sinamics S120 cable length


Created by: honganh4790 at: 5/14/2019 9:10 AM (3 Replies)
Rating (0)
Thanks 2

Actions New post

4 Entries

5/14/2019 9:10 AM Rate (0)


honganh4790 Hi everyone,

im building a system using sinamics S120 to control speed for tension motor . can
i use power cables without shield?
And one more thing, i read in sinamic s120 module datasheet they wrote :
Max. motor cable lenght:

Shielded100 m (328 ft)


Advanced Member
Unshielded 150 m (492 ft)
can someone explain to me why maximum length of cable with shield is shorter
then unshield? i think cable with shield is better than without shield.
Joined: 1/5/2016
Last visit: 5/12/2020
Posts: 38
Rating:

(0)

Suggestion To thank Answer Quote

5/14/2019 10:47 AM Rate (0)


Technology Team Hello,

the inverter is using fast switching power semiconductors, providing a PWM


voltage output to the drive. The capacity of the motor cable is higher for shielded
cables and as this capacity is charged / discharged with the puls frequency of the
drive, it causes additional leakage currents, the inverter must provide.

As the inverter has some limits for the current it can provide, the possible capacity
of the cable is limited and so the length is shorter with shielded cables.
Platinum Expert

Joined: 10/11/2006
Last visit: 8/5/2020
Posts: 4353
Rating: With best regards,

(518) Technology Team

Application consulting and pre sales support for SINAMICS, SIMATIC Technology,
SIMOTION, SIMOTICS and MOTION CONNECT

Suggestion To thank Answer Quote


This contribution was helpful to
PISCEAN 2010 RB91

5/15/2019 2:57 AM Rate (0)

https://support.industry.siemens.com/tf/ww/en/posts/sinamics-s120-cable-length/213346?page=0&pageSize=10 1/2
8/6/2020 sinamics S120 cable length - Entries - Forum - Industry Support - Siemens
5/15/2019 2:57 AM Rate (0)
honganh4790 Thank so much for your answer.

So can i use cable without shielded for s120 ? maximum length is about 120m.
Because of we are have spare cable without shield,so we are considerring to use
it for saving the cost . but i really worrry about the inverter will be damage if we
using it
Technology Team

Hello,
Advanced Member
the inverter is using fast switching power semiconductors, providing a PWM
voltage output to the drive. The capacity of the motor cable is higher for
shielded cables and as this capacity is charged / discharged with the puls
Joined: 1/5/2016 frequency of the drive, it causes additional leakage currents, the inverter
Last visit: 5/12/2020 must provide.
Posts: 38 As the inverter has some limits for the current it can provide, the possible
Rating: capacity of the cable is limited and so the length is shorter with shielded
cables.
(0)

Suggestion To thank Answer Quote

5/15/2019 8:51 AM Rate (0)


Technology Team Hello,

unshielded cables will not damage the inverter, but please take into account, that
the EMC category may not be fulfilled with unshielded cables.

Depending on the size of your Motor Module, oversizing would also allow 120 m
shielded cable. See extract from the catalogue.

Attachment
Platinum Expert Cable length S120.jpg (63 Downloads)

Joined: 10/11/2006
Last visit: 8/5/2020
Posts: 4353
Rating:

(518) With best regards,

Technology Team

Application consulting and pre sales support for SINAMICS, SIMATIC Technology,
SIMOTION, SIMOTICS and MOTION CONNECT

Suggestion To thank Answer Quote