You are on page 1of 5

Building parameters:

1 Length of the As per Architectural Drawing


building
2 Width of the building As per Architectural Drawing
3 Building height As per Architectural Drawing
4 Roof slope Flat
5 Importance factor, I 1.0

The above Floor system has been Designed under the following Loads, Specifications and
Codes:

Design loads: Floor system in this job are designed for the following loads:

Design dead load on floor for 125 mm casting with floor finish 3.6 kN/m2
Design dead load on floor for partition wall 1 kN/m2
Design live load on floor 3.0 kN/m2
Wind speed 58.33 m/s
Wind exposure A

Load cases

1. EX & EX-, EZ & EZ-: Eartquake load from positive & negative X & Z-direction
respectively.

2. WX & WX-, WZ & WZ-: Wind load from positive & negative X & Z-direction respectively.

3. DL: Dead load with self weight of members and other superimposed Dead loads.

4. LL: Live load


Design Load combination: As per BNBC’2006

1. DL
2. DL+LL
3. DL + EX+
4. DL + EX-
5. DL + EZ+
6. DL + EZ-
7. 0.9 DL + EX+
8. 0.9 DL + EX-
9. 0.9 DL + EZ+
10. 0.9 DL + EZ-
11. 0.75 (DL + LL + EX+)
12. 0.75 (DL + LL + EX-)
13. 0.75 (DL + LL + EZ+)
14. 0.75 (DL + LL + EZ-)
15. DL + WX+
16. DL + WX-
17. DL + WZ+
18. DL + WZ-
19. 0.9 DL + WX+
20. 0.9 DL + WX-
21. 0.9 DL + WZ+
22. 0.9 DL + WZ-
23. 0.75 (DL + LL + WX+)
24. 0.75 (DL + LL + WX-)
25. 0.75 (DL + LL + WZ+)
26. 0.75 (DL + LL + WZ-)
Material Specifications
Below are BBS standard material specifications that will be used in the project. BBS reserves the right
to make material substitutions and changes in specifications as and when deemed necessary.
No. Components Specifications Strength
1 Built-up ASTM A572M /SS 400/Q345B Grade 345 Fy = 34.5 kN/cm2
Type1 ASTM A370
Tubes/Pipes JIS - G 3466 – STKR 490 Fy = 32.5 kN/cm2
2 Hot Rolled
Channels EN - 10025 S355JR Fy = 35.5 kN/cm2
3 Cold Formed ASTM A607/SS 400 Grade 40 Fy = 27.6 kN/cm2
JIS - G 3131 SPHC Fy = 27.6 kN/cm2
JIS - G 3132 SPHC

4 Wall, Roof & Liner Panel ASTM A792M Grade 345B: Coating AZ150/ Fy = 34.5 kN/cm2
ASTM A792M CS-B AZM150G/M2/
ASTM A792M Grade 50, PREPAINTED Al-Zn/
ALLOY-COATED
ASTM A653M SS Grade 345 Class 1: AZ Fy = 34.5 kN/cm2
5 Mezzanine Deck Panel Coating
ASTM A792 AZ150G/M2 AFP
Rods ASTM A615M Grade 420 Fu = 124 kN/cm2
Angles JIS - G 3101 - SS 400 Fu = 40.2 kN/cm2
6 X-Bracing
Cable ASTM – Fy = 119.7 kN/cm2
- Extra High Strength Class A Pu= 90 KN
7 Anchor Bolts ASTM A370 Fy = 27.6 kN/cm2[Dia
JIS G3101 – SS 400 >30 mm]
Fy = 24.84 kN/cm2
[Dia <= 30mm]
8 High Strength Bolts A325 M Type 1 Hot Dip Galvanized FU = 82.7 kN/cm2
DIN 933 Class 8.8 Zinc coated
9 Sag Rods ASTM A 36 M or DIN 933 Grade 4.6 Fy= 25.0 kN/cm2
Fy= Yield Strength ; Ft = Allowable Tensile Stress ; Fu= Ultimate Tensile Strength ;
Pu = Minimum Breaking Load.

Applicable codes: All buildings included in this proposal are designed in accordance with the
following codes that dictate the design and manufacture of pre-engineered steel buildings.
Loads on all buildings are applied in accordance with
1 International Building Code: 2006
International Code Council Inc. (ICC)
5203 Leesburg pike, Suit No 600, Falls Church, VA-22041
2 Bangladesh National Building Code (BNBC): 2006
3 ASCE-7-05
4 The 1996 edition of the Low Rise Buildings Manual
Metal Building Manufacturers Association Inc. (MBMA)
1300 Summer Avenue, Cleveland, Ohio 44115, USA

Build-up Sections are designed in accordance with


1 2005 Manual of Steel Construction – Allowable Stress Design
American Institute of Steel Construction Inc. (AISC)
1 East Wacker Drive, Suite 3100, Chicago, Illinois 60601-2001, USA
2 AISC (360-05): LRFD Manual of Steel Construction (3rd Edition)
American Institute of Steel Construction Inc., Chicago, IL

Cold Formed Sections are designed in accordance with


1 2003 Edition of Cold Formed Steel design Manual
American Iron and Steel Institute (AISI)
1000 16th Street, NW, Washington, DC 20036, USA

Welding is applied in accordance with


1 2006 American Welding Society (AWS D.1.1.96)
Structural Welding Code - Steel Manual
550 NW Jejune Road, Miami, FL 33126, USA

Bolt Strength:
Allowable capacity of Anchor Bolt

Tension capacity: 0.375 Fu Ab


Shear capacity: 0.2 Fu Ab

ASTM A36
Bolt Fy 248.2 Fu 400
dia (MPa) (MPa)
(mm) Fy (ksi) 35.989 Fu (ksi) 58
Tension (kN) Shear (kN)
20 47.14 25.14
25 73.66 39.29

Allowable capacity of Chemical Bolt

HILTI: HAS-(E) 8.8


Bolt Fy 640 Fu 800
dia (MPa) (MPa)
(mm) Tension (kN) Shear (kN)
M20 80 66

Allowable capacity of Connection Bolt

Ultimate tensile strength, Fut 827 Mpa


Nominal tensile strength, Fnt 620 Mpa
Nominal shear strength, Fnv 331 Mpa

Tension capacity: 0.5 Fnt Ab


Shear capacity: 0.5 Fnv Ab

Bolt dia (mm) ASTM A325/ DIN 933 Grade 8.8


Tension Single shear (kN) Double shear
(kN) (kN)
12 35.07 18.73 37.46
16 62.35 33.29 66.58
20 97.43 52.01 104.02
24 140.3 74.9 149.8
30 191.81 102.4 204.8