Panel Name:- Mounted: SURFACE

Size of
Size of Size of wire Feeder From :- Panel Location:- Size of
Conduit
Conduit (mm) (mm2) Cable (mm2)
Phase (R) Phase (Y) Phase (B) AMP Phase (R) Phase (Y) Phase (B) (mm)
Description PH AMP Trip BR No. R Y B BR No. AMP Frame AMP Trip PH Description
(Watt) (Watt) (Watt) Frame (Watt) (Watt) (Watt)
1 1 C 2 1
1 3 C 4 1
1 5 C 6 1
1 7 C 8 1
1 9 C 10 1
1 11 C 12 1
1 13 C 14 1
1 15 C 16 1
1 17 C 18 1
1 19 C 20 1
1 21 C 22 1
1 23 C 24 1
1 25 C 26 1
1 27 C 28 1
1 29 C 30 1
1 31 C 32 1
1 33 C 34 1
1 35 C 36 1
1 37 C 38 1
1 39 C 40 1
1 41 42 1
C
1 43 C 44 1
1 45 46 1
C
1 47 48 1
C
Sub-total 0 0 0 R Y B 0 0 0 Sub-total
connected load (KVA) 0.00 0.00 0.00 0.00 0.00 0.00 connected load (KVA)
Total Connected Load 0.00 Kwatt Total connected load "R" 0 Watt
Total connected load "Y" 0 Watt
Demand Factor "DF" 0.80 Total connected load "B" 0 Watt

Total Demand Load (KVA) = 0.00 Kwatt Panel Balance Check #DIV/0!

GENERAL NOTES FOR ALL PANELS:


1- All circuits feeding equipment located in wet areas to have earth leakage protection.
2- All external lighting panels to have photocell,contactor and timer with selector switch.
3- All lighting circuits that controlled by push buttons to have contactors.
4- All feeders that feed direct online motors to have motor type circuit breakers.
5- All outgoings for motors over than 7.5 HP to have starter.
6- All outgoings for lighting and sockets circuits shall be miniature type circuit breakers.
7- All circuit breakers exceed 800A to be Air circuit Breaker.
8- All outdoor panels are to be weather proof type minimum (IP65)
9-All local distribution panel board must be fed with moulded case circuit breaker .
10-All panel boards must have an indicating lamps .
11-Enclosure of all local distribution panel board must be IP42 and Form 2 .
12-All loads inside EXCEPT SOCKETS ( FLOOR BOX OR NORMAL SOCKETS ) OR LIGHTING LOADS this panel board are fed through CU/XLPE/PVC cable
Panel Name:- Mounted: SURFACE 400/230, APMse, -----------4W&G: BUS TRUNK ( -----)
Size of
Size of
Size of Cable (mm2) Feeder From :- Panel Location:- Main circuit breaker rating:- (--------) Size of Cable (mm2) Conduit
Conduit (mm)
Phase (R) Phase (Y) Phase (B) AMP Phase (R) Phase (Y) Phase (B) (mm)
Description PH AMP Trip BR No. R Y B BR No. AMP Frame AMP Trip PH Description
(Watt) (Watt) (Watt) Frame (Watt) (Watt) (Watt)
910 1 C 2
245 3 3 4 3
C
298 5 C 6
961 7 C 8
1506 3 9 10 3
C
2250 11 C 12
647 13 C 14
422 3 15 16 3
C
0 17 C 18
1250 19 C 20
2000 3 21 22 3
C
300 23 C 24
884 25 C 26
1500 3 27 28 3
C
1125 29 C 30
233 31 C 32
100 3 33 34 3
C
697 35 36
C
1000 37 C 38
0 3 39 40 3
C
1000 41 42
C
43 C 44
3 45 46 3
C
47 48
C
Sub-total 5885 5773 5670 R Y B 0 0 0 Sub-total
connected load (KVA) 5.89 5.77 5.67 0.00 0.00 0.00 connected load (KVA)
Total Connected Load 17.33 Kwatt Total connected load "R" 5885 Watt
Total connected load "Y" 5773 Watt
DEMAND FACTOR 0.80 Total connected load "B" 5670 Watt
DIVERSITY FACTOR 0.80
Total Demand Load (KVA) = 11.09 Kwatt Panel Balance Check BALANCED

GENERAL NOTES FOR ALL PANELS:


1- All circuits feeding equipment located in wet areas to have eAPMh leakage protection.
2- All external lighting panels to have photocell,contactor and timer with selector switch.
3- All lighting circuits that controlled by push buttons to have contactors.
4- All feeders that feed direct online motors to have motor type circuit breakers.
5- All outgoings for motors over than 7.5 HP to have stAPMer.
6- All outgoings for lighting and sockets circuits shall be miniature type circuit breakers.
7- All circuit breakers exceed 800A to be Air circuit Breaker.
8- All outdoor panels are to be weather proof type minimum (IP65)
9-All local distribution panel board must be fed with moulded case circuit breaker .
10-All panel boards must have an indicating lamps .
11-Enclosure of all local distribution panel board must be IP42 and Form 2 .