Contents
1 Introduction 1
1.1 Target Group 1
2 Product Overview 2
2.1 Main Features 2
2.2 BBS 6301 Overview 3
2.3 Configurations 5
3 Function Description 6
3.1 Power 7
3.2 Supervision and Control 8
3.3 Climate System 8
3.4 Installation Alternatives 12
4 Technical Data 14
4.1 Dimensions and Color 14
4.2 Space Requirements 15
4.3 Power 17
5 Environment 18
5.1 Operating Environment 18
5.2 Acoustic Data 18
6 Interfaces 19
6.1 Connection Interfaces 19
6.2 Indicators 22
7 Safety Approvals 24
Glossary 26
Reference List 27
1 Introduction
The BBS 6301 is an outdoor Battery Backup System (BBS) designed for the
RBS 6301 main-remote system.
P022167A
2 Product Overview
This section describes the main features and configurations of the BBS.
To a large extent, the BBS 6301 uses the same basic cabinet hardware as
the RBS 6301. This means the same visual appearance at site, but also
similarity in for example cabinet handling and installation, vandal protection,
and quality. The compact design and low weight simplifies transport to the
site and installation. It can be installed either on the ground, on a wall, or a
pole using the available installation kits. The BBS front door is supplied with
Ericsson's standard locking system.
The cabinet meets the requirements for installation in Earthquake Zone 4 and is
approved for operation throughout the world.
The thermoelectric climate system ensures long battery life by keeping the
well-insulated battery compartment in the mid 20C temperature range. The
optional heater will ensure that the batteries can deliver proper capacity even in
very cold areas.
Positio Description
n
J Battery cables
K Gas ventilation tube system
L Gas ventilation outlet
M Battery harness, belts
N Battery temperature sensor
O Climate temperature sensor
P Temperature sensor holder
Q Heaters (optional), one per battery shelf
R Service hatch
S Alarm Over-Voltage Protection (OVP)
T Climate unit drainage hose
U Surge Protection Device
2.3 Configurations
This section describes the BBS configurations.
P022248A
One or two BBS 6301 cabinets can be connected to each RBS 6301.
The dual-BBS configuration uses the extension kit, consisting of power cables
and a Surge Protection Device (SPD), to connect the battery strings in parallel.
3 Function Description
BBS 6301
Battery
To RBS temperature
sensor
-48V
Battery cables
to RBS 0V
-48V PCU-DC Battery circuit breaker
Battery cables
to extension 0V
Battery blocks
BBS
Battery circuit
breaker alarm
Door alarm
Alarm cable OVP Alarm
to RBS Climate unit
alarm Climate unit
Power supply
SCU alarm
SCU Climate
temperature
Climate unit -48V -48V
sensor
and SCU SPD
power supply 0V 0V
Optional heater
Optional heater
-48V -48V
To extension
BBS Additional SPD
0V 0V
P022165C
3.1 Power
The BBS 6301 is an outdoor BBS designed for the RBS 6301 main-remote
system.
The battery blocks are charged with 048 V DC from the RBS. The climate unit
and the SCU are fed with power from the RBS by a separate cable.
The battery cables are connected to the PCU-DC and the climate unit and the
SCU power cable is connected to the SPD.
For a list of approved battery types, battery dimensions, and battery weights,
refer to Spare Parts Catalog, Reference [7].
The battery blocks must be used with the battery accessory kit that is supplied
with the BBS cabinet, which includes front terminal adaptors, battery trays,
battery harness, and gas ventilation tubes.
8.0
7.0
6.0
Backup Time (h)
5.0
4.0
200 Ah
3.0
80 Ah
100 Ah
2.0
60 Ah
40 Ah
1.0
0.0
0.5 1.0 1.5 2.0 2.5 3.0 3.5
DC Load (kw)
P022164A
More information about batteries and battery handling can be found in the
document Battery Guidelines, Reference [3].
Charge and control of the battery blocks are performed by the RBS 6301.
Remote site management of the RBS and BBS network is possible through the
Ericsson Operation and Support System (OSS).
3.2.1 Alarms
The SCU in the BBS issues the following alarms to the RBS as external alarms:
The main BBS cabinet and the extension BBS cabinet are both connected to
the RBS by separate alarm cables.
The battery temperature sensor, attached to one of the battery blocks in the
main cabinet, monitors the battery temperature for battery charging. The
battery temperature sensor cable is connected to the Battery Fuse Unit (BFU)
in the RBS.
The climate temperature sensor monitors the cabinet inner temperature and
forwards the information to the SCU, which controls the climate unit.
The SCU supervises the climate system and regulates the temperature inside
the BBS using the active cooling unit and the optional heaters.
The TEC separates the interior climate from the exterior climate. It provides
the batteries with a room-temperature environment, which maximizes the
battery life.
The heaters, equipped with internal overheating protection, keep the battery
temperature within operating range as long as the outside temperature is not
below 033C.
The climate system and its control system operate at 048 V DC supplied by
the RBS. When AC mains power to the RBS is lost, the system voltage drops
and the climate system controller stops cooling and heating, to maximize the
battery backup time for the RBS.
During AC mains power failure, the cooling system, as well as the optional
heaters, are switched off to ensure maximum battery backup time for the
connected RBS. The internal fans continue to operate to ensure proper air
circulation around the battery blocks.
Table 4 and Table 5 specify the power consumption of the climate system
units per BBS cabinet.
Section 6.2 on page 22 describes the status indicators of the climate control
system.
Ge1560A
4 Technical Data
Figure 7 and Table 7 show the dimensions and weight of BBS and its installation
frames and brackets.
Height
Depth
Width
P022166B
Table 9 Weight
Unit Weight (kg)
BBS 6301 cabinet, excluding battery 70
blocks
(1)
Battery blocks 56 – 136
GBF 18.5
Installation frame back 17.3
Installation frame side 18.8
Air spacer 14.1
(1) Depending on battery type
The BBS must be installed straight with a maximum horizontal and vertical
offset of ±2 and not more than 1.5 m above ground level to fulfill earthquake
requirements.
The minimum and maximum distances between the units depend on the
connected cables.
Figure 8, Figure 9, and Table 11 show the space requirement for the BBS 6301.
100**
50* 50*
0*** 0***
700***
Ge1684A
P022249A
Drill patterns are found in the document Installing BBS 6301, Reference [1].
4.3 Power
The power data for the BBS is described in Table 12.
5 Environment
This section describes the requirement on the operating environment and the
environmental capabilities of the BBS 6301.
6 Interfaces
DC DC DC DC
SPD SPD SPD SPD
P022163C
6.1.1 PCU-DC
The external battery power cables (35–95 mm2) are connected to the PCU-DC
screw terminal.
6.1.2 SPD
The shielded climate unit and SCU power cable (10 mm2) are connected to the
SPD power connector. The supplied connector is fitted to the cable on site.
A BBS main unit SPD, a chassis connector, and connection cables required for
the extension are supplied with the extension BBS.
6.1.4 Grounding
The grounding bolt is placed in the bottom of the cabinet as shown in Figure 11,
and each BBS is connected to the Main Earthing Terminal (MET) at the site.
Socket 13 mm
24 Nm
Ge1568A
More information about site grounding can be found in the document Grounding
Guidelines, Reference [4].
External alarms from the BBS are transmitted through the external alarm
outputs (OVP A1–A4) and a digital alarm output (EC; currently not used).
The BBS external alarms are related to the SCU alarm indicators and
transmitted as shown in Table 15.
6.2 Indicators
The SCU is equipped with the following indicators, as shown in Figure 12 and
Table 16.
SCU 04 01
Power in
Temp sensor fault Heater fault
Operational
Heater Fuse
Light Door A B sense
Fault
Alarm out EC
Power out
TEC DAC
P022240A
7 Safety Approvals
Safety
• IEC 60 950-22:2005
• EN 60 950-1:2006 Ed. 2
• EN 60 950-22:2006/A11:2008
Approval
• CE
• CB
• ETL
EMC
• ICEC-003
• CISPR 22
Enclosure
• IP 55
Earthquake
Glossary
AC
Alternating Current
BBS
Battery Backup System
BFU
Battery Fuse Unit
CB
Circuit Breaker
DC
Direct Current
GBF
Generic Base Frame
MET
Main Earthing Terminal
OSS
Operation and Support System
OVP
Over-Voltage Protection
PCU-DC
Power Connection Unit DC
RBS
Radio Base Station
RRU
Remote Radio Unit
SCU
Support Control Unit
SPD
Surge Protection Device
TEC
Thermo-Electric Cooler
Reference List