Thread Starter #1
A Abdul Karim
Today at 5:11 AM
Hi Gents,
I seek your support in understanding and rectifying issues related to secondary flame scanners on GE Make 7EA
Gas Turbines- Machines Installed in KSA, Cogeneration plant, ambient condition high temperatures, and less
humidity. 04 UV water-cooled secondary flame scanners have a history of the issue initially with primary flame
scanners showing less intensity and later with secondary flame scanners intensity issue. Recently, we changed
problematic flame scanners 7S & 8S and cleaned the remaining 3S & 4S, tested their intensity above 90 %. After
completion of Hot Gas path inspection, once we started the machine, before DLN (DLN-1 machine) mode
transfer, secondary and primary flame scanners showed normal behavior, however, once mode transfer
happened, Flame scanners 3S & 4S drastically changed from around 50 % each to 0 & 8 % respectively.
Note that we had just prior to startup performed rinsing of the machine, however, note that our same capacity
machine has no such issues reported.
Like Reply
ControlsGuy25 #2
Today at 6:04 AM
Hi Gents,
I seek your support in understanding and rectifying issues related to secondary flame scanners on GE Make 7EA Gas
Turbines- Machines Installed in KSA, Cogeneration plant, ambient condition high temperatures, and less humidity. 04 UV
water-cooled secondary flame scanners have a history of the issue initially with primary flame scanners showing less
intensity and later with secondary flame scanners intensity issue. Recently, we changed problematic flame scanners 7S &
Click to above
8S and cleaned the remaining 3S & 4S, tested their intensity expand...
90 %. After completion of Hot Gas path inspection,
Hi Abdul Karim,
I strongly suggest you to have a read, on this very useful and excellent thread posted in this excellent
control.com forum:
https://control.com/forums/threads/ge-9e-dln1-secondary-flame-trouble.43322/
The issue was on a frame 9E but it can give you some tips advices for getting a solution at site.
Abdul Karim
Like Reply
ControlsGuy25 #3
Today at 6:47 AM
ControlsGuy25 said:
Hi Abdul Karim,
I strongly suggest you to have a read, on this very useful and excellent thread posted in this excellent control.com forum:
https://control.com/forums/threads/ge-9e-dln1-secondary-flame-trouble.43322/
The issue was on a frame 9E but it can give you some tips advices for getting a solution at site.
Click to expand...
So you get a read and found the post that I shared interesting Hum!!
Controls Guy25.
Abdul Karim
Like Reply
Thread Starter #4
A Abdul Karim
Today at 6:51 AM
ControlsGuy25 thankyou for comment-Can i get "Secondary Flame Detector Warm up System." document, if
you posses.
ControlsGuy25
Like Reply
ControlsGuy25 #5
Today at 6:55 AM
ControlsGuy25 thankyou for comment-Can i get "Secondary Flame Detector Warm up System." document, if you posses.
Abdul Karim
I am also looking for such document and looks like Drive link on this post is "dead".
You right to ask Adel S but FEFO shared a drive link with , you may ask him for getting it.
ControlsGuy25.
Like Reply
ControlsGuy25 #6
Today at 6:59 AM
ControlsGuy25 said:
Abdul Karim
I am also looking for such document and looks like Drive link on this post is "dead".
You right to ask Adel S but FEFO shared a drive link with , you may ask him for getting it.
Click to expand...
Looks like Adel S & FEFO are more posting/in activity on this forum.
Let check on the world wide web if there is kind of document.
Like Reply
Power
D Tuning Issue After CI on Frame 7EA DLN 0 Oct 7, 2019
Generation
Power
B Auto-Synchronizing GE Frame 7EA 8 Oct 2, 2014
Generation
Power
S GE Frame 7EA Loss of Flame/TripOil 11 May 7, 2013
Generation
Power
J Frame 7EA High Gas Flow 2 May 31, 2012
Generation
Y O U M AY ALSO L IK E
Networking Military/Aerospace
Sensors Utilities
© EETech Media, LLC. All rights reserved Privacy Policy · User Agreement