulation 3 PVC inner Sheath 4 Black PVC outer Sheath, cone $B PHYSICAL DATA ELECTRICAL DATA Korexmn® 995.0 mm mm. FRM gk gikm ohmvkm —ohm/km api amps amp? amp ‘as viae e088 2S | 0 m1 te) 6 ‘ds 782m kT Os 21 n is sos vie 0818140 a5 ie) 2 sas 7087 om Ok 48H 7a 30 B ax yas rm 1018628 299g! 2k) ks as hos mm 10 8 17S | 5a 34S 308 ast wk aw slo 735m =O 200g aad? k wt SG ais 77D mB aS oO NST ww SR sas 7214 om 1218278 600 9000727 120d 405 ming | sm) 12 18264 goo 94s 0528 ase | a0) a0 40 ming sm 1418280 2460 1310 0387 OHSS 20.50.16 4g mint2 sm 1421 | 335 5250. 1700! 268 ome 190 as 90s 495 min 15 sm 1822384 g4g0 2190 0193 0320S 75RD 4120 mintw/is | sm 1624 | AND 5500 2605, 0153 | 053 260 | 202 270/210 iso mints sm 1825452 ean. 3210 0128 020629529 40s a7 ‘iss min30 sm 2027 | SS a350. 3490 Ope ots a0 25735022 224 min3a30 sm 2228560 yo700 4925 00754 12s aes 89a 4300 min3430 | sm 24 31 640. 13200! $950 00601 | 0100 | 42s) 29 a7. 368 KEY Ms = Oe. §- a Be 1) a ST] renee @ vm oe) oom Paice? Note: 1. Current ratings are valid for cables lid under defined consltions at page no, 94, Fr curent ratings at deviated conditions apply conection factors as given on page no, 95-99 SS 26 OBBS CABLES" Application : Suitable fer indoor outdoor underground and in water for continuous permissible service voltage of raani200Vets. Ff € Ls = ; 1 Construction: 1 Annealed Copper/ Aluminium Canductor2.PYCinsulation 3. Round Aluminium wire Armour 4 Black PVC Sheath colour @ PHYSICAL DATA FLECTRICAL DATA Cr NG AG ne mm) mm mm | mm “Agikm kg/km’ ohmfm ohnvkm | amps amps | amps _ amps twas ming | rm 12195 | 18173 IS 90 ase ogee 15520-60124 tso | ming fom | 14) 435) 18 | 193 | 770 F370 One Ome tas | aa: 195 | 182 fd maid mm 14 135 18 208 3904550268 a2 TTS aS pas i miniS fom) M6) 495 | 18 | 233 F265 | 70 at | om | 270 | 210; 300 | 2 fo mings om 184g 1825S 1575 8001S 0253 310—« MO. 350 | 272 tisp min 183/18) g | 1A | 27S gets | 00) one 208 | 350270: OS 54 tgs mn. m 20 te, 18285325. 950 ous leh 390 «302460358 faa imins4z0 rm | 22) yg | 18 | 323 29201195. ome OS | 45D! 55 RT sod min3430, rm 24 20 | 20-360 3g20ta¥SOKOT—taD_—«SIS— ke KO. at tatoo minss | om | 26 | 39 21 | 40.1 675 1873, 0H nT | SES. 439 | 770. SAD iso) mins} om 28 3922-436 5795270 mRGS —ODmISgRD.S10.«900«GHD yesa0 mings fom | 28 | 30 | 24 | 472 | 7025 2760. ome | ODKee | 800 | 600 | 1030 | 721 wand m™nS3_ orm 28 3s 28 S44 9203465 OmD mH 9u5_ 708 116017 pesbo ANN 3 rm BSF 27 583/020 4250.) 90176, omen | toes. aan fata, 917 EY ° Note: 1. Current ratings ae vali for cables laid under defined condi apply correction factors as given on page no. 95-99 2. Forcompact conductors and lugs refer fo page ne, 108-109 jons at page no. 94, For current ratings at deviated conditions 7 Application: Suitable for indoor outdoor underground andin wate for continuous permissible service voltage of 72971200 Volts. PHYSICAL DATA ELECTRICAL DATA Gi aL @ aL @ au G nN comer Seren mre nein See ene ae eo ee eee mae ee io wna am | mie a mm Sena aa mi dm sc so San ee ete tg att teeta eat een naee cues te mn ame am as em eee eee ane ae on ogg ate ane ee eee Sm da aig ge caso am aang gig Sage egge cae gan ee ee ee Seng ag een Seg den / aug, mong) main maze ease mana a B=. S~ ; oom coms wins = Note: 1. Cureentratings ae vali for cables aid under defined conditions at page no. 94 For current ratings a deviated conditions apply correction factors as given on page no. 95-99 SS 28 Application: Suitable for indoor outdoor underground and in water for continuous permissible service vokage of n20/1200Voks: ‘Construction: 1 Anealed Coppr/Auminium Conductor 2 PVC sation 3. PVC nner Sheath 4 aly Stee Stip Amour. PVC outer sheath Colour: PHYSICAL DATA ELECTRICAL DATA GA GA GA GA Oem nok IM FM rim. | mm. MM. ghkm) ohnikm — ohmvkm | amps amps amps amps 30506 miné mim 12 0818 DOIG. 1434 OTDMMAS 20s TT0 «ws mins 10 bos pasei6 ming smim 12. jog 182832130. vane 052415 oaeenst 130 10128 mins 10 | os stds ming swim 14 $e08 193223060. 1608 O3HTOTRT eM 155 1D 50116 min 12 408 ‘goes | mm'i2_smim 14 | fos 2136129502176 o2ee0sM catanase’ 190 148190 a8 min 12 S08 yossa omnis smim 16 jaa 22-«410_ S110. 2775 avsuoaey ones 225 175-280-179 mine 14 S08 se20+70_ min 18S smiim 16 08-2544 gas0. 3323 oTSRONEE oISIOUD 260 202 270210 rnin 12 14 bos iso70 | mmis/is smi 14 | og 24 48373003723 arze026e ozmeosss! 295 20930527 rnin 12 14 | os sissTn30_ sim 20x08 «265855050. 5019 aosEVOINY o16tom0 330 257350272 mn. 1s 1s 08 ‘oon _min/i0_smim 22. fas 2858511100 S812 aorswoIsy eyase2s 363 299 41018 min 18s 16 S08 ‘sooiso min 3430. smim 24 faa 3068014400, OOP aowsyOI24 ejoDeR6. «25 329470 min 185 18 oa KEY eat » 08 . res seman wnste = Note: 1. Curtentratings are vali fr cables laid under defined conditions at page no. 94 For currentratings at deviated conditions apply correction factors as given on page no, 95-99 q 29 30 Application : Suitable for indoor outdoor underground and in water for continuous permissible service voltage of ‘720/1200Vels Construction: . Annealed Copper/Aluminium Conductor 2,PUCInsulation 3 PUClone Sheath 4. Gal Stel Sup Armour PVC outer sheath PHYSICAL DATA ELECTRICAL DATA — seo Se Se SIS ee ey uo. (mo too om | tm vom m6 ema Sa uae SS ee mem er 24 es See soa Soe See ee ee eee oy en nner Gio ntans im te HOE ak koto ay aise 8s ows To Se eg aan ee gs ee aay ot omen Saou az eqn azo comes mie mos se ee anon Ege aoa mg sg ae tag Meme mange ore a KEY B= ee is jo =~ — 8 1. Currentratings ae valid for cables laid under defined conditions at page no. 94 For current ratings at deviated conditions apply conection factors as given on page no. 95-99 Opps capies’ lication: Suitable or indoor outdoo underground and in wate for continuous permissible service voltage of 720/1200 Vo: ‘Construetion: J. Annealed Copper/ Aluminium Conductor 2. PVC Insulation 3,PVC inner sheath 4 Round Galy Stee ire armour 5.PYC outer sheath Colour dé PHYSICAL DATA forexmmy) M&M rm mam mm Agikm kg/km | ohm | ohm ampe | amps amps ampe 3a5 ming m 12 16 | 182851758 1376 am? 12008 385: ming sm | 12 | 16 | 18 | 278 | 2080 TaIS | o5ae ods 30 TNO 30 ming sm 14 | 18 | 20 | 307 2650 1658 0387 ous) | 1881201506 B00 mint sm 14) 20°) 21 | 346 3700 23620268 owes | 50 Taste SoS mint sm 16-20-22 3904759 2945018 as9 257s 9 5x20. min tS) sm M6 | 20-23 | 421 S660 33a | ass ass | 260 20227 | 210 SISO matais| sm | 18 25-25 473. 7265 aaa ia ame 8S BGS BT SxI85 min30_| sm 20-25-27 50S 660 S149 coos age 33025738022 52a ma3a30 sm 22-25-28 | 570 t0ei9 624s agysa —as2s 8S 259108 00 imin340 sm) 241251 34.) 61012998, 7208 | 9061000498. 328 ao a KEY ee, eo] oe 1 {Current ratings ae valid for cables lat under defined coneltions at page no. $4 For curent ratings at deviated conditions apply correction factors as given on page no. 95-99 31 Gaps canies: Application: Suitable for indoor ovtdoor underground andin water for continuous permissible service voltage of 72071200 Volt. 5 4320 5 452 Constructo sheath, PHYSICAL DATA 1. Annealed Copper / Aluminium Conductor 2. PVC Insultion 3. PVC inner sheath 4 Round Gal Stel wire armour S.PVC outer Coles GA) @ | NG | A | [arexme? Pos mmr mim mm | awn igikm kgm) vim ohm/im | amps | amps | amps | ams Busi6 mms mim 12 16 18 308 2010 1580 o7mNIS ms] No ask mins 1 basiié mime | smim 12 16 19 301 2445 1686. osautts omens 130 Tomo mins 1 250125 miné smi 14 20203353980. 24D a3e7ON? osHND 155 | 120 150116 mins 2 p70 | min'2 | smim 14-20 | 21 | «387 | 4310 2752 oasunsze o4evoase 190 | 148190148 rmin 2 ‘pesis0 minis | amim 18 20 23-23 S401 | 3480 ojeuusay one 20517508 mn 14 ‘20170 mmislis anim 16 25 | 25 480 7159 4438 ojsunaee ozsyomn 260 202-270-210 mina 14 2y050170 mnisis) gm 18 25 | 26 S12 aB47 sou jawoaee cross 295 229305287 mina 14 ews mn30._ mim. 20252736). yoo | sees oomuin olsyoa0 20287380 a mins i ‘UIO1120 min34/30 mim. 222529 623_y23Hs TOA oysWoIS3 a7250255 345299410318 mina 16 ‘yOWO1150 miNSA mm 24 «25-31 682 H5100. 8280 owovI2E esonDI.6 | 425 a9 470 min. 18/15, bad, 4 \ J 4 i KEY omy ger seein, 7 Deaton = 2: l= f- ° Note: 1. Current ratings are valid for cables laid under defined conditions at page no. 94 For current ratings a deviated conditions apply correction factors as given on page no. 95-99 SS 32 ‘Gaps canues: Application Suitable fr indoor, outdocr, underground and in water for continuous permissible service vokage of 720/1200Vols, 4 T T 5 43200 5 43200 ‘Construction: 1. Annealed Copper Aluminium Conductor 2.PVC insulation 3. PUCinner sheath 4. Round Gal. Stel wir armour S.PVC outer sheath, cotwe 9B PHYSICAL DATA ELECTRICAL DATA ee ee oie pesto interne oam KEY jn: S- LE ee = Note: 1. Current ratings are valid fr cables laid under defined conditions at page no. 94 For current ratings at deviated conditions apply correction factors as given on page no. 95-99 q 33 Application: Suitable for indoor, outdoor underground and in water for continuous permissible service voltage ‘of 720/1200Voks Construction: Annealed Copper Conductor 2.PVC Insulation & multi cores lai up 3.VC /PE Tapping 4 PYC outer sheath. Core identification: Numbering PHYSICAL & ELECTRICAL DATA sas W138 re os 126 206 18 a ms W138 re 08 us 238 6 2 lois | iss re os 164 si a 10 was | ns re os 168 399 2 5 Tels 38 re os ass 07 1 . ams Vi38 re os 203 a5 9 7 dons W138 re 08 na m 9 7 ions 138 re os 26 31 & 6 sos N78 re 08 142 239 m4 1s mas 78 re os is3 360 2 7 was 78 re os as 00 ie 13 mes 17 cs os 194 67 6 B Teas | 78 re os 23 m7 4 0 amas V8 re 08 Bs 520 B 10 deos yi78 re 08 264 1059 2 5 Soas 178 re 08 2s 1274 10 8 Set 7088 mm 19 168 202 31 % te 7085 m™ 19 12 see 7 2 Tot | 7oas mm 10 zr 708 B 1s Ba TRS m™ 19 24 37, 2 1. KEY Mm = es. §- B-- g-- Bees sts sje Gee oe oe Note 1. Current ratings are valid for cables lid under defined consltions at page no, 94, For curent ratings at deviated conditions apply conection factors as given on page no, 95.99 SS 34 Application: Suitable for indoor, outdoor underground anc in water for continuous permissible service voltage of 720/1200Vols Construction: 1. Annealed Copper Conductor 2. PVC Insulation 3, PVC inner sheath 4 Concentric copper conductor wth helically copper tape binder 5. PVC outer sheath Colour PHYSICALDATA ELECTRICAL DATA mm es - osm mm mm) mm | kgikm — ohm/km | amps; amps pasties mins rm 12 18 m3 1302 azaias “Mo 8 19/05, Basi16C mn sm 12 1s 22 162 oseaas 130 120 sens 5150425¢ mins sm 14 18 soa 2266 0387/0727. 155, 150 aoinos ygosasc minim 14 2 Ryan ozswosza) 190 190 asa 3x95}50C min.ts sm 16 22 see 4005 ons3/0387 as 230 sorts 3x120670C mint sm 16 2a 421 sos1 0153/0268 260 270 ron 34150700 min 18am 18 2s 4536013 01240268295 305 rons 5x185+95¢ min3o_ sm 20 26 501 7458 ass1/0193 330 330 emas y04001200 min. am 22 28 sss 9497 gu7swoisa 38s a0 sna 3x800/150¢ mings | sm 26 32 6131730. oosovor2s as 47 re) WEY whee 1. Current ratings ate valid fr cables aid under defined conditions at page no, 94 For current ratings at deviated conaltions apply correction factors as given on page no. 95.99 q 35 BS CABLES" il il Construction: 1. Annealed Copper /Aluminium Conductor 2.PVC Insulation 3 Two/Four cores laid up, cin 3 8S urexcames PaYSICAL 8 ELECT. DATA oo Saas ctaiad ad 4. Bretse 1a too Talat Arm/Are 7x0.85/2.26 1s 18 i agvagy 740741 = i mee ents uf 2 sama gaa smem | nivsmnios | te us 1ibenhmerosnj soot Aas et ory Orm/10rm | 7x1.35/7x1.35. 16 146 262 136 | 183/183 308/308 62 47 WG rem/IG rm! TNT TANTT 16 166 382 y80 | 1.1syi.tg_, 19V/i9t 84 6S Cosmas mune 16 2st onze 1202 yas Guaounexcasies PaYSICAL 8 LECT. DATA a ne ign ahah ae swirmtre,Passias te ho ma taial (anal BxGrmy6re | 7x105/277 154 | 352, 308/308 | 461/461 al Semom. masinies | te i ee eee siismvtom fesimtss | 18 Ue SB GSAB Goo) 8 Meme) RUMI | te xo [EEE Zasmatm jawe | t 3 BM leben ivi) |S Wey oe. (ioe 1. Curren ratings are valid fo cables lid under defined congitions at page no. 94 For current ratings at deviated coneltions NS apply correction factors as given on page no, 95-99 36 Application: Suitable for telecommunication and signal circus They are suitable for expose or concealed conduit Installation permissible voltage 200. Construct ‘Annealed Copper Conductor 2.PE Insulation & mult pai laid up 3, PT/PE Tapping 4. PVC outer sheath, Colour @O COO E Insulated PVC Sheathed Telecommunication Cables 1 air (2 cor) os oa 02 08 a2 22 2Pai(4core) ons vos 02 os 3 244 3 Pair (6 core) as oa 02 19 so 35 4Pai (Score) ons oa 02 2 66 sas Pair (10 core) ors oa 02 2 7 ar Par (2 core) ons oa 02 4 7 Bs 7Pair(4 core) ons oa 02 14 an a1 SPai()6core) | 0.125 vos 02 4 325 as WOPai0cor) 0.125 oa 02 4 985 108 1SPav(0cor) 0125 oa 02 4 nay var 2oPairdeore) 0125, oa 02 16 Ba as 30Pai(60core) 0125, oa 02 18 15.00 303 1 air (2 cor) 0282 vos 02 os 420 2S 2Pai(4core) 0282 vos 02 os 432 300 3 Pair (Score) 0282 wos 02 10 508 35 4Pai (Score) 0282 vos 02 2 680 655 Sair(10 core) 0282 vos 02 2 720 760 Pa (12 core) 0282 os 02 4 780 500 Pair (4 coe) 0282 vos 02 14 an 1035 Pair (16 core) 0282 vos 02 4 325 170 WOPair(20cord) | 0282 vos 02 14 565 v0 15a (0cor) 0282 os 02 14 i282 187 2oPair(oeore) 0282 vos 02 16 sas 7 30Pai(60core) 0282 vos 02 16 1677 358 soPair(topeotes) 0282 vos 2 is 2020 5350 100 aie 200cores): 0282 vos 02 16 2700 9420 SS —ee §- @22 Fo Ae, Curren ratings are valid for cables laid under defined coneltions at page no. 94 For current ratings at deviated conditions apply correction factors as given on page no, 95-99 37 38 BS CABLES" Application: Suitable for telecommunication and signal circuits. They are suitable for expose or concealed conduit installation permissible voltage 200, Construction: 1 Annealed Copper Conductor2.PEisuaion. Jumper Wire PHYSICAL DATA aime mm mm m 2eore( pa) ons ‘10132 o2 2 ‘ Seoretapa) ons 70132 3 2 2 Scores par ona 9012 02 as % Score(4 pain on smi 02 265 # oeore(span) 18 910.32 0 400 to PVC Insulated Drop Wire PE Insulated Drop Wire. PHYSICAL DATA PHYSICAL DATA velmm mmm gm ‘enn r Zeore( pa) vos 787 ats 80 eoe(ipal) oo o7s7 ania Deotelipad 09 108 630 SS) ewelipay os tos bas PE Insulated PVC Sheathed Co-Axial Cables Specification: Plain annealed copper conductor, polyethylene insulated with screen braided and PVC sheathed for use as aerial BT lepton ae apm Zs aces sgea ae ee mamn 2 BAA jonathan masta Z Sao a a ea oe Pe ee yo ms 2 oo @o ow om om om es sf Sonny deme pg oo oo ao a en BSc omit fata th fod appeal ited Seen ae ee re tae ares aaa maaan ease aes eee eee ee ee a Somber eset a a a Moonie ee we ee ae am ee gp KEY = fea f= S- = eo] moments 0) We Conet @ in Free ni os Norra are Note: 1. Current ratings are valid for cables lid under defined conditions at page no. 94, For current apply correction factors as given on page. 95-89, 195 at deviated conditions 45 Application: Suitable for indoor, outdoor underground and in water for continuous permissible service voltage ‘of 720/1200 lt. ee 4 22d 1. Anneald Copper/ Aluminium conductor 2.XLPE Insulation 3.PVC Inner sheath 4 Black PVC outer heath PHYSICAL DATA ELECTRICAL DATA See a an oon rear aces rmee soe Sa5I6 mine_smm | 0318 217/110 a7 aris iavisn yO m4 196 mae @ Soe mine aim 89 Ts HO wiz 72 osanis os@igt ss TM iso 17 mae 3 So mn im enna nz7o ams 6, owmr7 osina 0 a ie ie mae a3 30005 ma vm en tg 303 75) vot onansefownose 2s | Wt nD 18 ns a3 350 URS mim tt Wasa | 1555 orn oxen 200 | 196 270 | 21 ie to Sonam inlay inm 1222 M2 p12 98 oraz exmi04s 155 ws 05287 mina a 3osia mig rm Tz | 23 a2l gery | 234 01a azoo4s 30 29 350 292 mn a 30055 Rm ete 2s a3 as | an oom eNsoam ats at no. a7 ans i Sarno mao sv |i? 27 #4’ 219 940) oosmisausoa0. 5/327 7040 mnie 1 man3io sm 1a 29 | Sk6 143. 487 anovmre ovoanzoe aku _—seh_ ass imate i Key eee a ind SS Ben == f= fee Se i ee Oe wins ° = woe: {Current ratings ae valid for cables laid under defined conditions at page no. 94. For current ratings at deviated condltions apply correction factors as given on pageno 95-99 BBS CABLES* Application: Sutable for indoor outdoor underground and in water for continuous permissible servic vokage of ‘rronize0Vots as i 4 32 Construction: 1. Annealed Copper/ Aluminium conductor 2.XLPE insulation 3.PVC Inner sheath 4 Black PVC outer sheath, Colour: PHYSICAL DATA FLECTRICAL DATA Aw emexmm nos ar est eran etter cereal eel area ais vise m1 oa mio sis gost m 07 te) aa de mow 4as ee 0718188 280 yale 405 76h 2m 071814 ae a ae fw 7088 om 0718134 345 2a gs] a) we wa 46 | 704 om O78 | 168 ate 285 0H Tks a aio 735m 07 18182 ge kt RSD ais 77m | OF 8S 060 aS tS 8D 405 72i@ om 08188 ngs Sig za) 280k G 485 ming m= 0818S Re THES oases 41ST aso ming | sm 101973 ame 970. ass) aaah 90.1339 ta 470 mint? sm 1120 307 a07e 1250 02h ca |S toe 279 gS mints sm 1 | 21 | 358 406s eet 0193 032260196270 aia mintwis) sm | 12-23) 384 | S080 952 ois cas 8s ans as | 57 ariso_-mintais sm | 14 24 423. aos 2488 1M oes 33029350282 4185 "ming0 sm 1626 ABO 7974 3042 cose ate 8S 2 BIO ST 4am mingajso. sm 1728 $36 oni 3917 ays | 02s 28327470 +400 800, minga30. sm | 18) 300 $86 19508 4705.06) O10. S78 368) 564) 5S KEY = Hs Ma S- Be FoF incon @ cana a are FRR ome Note: 1. Current ratings are valid for cables lid under defined conditions at page no. 94, For current apply correction factors as given on pagena, 95-99 ings at deviated conditions 46 OBB cantes’ DOBBS CABLES lation: Suitable for indoor, outdoor underground and in water for continuous permissible service voltage ‘of 720/1200 Volt. =i 5 432 4 5 432 Construction: 1 Annealed Copper/ Aluminium conductor 2 XLPE Insulation 3 Round Aluminium wire Armour 4, PYC outer sheath, colour @ PHYSICAL DATA ELECTRICAL DATA corxmm nos) mm mm mm | mm kglkm _kgiken chr —ohmikm amps amps amps. amps Ings | ming m= 09) 128 18 73 5a7 70 as assist 195 150 1380 ming rm | 10128 18193) 720. 456 BHT eS 7s S180 tg mint? rm 1125 | 18 | 208 | 957 | 5500768 04s 210 500233 1x95 mint rm | 1 128 18 33 a ss oI oR HO MO as0. 272 pen minisis mm 12) 16 18 | 5S 1510790 0ns2 ss 350 ais txi50 mintWiS tm | 14) 16818 | OTS yes | 880 ork 2083802 357 twigs min30 rm 16 =| 1818285 aa NaHS oops lee 459350, 430 240 ming43O m7 | 16 | 19 | 323. D798 | T3B5. OOrSE | OS | SIS 40 498 19900 min3430 rm 181618 360 44g? 12S nee ad SHS ag 770 HT tao "mins8 rm =| «20,2021. 404 4491 | 2080 One? n77e «gad 509 90086 19500 mins) rm 2220-22436 $509 505 anne casas go «592 «1080788 1x60 mins3| rm | 24 | 20 | 23°, 472 | AO | 3100; oom OmHeDS4s 6961160 aS tygoominss rm 26 | 25 255403695 5a75 omer oms67 1095211310925 sto00, in 53 orm. 2828 27.589. gorse. | ar3s.)90i7e. onan sar. 952 1440. 1092, KEY = = = © a &. Bee He. - we Beene fee, [5] omens —_ a 1. Current ratings ae valid fo cables laid under defined conditions at page no, 94, For current ratings at deviated conditions apply correction factors as given on page no, 95-98 2. For compact conductors and lugs refer to page no. 108-109. Opps capies* DOBBS, CABLES’ ‘Application: Suitable for indoor, outdoor underground and in water for continuous permissible service voltage of F20/1200Voks. 5 4321 5 4321 1. Anmealed Copper / Aluminium conducor2XLPE insulation 3.P¥Cinner sheath 4. Gal Stee stp armour PVC outer sheath PHYSICAL DATA ELECTRICAL DATA coroner nos mmm. “gk AIK ohm amps ampe amp ampe 325 ming m gg 0818248 aT 1071 o7a 0130-9096 385 ming sm gg 0B | 18284157 117s ms 155 114 | aS0 117 bis0_ ming sm | 49 | 4x08 | (19-272 299 tay 0387 we 190 133 | 90a 30 | min sm | 1} | Ob | 20 | 304 2906 1690 0268 aS Tes 28078 3195 _mint5_ sm] 0821352. | 4136 208318 OD_—260—- 1962702 Sxi20 minig/'S sm 12 OS 22 «380 | Sons 2610. ISR ORss 285208405257 3x50 min8/15 sm 4 40H «2422 ray 2862 N24 0206 ~—«380—= «49350292 3x85 min30 sm tg | OS 25 | 460 7268 3398 OOH ON BAS 28D 410237 S240 min3430 sm 17 OS 27 STB 9588 4147 O07S8 ONS as 327450400 31300, min 3430 am ta Oe | 28.565 162). 4900/9060 S78 368 get ASS KEY OS Gee Mes S- Be Bex 195 at deviated conditions 1. Current ratings ae valid for cables laid under defined conditions at page no. 94, For current rat apply correction factors as given on page ne, 95-99 48 49 Opps caBies* Application: Suitable fr indoor, outdoor, underground and in water fr continuous permissible service voltage ‘of 720/1200 Vals, 5 432 0 Construction: |.Anneoied Copper /Aluminium candctor2XLPE insulation 3,PVC inner sheath 4. Gal, Steel strip armour 5. PC outer sheath, Colour sca ox PRISE SS Se Se NG ned ace Rae we taste | mine (mim! 09 | 408 | 14 | 259 (Yue (tp OTIS Inyist | | ot THD 56 me 7 save | nme. im 09 oa) Ta 277” om | 1236. osuss omen 55 | 1M 150 117 mn ssurs nt sm 12 408 19312 asis 7 omar oma 50 ime ms 3 sous md sum 408 20353. ym tem omense o«anss ms tw 018 we 0 3es50 mS nm bod UL M00 fet (ne ormany anen noe | ae an one to Se179 mens om 1208 2384 sr 286 ovsUAW omDHD Sm _—38__sT a ui esa |omidhs vm it | 80s. | 24 | 473 (yon (ams ormoae omenen m0 | 25 | 0 252 mnt? i sossss Immat_sum 18 408 26 527 7 noe comin ovum 305 22 m0 37 ms i sonra nmin! sum 17 408 28583 1m 410 comOID oRSUB BS m7? 4D mas B 3ono1s) mnii0|svm | Ib 808 | 29” 46402 (50s onsnay24 acon 78 sk eet pw 1 Key oer Seb ey Lense tea =. ee Pe. - vee ‘mare LS. . Note: 1. Current ratings are valid fr cables laid under defined condi apply correction factors as given on page no, 95-99 jons at page no. 94, For current ratings at deviated conditions BBS CABLES’ Application: Suitable fr indoor, outdoor, underground and in water for continuous permissible service volage (of 72/1200 Vals 5 43204 5 432 1 ‘Construction: -Anneoled Copper Aluminium conductor. XLPE Insulation 3.PVC ier sheath 4. Gali Stel strip armour 5 PVC outer sheath PHYSICAL DATA ELECTRICAL DATA So oC eC tus ming 09 agg M4253 ga) tas ary tee mt oe Sasa er ets meatal eon ageamona v SET comme mie age 20 ne ae te et be ia be le oo omeb om Ma at ase A amy ae) es dake Se ee yy ia ae a ee eae Gio emis) om 12a dee ee aie pds Be dos | ey Sis mits sm 14 os 35 75 fees gym. orm ome asd 282 Stas "mmo jm Me aan par gint aoe ooh eet gas gata bar Sie amliso sm 17 dog a3 sve ipna. Suir oot ss as ar ts0 400 Sb S240 LAL URAL LOLA AGO LoD HLOIOLETUTAN TB gata wey oat Pn oe ~ SM tansroe sg f= 22 f= w- eee se] mame — Note: 1. Current ratings are valid for cables laid under defined conditions at page no. 94, For current ratings at deviated conditions apply correction factors as given on pager, 95-99 50 51 Application: Suitable for indoor, outdoor underground and in water for continuous permissible service vokage of 720/1200Vols 5 432 KEY Me Mes SB I~ 3 1, Current ratings are valid for cables laid under defined conditions at page no, 94, For current ratings 3t deviated conditions apply correction factors as given on page no. 95-99 BBS CABLES* Application: Suitable for indoor, outdoor underground and in water for continuous permissible service voltage ‘of 720712000 ‘Construction: Annealed Copper /Aluminiu conductor 2.XLRE Insulation 3.PVCinner sheath 4 Round Gal Stel wie armour. PC outer sheath, cote 9S PHYSICAL DATA FLECTRICAL DATA SS SS Sry eee ee eee aS ao 8 DRE mn =e mR Se aot Se eos eo Seo Be Deter oleaelea hares Spon Seem sae aoe: eer ees eared ear oleae Seo SI cee eo ae ao Ee iegimee ees ano KEY OS Mee Bee. S~ -- Bee = Note: 1, Current ratings ae valid fo cables laid under defined conditions at page no. 94, For current ratings at deviated concitions apply correction factors as given on pagena 95-99 q 52 53 Application: Suitable fr indoor, outdoor, underground and in water fr continuous permissible service voltage of 720/1200Vols 1: Annealed Copper /Aluminium conductor 2.XLPE Insulation 3.PYCinner sheath 4 ound Gali Stel wire armour S.PVC outer sheath, coowr OS PHYSICAL DATA ELECTRICAL DATA eorex. mm mm mm TN Rgikm "kg/km ohm ohm/km amps” amps” amps” amps ans miné rm 083 18284 2038 | 1400 0727-1200 | 130-980 405 ming | sm | 09 | 16 | 19 | 294 | 2509 1622! 0524 ose 1551148150. 117 4x50 ming sm | 10 3g | 20: 338 4364 2096. 0387 ost 190133190 a2 4x70 mni2 sm | 44 | 20 | 22 | 389 | 4503 2720; a268 om 2S tgs 230179, 4x95 minis sm 1129.23 452 | gig8 3791 ots 03m 260196. 270221, 420 mings sm 122028 AB 780 aaa OSS 02S | 29S mE 30S 7 4050 minigiis sm «A526 S12. gate Soa 01m 0206 = 330 «249350 282 485 “ming0 sm) «18-25-28 | S75 10674 Sos comm Ol aS 2824107 424 min3a30 sm 172530 A 13362 7265 OOS 0182S 2749000 41900, min. 2490, sm 18 | 281 32 | 648 nenaea969 | aos) 0100.78 3684S KEY SY | ae Note: 1. Current ratings are valid fr cables laid under defined conditions at page no. 94, For current ratings at deviated conditions apply correction factors as given on page no, 95-99 Application: Suitable for indoor, outdoor underground and in water fr continuous permissible service voltage of 20/1200Vels, Construction: I.Anneoled Copper Conductor 2 XLPE Insulation & mult cores laid up 3. PVC/PE Tapping 4.PVCouter sheath. Core Identification: Numbering PHYSICAL & ELECTRICAL DATA ‘corexmm® nos mn =m mm kgm amps amps sos 13s re oy 18 ns v5 20 4 ms M38 re o7 1 a as ie a fons iss re a7 is 152 250 18 n Bas 38 re o7 18 157 235 1B 10 ies 38 re o7 18 168 410 2 5 as 138 re o7 18 190 525, 10 5 rons V138 re 07 te 20 600 10 : ions 138 re o7 8 no no 8 7 sas 178 re 7 is us 20 % 2 yas N78 re o7 7 37 2 2 19 jas | yi78 re 07 is am ae Fs 15 mas | 7 re o7 ry wa 460 ie 4 jos 78 re o7 is a2 570 15 2 amas V8 re 7 18 20 750 4 " paos N78 re o7 is BS 350 3 10 goes ie re 7 18 mas 1040) 1" 8 Se 7/085 m 07 1s us HS B z Teh 71085 m o7 18 160 23 2% 2% Joe 77oas mm 7 is 199 sus 2 2 Tat 70085 mm 07 4 205 se 2B 19. 1. Current ratings are valid for cable laid under defined conditions at page no, 94, For current ratings at deviated conditions apply correction factors as given on pager, 95.99 q 54 Applicaton: These cables are designed for emergency lighting, fire alarms and essential equipment in fre situations where an uniaterupted power supplyhas tobe guaranteed During fire, electric crcuits and the assocate lighting may be damaged. Power and data communications may be suspended. Human safety may depend on continued operation of Ighting, elevators and escalators fe fighting ater pumps, fire alarm and ventilation fans. The conductor is manufactured with a specially designed heat barrier ad fire resistant insulation wich resists the fre to reach conductor surface. The cable continues to rem into ‘operation at high temperatures ke 650°C, 750°C & 950% as per various conditions of operation and applications. Construction: 1. Annealed Copper/Aluminium Conductor 2. Mica Tape Syntheti/Glass over Conductor 3. Flame Retardant (FR) PVC Insulation 4, Flame Retardant (FR) PVC Sheath © othercolours available on request Coto PHYSICAL DATA ELECTRICAL DATA Gia aw a wl carexmim? nas /mm mm mm mm. kg/km “kg/m. ohmvkm ohmvkm amps amps amps. amps mS 38 e082 want 2 MS | 72 fom fos ta 78 ema 2 jes ee Ok 18 eS) 30 as | 768 om 0B ta 73 as 30 maa 78S orm 017168 10a) 8H 60 7/08 Fm 1D 1a 95 ase 2 308 ast Sa goat xo 7/135 om 0 18 tog 0013513308 ew ws 77m 1D Da tah TIS toe mas 72k 2 1a 132 390 0 oy esos 3S) oming om 12 1H; TBR; 486-270, 0528 ogee 1551206 ae 30 miné orm = tA TB | 156 | 652 3600387 antes tae 98ST tO |ominiz mm | 14 1B: ATT; B65 | at; 0268 | om ass as 0 fag5 minis sm 6 | 18 194 a0 $65 01830320 270210300282 W120 mintB/IS mm 18 1B DLT 1400 6B 0453 | 0283 310 | O80) eis0 = miniB/iS tm 5 | 18 23) 1726 84S Oz 0206 350,=« 2700S 18 Wigs | mind m=) -20,=| 20-256 | 2125 1002: ons ate | 390302 asd 37 2d minsa/30 rm 2220282714 1490 07S | 012s 850349 430 200 min34/30, m= 24 20 310. $342 1505! GOT | a100 SIS 386 a8 es00""minss mm =—-26~=«-22—=|«350 «4385 1947 O47 gu7TR | ses 42977040 ‘soo mins} tm =| 28 22 | 380 | $400 2548 00366 | 060s | G80 SID | 90010, re30 mins) orm = 2222 «ITS 2830. 00283 | 010009 BOD dD_——«T030| 728, ‘ws00mins3 rm = 28-24 489 R628 3400 00221 | cose? 945 | 7081160 |Z ywio0 | mins rm «30-26 S43 t0H00 63280176 G07s1 . 109s 2.08? KEY es. es / Se: Gee Bin. jes (me Qe 1, Current ratings ate val for cables ad in under defined conditions at page no. 94 For current ratings are deviated conditions apply correction factors as given on page no. 95-98 2, For compact conductors and lugs refer to page no 108-109. Z| 55 ‘OBBS CABLES" 3m: These cables are designed for emergency lighting, fre alarms and essential equipment in fre situations where an uninterrupted power supaly has tobe guaranteed, During fre, electric circuits and the associated ighting may be damaged. Powe and data communications may be suspended. Human safety may depend on continued operation of lighting, elevators and escalators, fre igntng ‘water pumps, fe alarm and ventilation fans. The conductor is manufactured with a specially designed heat batt and fre resstant insulation wich resists the fire to reach conductor surface The cable contines to remain into ‘operation at high temperatures lice SOC, 750°C & 950°C as per various candilions of operation and applications 4 3201 Construction: 1, Annealed Copper/Aluminium Conductor 2. Mica Tape Synthetic Glass over Conductor 3. XLPE insulation 4. Flame Retardant (FR) PVC Sheath Colour: @ _othercoloursavalableon equest PHYSICAL DATA ELECTRICAL DATA corexmen? _nosdmm ™ am Kgikm g/km ohevlen ohmvien amps amps? amps amos mis gee 1 8a wi 36 30 ws 7082 om | 07 1a 8 sof ar) te a6 30 yas IB eat Boss mm oa aw 38 a5 788m 1 sem nar 39 yao OBS rm 714 9 gas a a ee) ee i Wm ke at ee 6 wa 38 rm O71 66 i001 30k t00 |) mis | 7170 m7 1A BS Ms) te a0 tor Eas 7 yes 4 tm 8 T Be om =| oss 206s pas ming orm 0914 $31 220 ose one 1BS ae 195150 so ming m1 Ses 703” aah oas SS 190 wo mint? om M1 793 360 028 | ome 7010300285 95min 'S tm 1 as Woo 42 ais aaa) 302d; wo mintets| om 1215 1296 $67 01530283350 272s SIS iso mm ia/iS rm 4 18 Wir yoo aie aes 3002 asd miss min30 om 1818 1979 e4s | ome ase 450.3508 0 hot min3/30/ tm 7 17 | 256 3537 t068 | ons ons | 515 | 400 HO 088 300 /min3/30) rm |B 283 3140 13T0. aso aio seS aes 770 | S37 yxaoo mins} | rm 2) 1332 4137 | 1480 opm70 00mm | se S09 | 50026. S00 | miss m2) 2384 | 5T4Z_ oss | ames nso goo S82 toa | 731 x50 mins) | orm | 24 22398 SAB D565 0me3 0K S65 16D aod minS3 rm 26-23 4815 8355300 oma | omer | 105s) ga 1310 9a yxio00 _mins3 | rm =H 2483S 10450 3050. ao17S aaa _=—«127=S—«9S2_——akO «1068 KEY es, Eee:/Be. le: Bes. (Cfemare (meme Gm fee Note 1. Current ratings ae valid for cables lai in under defined conditions at page no.94,For current ratings are deviated conditions apply correction factors as given on page no. 95-99. IS 2, For compact conductors and lugs refer to page no. 108-108, 56 Applicaton: These cables are designed for emergency lighting, fre alarms and essential equipment in fre situations where an uninterupted power supply has tobe guaranteed During fre, electric crcuits and the assocated lighting may ae damaged. Power and data communications may be suspended, Human safety may depend on continued operation of ighting, elevators and escalators fe Fighting ‘ater pumps, fie alarm and ventilation fans Te conductor i manufactured with a specially designed heat barcer and fire resistant insulation wich resists the fire to reach conductor sueace. The cable continues to remain into ‘operation at high temperatures ke 650°C, 750°C & 950% as per various conditions of eperation and apalications. 5 e352) Construction: 1. Annealed Copper/Aluminium Conductor 2. Mica Tape Synthetic/Glass over Conductor 3. XLPE Insulation 4-Flame Retardant (R) PVC Inner Sheath 5. lame Retardant (FR) PVC Sheath Colour: PHYSICAL DATA ELECTRICAL DATA ‘exe nos mm mm. mm kg/km “kgixmahmvkm ohmvim "amps amp amp amps ais | vise |e | 07 | 18 13220 190 wre ae ais | msz om 0718 BSS wean nde ras wigs |e | 07 18 0S 7a) NaS das | 7ose fom 0718 az mo 7a a we as dee | dsm 0718 SS | Ge 80. ts] TNS ds | ibs rm O78 166 365 28D 308 ase yo 735m at t84 | aye 338! 183 3085s gS 26 7N7 | mT IB 205 Ga aes aS Eas ED | 70 das 7214 om | 08 1B; 242 | a9 S55. O727 1205088 2x55 Ming | mm | 09) 18 | 253. | tHo0 | 662! 0524 | ogee e014 190117 KEY Re. s/s. /fe: ¢ Bix. ese (me Gem ee Note: 1. Current ratings are valid for cables lad in under defined conditions at page no.94.For current ratings are deviated conditions apply correction factors as given on page no.95-98, 57 SS 58 Applicaton: These cables are designed for emergency lighting, fre alarms and essential equipment in fire situations where an uninterrupted power supply has tobe guaranteed, During fe, electric circuits and the associated lighting may be damaged. Power and data communications may be suspended. Human safety may depend on continued operation of lighting, elevators and excalatrs, fre fighting water pur, fie alam and ventilation fans, The conductor is manufactured witha specially designed heat barrier and fire resistant insulation wich resists the fie to reach conductor surface. The cable continues to remain nto ‘operation at igh temperatures like 650, 750°C & 950'C as per various condition of operation and apelications Cec eR cee! Construction: 1. Annealed Copper/Aluminium Conductor 2. Mica Tape SyntheticGlass over Conductor 3. XLPE Insulation 4. Flame Retardant (FR) PYC Inner Sheath 5 Flame Retardant (FR) PC Sheath colour @O@ PHYSICAL DATA ELECTRICAL DATA nossmm mm) mm mm “agikm kgikm’ ohmien ohm/km | amps amps amps amps eoexmm 138 re 07 B38 se ats SIS 752m 07 TBO a masta Bas V8 te 7 S46 20 7) ths 325 788m OF, 1B M9 ee Sat 525 708m O71 160350 56a) Be Ohm OF TR 7A aa IS Soest kaa BS 3S tm OT #92 see ek 30 770m | OF 1B NS | aos aos gtk Bis 7214 om | 08 B 285 160 67 oz? 12130208 325 ming | sm) 03 18 260 | tas | aos | se | ome ass |e 50) 17 Bos ming mT 8 | 265 (1950895 0387 Oss] 1901331902 S60 mint2 sm 1119, 302 2540 ti97 | ome ams 2s ee 30 | 179 30 minis sm 1 | 2 | 338 | 3210 1502 093 o3z 260196270 BSS min 8/5) sm) 12 237A ano 137 | nse 0258295 mas 4058257 3x20 MINIS sm 4 23 415 sap 2308 | ona | anne | 304950292 S80 min30 | gm 16 2A | 444 | g255 2740 mse tee aRS | 2a 410337 Sule min 3430/ am 1728502 gags 3525 onrst aus 2s 32770. a0 3240 min3430/ sm | 1B} 28 | 545 | 9900 4220 | oneor alo | 478 368 | Son 455 KEY e Ce /ee /Bie: Aes Be. Gjtaess (mene Gene fe eee 1. Current ratings are valid for cables laid in under defined condition at page no.94.For current ratings are deviated conditions apply correction factors a given on page n0.95-99. 2. For compact conductors and lugs refer to page no. 108-109. OBBS CABLES" in fre licaton: These cables are designed for emergency lighting, fre alarms and essential equipment situations where an uninterrupted power supply has tobe guaranteed During fre electric cicuts and the associated lighting may be damaged. Power and date communications may be suspended. Human safety may depend on continued operation of lighting, elevators and escalators, fe fighting ‘water pumps fire alarm and ventilation fans. The conductor is manufactured with a specially designed heat oarer land fre resistant insulation wich resists the fie to reach conductor surface. The cable continue: to remain into ‘operation at high temperatures like 650°, 750°C & 950°C as per varous conditions of operation and applications. mat Construction: 1 Aone ager Coder Mica Tape Synthetic/Gloss over Conductor 3 XLPE insulation 4 Flame Retardant (FR) PVC Inner Sheath 5. Flame Retardant FR) PVC Sheath 2 fi —a PHYSICAL DATA ELECTRICAL DATA aE nnn gk gin ini aaa range ang Sastis msm 038 «BB yn mr ammnis taal mm 36 mea o ose BRS smim 0318 S90 ow asMnIS | emmy is 1 ts) ns % soos MPS mim 118 837s 1e ooo? omnes im) mw a 03 mas mimia anim $1199 3055 stn Das ase De Tae 3 sist mrs anim tt 2) SA mp Tes apes omen 260. 198 70 2M Tie a m0 mnlans mim 12 22 408 5007 0 ays OND Sma ST a u snsoi nifans smim t+ 23-0 ipsa o1uone ono4n | 0 9 350192 van u srusiss Mihsp smim Ls 2s 4 ass 380 commer oman vem 407 mn u sarin nity sm IP 27 S47 5508S ovsmID amsem as BT a an min ans iB sessist MRBM3D smn Tf 28 608 117% s179 onmMIM vIn Te 368 sk_—S8 mens u see ea hee om eer (~~ Ble a, «/ es. (Ee: ES Bs Ble. Ges Gi le 1. Currentratings are valid fr cables laid in under defined conditions at page ne.94,For current ratings are deviated conditions apply correction factors as given on page no. 95-88 2. For compact conductors and lugs refer to page no. 108-109. 60 Applicaton: These cables are designed for emergency lighting, fre alarms and essential equipment in fire situations where an uninterrupted power supply has tebe guaranteed, During fre, electric circuits and the associated ighting may be damaged. Power and data communications may be suspended. Human safety may depend on continued operation of lighting, elevators and excalators, fre fighting water purnp, fire alarm and ventilation fans, The conductor is manufactured witha specially designed heat barrier and fire resistant insulation wich rests the fie to reach conductor surface The cable continue: to remain nto ‘operation at high temperatures like 650°C, 750°C & 950°C as per various condtions of operation and applications Construction: 1. Annealed Copper/Aluminium Conductor 2. Mica Tape Synthetic/Glass over Conductor 3. XLPE Insulation 4.Flame Retardant (FR) PVC Inner Sheath 5. Flame Retardant FR) PVC Sheath Colour @8O@ | phvsical bata LecTRICAL DATA SoM RE Be Ga bs ee Sone eth Po AROS A NB ee eh KEY eee, Ciee:/Ete.. Ble: rer B-~ Be is... peat: (mm (gro 1, Currentratings are valid for cables laid in under defined conditions at page no.94.For current ratings are deviated conditions apply correction factors as given on page no. 95-88. 2. For compact conductors and lugs refer to page no. 108-109. Applicaton: These cables are designed for emergency lighting, fie alarms and essential equipment in fre situations where an uninterrupted power supply has tobe guaranieed During fire, electric circuits and the assocated lighting may be damaged. Power and data communications may be suspended. Human safety may depend on continued operation of lighting, elevators and escalators, fre fighting ater pumps, fie alarm and ventilation fans. The conductor is manufactured with a specially designed heat barrier and fe resistant insulation wich resists the fre to reach conductor surface. The cable continues to remain into ‘operation at high temperatures like 650°, 750°C & 950°C as per various conditions of operation and applications. 6 aag20s Construction: 1. Annealed Copper Conductor 2. Mica Glass Fire Barter Tape over Conductor 3. Flame Retardant (FR) PYC Insulation 4.AlMyiar Tape Collective Shield 5. Solid Copper/ Tinned Copper Drain Wire 6. Flame Retardant Low Smoke (FRLS)/Low Smoke Halogen Free (LSHE) Outer Sheath cot ©@ oc rea ooo —— cee! a a a Seddon let: uu atogu warts eaten tS gedaan WEY eee. Eee / EES. Eee: Bes. Gem i Gem 61 LSHF / LSZH / LSOH PVC INSULATED LT CABLES ‘Gees cantes* LSHF Cables: Low Stoke Halogen free or Low Smoke Zero Halogen (LHF or LSZH or LSOH) isa material classification typicaly used for cable insulation & sheathing in the wire and cable industry. LSHF cable insulation & sheathing is composed of thermoplastic or thermoset compounds. When, these cables comes in contact with a lame very litle smoke is produced making ths product idea fr applications where many people are confined ina certain place Abbreviation LSHF Low Smoke Halogen Free isa Tow Smoke Zero Halogen [50H Tow Smoke Zero Halogen Application of SHF Cables LSHE cables are perfect for applic ns that require high performance and reliabilty while offering outstanding safety, soit canbe typically sed for Care Homes Shopping Malls School & College Hospitals & Clinics Public Bulngs Hotel ‘Old Age Homes ‘Airport Terminal Residential Compounds Gemas & Theaters Commercial Office ‘Garments factory buling Catton Spinning Mi Zate Spinning Mil Why use LSHF Cables? + Halogen Free Products Halogens are elements suchas fuorine, chlorine, bromine and lodine. Common cable insulation, such as PVC contains high amount of| halogens. The Cin PVC is corde, which isan ion of chlorine Halogens, under normal circumstances, are very stable and present no danger. Problem arises when they burn. A haloger-containng plastic can release hydrogen chloride, hydrogen fluoride and other dangerous gare: when bumed. When hydrogen chloride comes in contact with water, it forms hydrochloric acid, which i= also dangerous. + NoEmission of Toxic Gases Eliminates the threat of inhaling toxic gases which reducing the damage tothe human respiratory system. ‘+ Reduce the Smoke Emission tothe Minimum LSH Cables emit white smoke in place of black smoke. When PVC cables burn they give off thick black smoke. This obviously creates a major problem as it can obscure escape routes and signage, restricting safe evacuation of a bullding and increasing panic & increases suffocation. White smoke gives affected people better chance to evacuate ire place. + Resistant to ignition Tetakes much more time tha traditional cables to catch afr, which facitating the evacuation procedures ‘+ Reduces the Flame Propagation Its excellent flame retardant property prevents the fre from spreading through the place. + Easy totnstall LSHE sheath have alower coefficient of ition than some non-LSHF sheaths, which can make the able installation easier ‘+ Green, Safe and Healthy Itoffers the added benefit of being more environmentally-siendly, 62 ‘Applicaton: Electrical safety isa function of five characteristics viz. smoke, hazardous gas generation, rate of. neat release, lame spread and rate of burning. In case of fie ina close, rapped people are unable to fnd the ‘ext due to emission of thick black smoke and love consciousness due to the inhalation of toxic furnes before they can evacuated to safety. The advantage of low smoke and low acid gas generation are addtional and critical features avilable with LSHF / LSZH / LSOH wires in comparison with FR (Flame Resistant) wires wich do ‘not provide these properties, ‘Construction: 1 Annealed Copper/Aluminlum Conductor 2, SHF insulation 3 LHF Outer Sheath colour @ PHYSICAL DATA ELECTRICAL DATA ‘os Jmm ‘amps amps amps corexmm: 1/38 re O81 BBS a a1 no wis) 7082 om) OB 1B 6B SR tat ta es ms vim eR B28 oe tas | ross om O88 74 Tat Ea a8 a: yas asm 19182 105 os] 7a] AD Toe m7 gs 9 me ae swe soa eo 73s mB tp eames wo 77 | mm 1D 1B 107 F252 150s tT 0S wis 7eié om 12s A M3 dg 120s was ming om 12 1B; 137 24g 058 nse 155120160124 vas ming mA TB 1B gaat ase t8s ST SO ming m1 13 420 one OM USTs | S190 ty omnis mB 19 500193 032270 7103002 95min TBS) om 1S 1B 2 em) 1s cass Ho Mo a80. 27 tego mintgis) rm 1818231 | 709 7a 1m aay 350:« «270 | A018 W150 ming0 rm | 20 20256 | 2057 932 asst ate 350, 30246057 wie mina/s0, rm = 2220286 270g 1190 a7S 2S 4S]. SS ABD texto min34/30, rm 24 | 29313 Sans 1248 nso | an | SIS 386 | a0 ate goo mings rm 2622353. aad 1952 ON ogre Sas 439770 SAD telco | mings | rm | 28 22, «38D, 5436 2340 om366 00m | 6H SID: 900 83D ‘soo minS3_ rm 2822420 grad 270 m78 amisd 800001030721 W630 minSs rm 28 2A 462 asi 3195! mma | omnes 7081160 | IZ ‘e00 | mins3 | rm 3026 S14 40530. 3350. c076 ae) 1085 gz 1310.97 wey Note: 1. Current ratings ar valid for cables laid in under defined conditions at page no. 94. For current ratings are deviated conditions apply correction factors as given on page no. 95-99, IS 2. For compact conductors and lugs refer to page no. 108-108 63

You might also like