ECG DB / PANELBOARD SCHEDULE Proj.

No 1658
According to IEC & Master Spec REV.(0)
NOTE
PANEL NO.: EMDB-2 LOCATION : Basement Floor Notes: 1,4,6,12,13,14 1- A.CB' s required 6- TVSS required 10- ELCB, 100 mA required

2- Isolated Earth Bus 7- Contactor and PB 11- ELCB, 30 mA required


Mains SHEET 1 OF 2 Rating Duty Enclosure Dimensions
Fed From : TR.4 Main C.B.: 2,000 A 380 / 220 V SURFACE W mm 3- 200% neutral size 8- Photocell and Timer 12- over&under voltage
Cable No. : F-EMDB-2 (SEC-2) << TCL : 1137 kW 8 kA-symm. IP42 D mm 4- Indicating Lamps 9- Two-Section Panel 13- Shunt trip
Cable size: 5 // ( 4 x 240 ) mm2 Max.Dem.: 764 kW 17 kA-peak Form 2 H mm 5-Contactor connected to BMS 14- Metering
SER NO. CCT C.B. WIRE ECC CONNECTED LOAD - No.of points per circuit unit CONNECTED LOAD
N
O 1P-C.B.'s REF SIZE SIZE No. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 Load PER - PHASE
T
ROOM / AREA / SUB PANEL / LOAD DISCRIP.
OR # TL CL/ HID Sing Twin Pwr 3 ph Mot/ W.B/ wind split VAV- @ R Y B
E
WAYS NO. A mm2 mm2 Ltg Exit Ltg S/O S/O S/O S/O Fan HD EWH H.P A/C A/C FCU kW kW kW kW
1 R1 97.3
2 Y1 630 2//185 185 ESMDB-S . 108.83 49.00 0.00 131.00 288.83 95.7
3 B1 95.8
4 R2 42.3
5 Y2 320 185 95 EMCC-B . 0.00 0.00 0.00 127.00 127.00 42.3
6 B2 42.3
7 R3 72.3
8 Y3 400 240 120 EDB-S-A/C 0.00 0.00 0.00 217.00 217.00 72.3
9 B3 72.3
10 R4 36.7
11 Y4 320 185 95 PET-SCAN . 0.00 0.00 0.00 110.00 110.00 36.7
12 B4 36.7
13 R5 15.0
14 Y5 125 120 70 COOLING TOWER 0.00 0.00 0.00 45.00 45.00 15.0
15 B5 15.0
16 R6 15.0
17 Y6 125 120 70 COOLING TOWER 0.00 0.00 0.00 45.00 45.00 15.0
18 B6 15.0
19 R7 68.4
20 Y7 630 2//185 185 UPS-S . 0.00 203.70 0.00 0.00 203.70 68.2
21 B7 67.1
22 R8 33.3
23 Y8 250 185 95 CATH LAB 0.00 0.00 0.00 100.00 100.00 33.3
24 B8 33.3
Dem. Factor ( DF ) Application SUB - 380.4 378.6 377.6
first 100 Kw next 200 Kw remaining Ltg Power Heating A/C TOTAL 1137
Lighting 0.9 0.8 0.7 TCL ( kW ) 108.83 252.70 0.00 775.00 1137 kilo-Watts
Power 0.7 0.6 0.5 -------- >> MD ( kW ) 97.06 161.62 0.00 505.00 764
Heating 0.6 0.6 0.55 Result. Dem. Factor 0.89 0.64 #DIV/0! 0.65 0.672
A/C 0.8 0.7 0.6
ECG DB / PANELBOARD SCHEDULE Proj.No 1658
According to IEC & Master Spec REV.(0)
NOTE
PANEL NO.: EMDB-2 LOCATION : Basement Floor Notes: 1,4,6,12,13,14 1- A.CB' s required 6- TVSS required 10- ELCB, 100 mA required

2- Isolated Earth Bus 7- Contactor and PB 11- ELCB, 30 mA required


Mains SHEET 2 OF 2 Rating Duty Enclosure Dimensions
Fed From : TR.4 Main C.B.: 2,000 A 380 / 220 V SURFACE W mm 3- 200% neutral size 8- Photocell and Timer 12- over&under voltage
Cable No. : F-EMDB-2 (SEC-2) << TCL : 1237 kW 8 kA-symm. IP42 D mm 4- Indicating Lamps 9- Two-Section Panel 13- Shunt trip
Cable size: 5 // ( 4 x 240 ) mm2 Max.Dem.: 824 kW 17 kA-peak Form 2 H mm 5-Contactor connected to BMS 14- Metering
SER NO. CCT C.B. WIRE ECC CONNECTED LOAD - No.of points per circuit unit CONNECTED LOAD
N
O 1P-C.B.'s REF SIZE SIZE No. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 Load PER - PHASE
T
ROOM / AREA / SUB PANEL / LOAD DISCRIP.
OR # TL CL/ HID Sing Twin Pwr 3 ph Mot/ W.B/ wind split VAV- @ R Y B
E
WAYS NO. A mm2 mm2 Ltg Exit Ltg S/O S/O S/O S/O Fan HD EWH H.P A/C A/C FCU kW kW kW kW
25 R9 33.3
26 Y9 250 185 95 CATH LAB 0.00 0.00 0.00 100.00 100.00 33.3
27 B9 33.3
28 R10
29 Y10 400 SPARE
30 B10
31 R11
32 Y11 250 SPARE
33 B11
34 R12
35 Y12 125 SPARE
36 B12
37 R13
38 Y13 630 UPS-S
39 B13
40 R14
41 Y14
42 B14
43 R15
44 Y15
45 B15
46 R16
47 Y16
48 B16
Dem. Factor ( DF ) Application SUB - 413.7 411.9 410.9
first 100 Kw next 200 Kw remaining Ltg Power Heating A/C TOTAL 1237
Lighting 0.9 0.8 0.7 TCL ( kW ) 108.830 252.70 0.00 875.00 1237 kilo-Watts
Power 0.7 0.6 0.5 -------- >> MD ( kW ) 97.06 161.62 0.00 565.00 824
Heating 0.6 0.6 0.55 Result. Dem. Factor 0.89 0.64 #DIV/0! 0.65 0.666
A/C 0.8 0.7 0.6
ECG DB / PANELBOARD SCHEDULE Proj.No 1658
According to IEC & Master Spec REV.(0)
NOTE
PANEL NO.: EDB-S-A/C LOCATION : Basement Floor Notes: 1,12,4 1- MCCB' s required 6- Led Dimmer Control 10- ELCB, 100 mA required
7- Contactor and PB
2- Isolated Earth Bus 11- ELCB, 30 mA required
Mains Rating Duty Enclosure Dimensions connected to BMS
Fed From : EMDB-2 (SEC-2) Main C.B.: 400 A 380 / 220 V SURFACE W mm 3- 200% neutral size 8- Photocell and Timer 12- over&under voltage
Cable No. : F-EDB-S-A C << TCL : 217 kW 19 kA-symm. IP42 D mm 4- Indicating Lamps 9- Two-Section Panel 13- Shunt trip
Cable size: 1 // ( 4 x 240 ) mm2 Max.Dem.: 161.9 kW 39 kA-peak Form 2 H mm 5-Connected to BMS via lighting control system 14- Metering
SER NO.CCT C.B. WIRE ECC CONNECTED LOAD - No.of points per circuit unit CONNECTED LOAD
N
O 1P-C.B.'sREF SIZE SIZE No. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 Load PER - PHASE
T
ROOM / AREA / SUB PANEL / LOAD DISCRIP.
OR # TL CL/ HID Sing Twin Pwr 3 ph Mot/ W.B/ wind split VAV- @ R Y B
E
WAYS NO. A mm2 mm2 Ltg Exit Ltg S/O S/O S/O S/O Fan HD EWH H.P A/C A/C FCU kW kW kW kW
1 R1 13.7
2 Y1 100 50 25 EMCC-F 0.00 0.00 0.00 41.00 41.00 13.7
3 B1 13.7
4 R2 33.3
5 Y2 100 120 70 EMCC-M7 0.00 0.00 0.00 100.00 100.00 33.3
6 B2 33.3
7 R3 6.3
8 Y3 63 16 16 ELEV.1 0.00 0.00 0.00 19.00 19.00 6.3
9 B3 6.3
10 R4 6.3
11 Y4 63 16 16 ELEV.3 0.00 0.00 0.00 19.00 19.00 6.3
12 B4 6.3
13 R5 6.3
14 Y5 63 16 16 ELEV.4 0.00 0.00 0.00 19.00 19.00 6.3
15 B5 6.3
16 R6 6.3
17 Y6 63 16 16 ELEV.6 0.00 0.00 0.00 19.00 19.00 6.3
18 B6 6.3
19 R7
20 Y7 63 SPARE
21 B7
22 R8
23 Y8 63 SPARE
24 B8
Dem. Factor ( DF ) Application SUB - 72.3 72.3 72.3
first 100 Kw next 200 Kw remaining Ltg Power Heating A/C TOTAL 217
Lighting 0.9 0.8 0.7 TCL ( kW ) 0 0.00 0.00 217.00 217 kilo-Watts
Power 0.7 0.6 0.5 -------- >> MD ( kW ) 0.00 0.00 0.00 161.90 162
Heating 0.6 0.6 0.55 Result. Dem. Factor #DIV/0! #DIV/0! #DIV/0! 0.75 0.746
A/C 0.8 0.7 0.6

Updated 05/03/2024 21:08:56


ECG DB / PANELBOARD SCHEDULE Proj.No 1658
According to IEC & Master Spec REV.(0)
NOTE
PANEL NO.: ESMDB-S LOCATION : Basement Floor Notes: 1,12,4 1- MCCB' s required 6- Led Dimmer Control 10- ELCB, 100 mA required
7- Contactor and PB
2- Isolated Earth Bus 11- ELCB, 30 mA required
Mains SHEET (1 OF 2) Rating Duty Enclosure Dimensions connected to BMS
Fed From : EMDB-2 (SEC-2) Main C.B.: 630 A 380 / 220 V SURFACE W mm 3- 200% neutral size 8- Photocell and Timer 12- over&under voltage
Cable No. : F-ESMDB-S << TCL : 289 kW 19 kA-symm. IP42 D mm 4- Indicating Lamps 9- Two-Section Panel 13- Shunt trip
Cable size: 2 // ( 4 x 185 ) mm2 Max.Dem.: 233 kW 39 kA-peak Form 2 H mm 5-Connected to BMS via lighting control system 14- Metering
SER NO.CCT C.B. WIRE ECC CONNECTED LOAD - No.of points per circuit unit CONNECTED LOAD
N
O 1P-C.B.'sREF SIZE SIZE No. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 Load PER - PHASE
T
ROOM / AREA / SUB PANEL / LOAD DISCRIP.
OR # TL CL/ HID Sing Twin Pwr 3 ph Mot/ W.B/ wind split VAV- @ R Y B
E
WAYS NO. A mm2 mm2 Ltg Exit Ltg S/O S/O S/O S/O Fan HD EWH H.P A/C A/C FCU kW kW kW kW
1 R1 5.9
1 2 Y1 40 10 10 ELP-S-G . 15.15 1.00 0.00 0.00 16.15 5.0
3 B1 5.3
4 R2 1.7
1 5 Y2 40 10 10 ELP-G-AD1 . 4.26 0.00 0.00 0.00 4.26 1.5
6 B2 1.1
7 R3 1.1
1 8 Y3 40 10 10 ELP-G-AD2 . 3.17 0.00 0.00 0.00 3.17 0.9
9 B3 1.1
10 R4 16.0
1 11 Y4 100 35 16 UPS-S-M . 0.00 48.00 0.00 0.00 48.00 16.0
12 B4 16.0
13 R5 9.6
1 14 Y5 80 35 25 ELP-S-7 . 29.58 0.00 0.00 0.00 29.58 9.6
15 B5 10.4
16 R6 13.1
1 17 Y6 80 35 35 ELP-S-2 . 38.85 0.00 0.00 0.00 38.85 13.1
18 B6 12.6
19 R7 6.2
1 20 Y7 63 25 16 ELP-S-F 17.82 0.00 0.00 0.00 17.82 6.0
21 B7 5.7
22 R8 43.7
1 23 Y8 250 185 95 EDB-S-10-A/C . 0.00 0.00 0.00 131.00 131.00 43.7
24 B8 43.7
Dem. Factor ( DF ) Application SUB - 97.3 95.7 95.8
first 100 Kw next 200 Kw remaining Ltg Power Heating A/C TOTAL 289
Lighting 0.9 0.8 0.7 TCL ( kW ) 108.83 49.00 0.00 131.00 289 kilo-Watts
Power 0.7 0.6 0.5 -------- >> MD ( kW ) 97.06 34.30 0.00 101.70 233
Heating 0.6 0.6 0.55 Result. Dem. Factor 0.89 0.70 #DIV/0! 0.78 0.807
A/C 0.8 0.7 0.6

Updated 05/03/2024 21:08:56


ECG DB / PANELBOARD SCHEDULE Proj.No 1658
According to IEC & Master Spec REV.(0)
NOTE
PANEL NO.: ESMDB-S LOCATION : Basement Floor Notes: 1,12,4 1- MCCB' s required 6- Led Dimmer Control 10- ELCB, 100 mA required
7- Contactor and PB
2- Isolated Earth Bus 11- ELCB, 30 mA required
Mains SHEET (2 OF 2) Rating Duty Enclosure Dimensions connected to BMS
Fed From : EMDB-2 (SEC-2) Main C.B.: 630 A 380 / 220 V SURFACE W mm 3- 200% neutral size 8- Photocell and Timer 12- over&under voltage
Cable No. : F-ESMDB-S << TCL : 315 kW 19 kA-symm. IP42 D mm 4- Indicating Lamps 9- Two-Section Panel 13- Shunt trip
Cable size: 2 // ( 4 x 185 ) mm2 Max.Dem.: 254 kW 39 kA-peak Form 2 H mm 5-Connected to BMS via lighting control system 14- Metering
SER NO.CCT C.B. WIRE ECC CONNECTED LOAD - No.of points per circuit unit CONNECTED LOAD
N
O 1P-C.B.'sREF SIZE SIZE No. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 Load PER - PHASE
T
ROOM / AREA / SUB PANEL / LOAD DISCRIP.
OR # TL CL/ HID Sing Twin Pwr 3 ph Mot/ W.B/ wind split VAV- @ R Y B
E
WAYS NO. A mm2 mm2 Ltg Exit Ltg S/O S/O S/O S/O Fan HD EWH H.P A/C A/C FCU kW kW kW kW
25 R9
26 Y9 100 SPARE .
27 B9
28 R10
29 Y10 100 SPARE .
30 B10
31 R11 10.0
32 Y11 63 16 16 ELP-SM . 26.56 26.56 8.4
33 B11 8.1
34 R12
35 Y12 100 SPARE .
36 B12
37 R13
38 Y13 100 UPS-S-M .
39 B13
40 R14
41 Y14 .
42 B14
43 R15
44 Y15
45 B15
46 R16
47 Y16 .
48 B16
Dem. Factor ( DF ) Application SUB - 107.3 104.1 103.9
first 100 Kw next 200 Kw remaining Ltg Power Heating A/C TOTAL 315
Lighting 0.9 0.8 0.7 TCL ( kW ) 135.390 49.00 0.00 131.00 315 kilo-Watts
Power 0.7 0.6 0.5 -------- >> MD ( kW ) 118.31 34.30 0.00 101.70 254
Heating 0.6 0.6 0.55 Result. Dem. Factor 0.87 0.70 #DIV/0! 0.78 0.806
A/C 0.8 0.7 0.6

Updated 05/03/2024 21:08:56


ECG DB / PANELBOARD SCHEDULE Proj.No 1658
According to IEC & Master Spec REV.(0)
NOTE
PANEL NO.: EDB-S-10-A/C LOCATION : Tenth Floor Notes: 1,12,4 1- MCCB' s required 6- Led Dimmer Control 10- ELCB, 100 mA required
7- Contactor and PB
2- Isolated Earth Bus 11- ELCB, 30 mA required
Mains Rating Duty Enclosure Dimensions connected to BMS
Fed From : EMSDB-S Main C.B.: 250 A 380 / 220 V SURFACE W mm 3- 200% neutral size 8- Photocell and Timer 12- over&under voltage
Cable No. : F-EDB-S-10-A/C << TCL : 131 kW 12 kA-symm. IP42 D mm 4- Indicating Lamps 9- Two-Section Panel 13- Shunt trip
Cable size: 1 // ( 4 x 185 ) mm2 Max.Dem.: 101.7 kW 25 kA-peak Form 2 H mm 5-Connected to BMS via lighting control system 14- Metering
SER NO.CCT C.B. WIRE ECC CONNECTED LOAD - No.of points per circuit unit CONNECTED LOAD
N
O 1P-C.B.'sREF SIZE SIZE No. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 Load PER - PHASE
T
ROOM / AREA / SUB PANEL / LOAD DISCRIP.
OR # TL CL/ HID Sing Twin Pwr 3 ph Mot/ W.B/ wind split VAV- @ R Y B
E
WAYS NO. A mm2 mm2 Ltg Exit Ltg S/O S/O S/O S/O Fan HD EWH H.P A/C A/C FCU kW kW kW kW
1 R1 13.3
2 Y1 100 50 25 EMCC-R8 0.00 0.00 0.00 40.00 40.00 13.3
3 B1 13.3
4 R2 5.0
5 Y2 40 10 10 EMCC-R9 0.00 0.00 0.00 15.00 15.00 5.0
6 B2 5.0
7 R3 6.7
8 Y3 63 16 16 EMCC-R10 0.00 0.00 0.00 20.00 20.00 6.7
9 B3 6.7
10 R4 6.0
11 Y4 63 16 16 EMCC-R11 0.00 0.00 0.00 18.00 18.00 6.0
12 B4 6.0
13 R5 6.0
14 Y5 63 25 16 EMCC-R12 0.00 0.00 0.00 18.00 18.00 6.0
15 B5 6.0
16 R6 6.7
17 Y6 63 35 16 EMCC-R13 0.00 0.00 0.00 20.00 20.00 6.7
18 B6 6.7
19 R7 0.0
20 Y7 63 SPARE 0.0
21 B7 0.0
22 R8
23 Y8 40 SPARE
24 B8
Dem. Factor ( DF ) Application SUB - 43.7 43.7 43.7
first 100 Kw next 200 Kw remaining Ltg Power Heating A/C TOTAL 131
Lighting 0.9 0.8 0.7 TCL ( kW ) 0 0.00 0.00 131.00 131 kilo-Watts
Power 0.7 0.6 0.5 -------- >> MD ( kW ) 0.00 0.00 0.00 101.70 102
Heating 0.6 0.6 0.55 Result. Dem. Factor #DIV/0! #DIV/0! #DIV/0! 0.78 0.776
A/C 0.8 0.7 0.6

Updated 05/03/2024 21:08:56


ECG DB / PANELBOARD SCHEDULE Proj.No 1658
According to IEC & Master Spec REV.(0)
NOTE
PANEL NO.: UDB-S-M LOCATION : Mezzanine Floor Notes: 1,4 1- MCCB' s required 6- Led Dimmer Control 10- ELCB, 100 mA required
7- Contactor and PB
2- Isolated Earth Bus 11- ELCB, 30 mA required
Mains Rating Duty Enclosure Dimensions connected to BMS
Fed From : UPS-S-M Main C.B.: 63 A 380 / 220 V SURFACE W mm 3- 200% neutral size 8- Photocell and Timer 12- Split Bus
Cable No. : F-UDB-S-M << TCL : 32 kW 15.43 kA-symm. IP42 D mm 4- Indicating Lamps 9- Two-Section Panel 13- Shunt trip
Cable size: 1 // ( 4x 35 ) mm2 Max.Dem.: 22.3 kW 31.63 kA-peak Form 2 H mm 5-Connected to BMS via lighting control system 14- Metering
SER NO. CCT C.B. WIRE ECC CONNECTED LOAD - No.of points per circuit unit CONNECTED LOAD
N
O 1P-C.B.'s REF SIZE SIZE No. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 Load PER - PHASE
T
ROOM / AREA / SUB PANEL / LOAD DISCRIP.
OR # TL CL/ HID Sing Twin Pwr 3 ph Mot/ W.B/ wind split VAV- @ R Y B
E
WAYS NO. A mm2 mm2 Ltg Exit Ltg S/O S/O S/O S/O Fan HD EWH H.P A/C A/C FCU kW kW kW kW
1 R1 20 4 4 IPP-OR1 . 1 2.90 2.9
2 Y1 20 4 4 IPP-OR2 . 1 2.90 2.9
3 B1 20 4 4 IPP-OR3 . 1 2.90 2.9
4 R2 20 4 4 IPP-OR4 . 1 2.90 2.9
5 Y2 20 4 4 IPP-OR5 . 1 2.90 2.9
6 B2 20 4 4 IPP-OR6 . 1 2.90 2.9
7 R3 20 4 4 IPP-OR7 . 1 2.90 2.9
8 Y3 20 4 4 IPP-OR8 . 1 2.90 2.9
9 B3 20 4 4 IPP-OR9 . 1 2.90 2.9
10 R4 20 4 4 IPP-OR10 . 1 2.90 2.9
11 Y4 20 4 4 IPP-OR11 . 1 2.90 2.9
12 B4 20 SPARE . 0.0
13 R5 20 SPARE 0.0
14 Y5 20 SPARE . 0.0
15 B5 SPACE . 0.0
16 R6 0.0
17 Y6 . 0.0
18 B6 . 0.0
19 R7 0.0
20 Y7 0.0
21 B7 0.0
22 R8 . 0.0
23 Y8 . 0.0
24 B8 . 0.0
Dem. Factor ( DF ) Application SUB - 11.6 11.6 8.7
first 100 Kw next 200 Kw remaining Ltg Power Heating A/C TOTAL 32
Lighting 0.9 0.8 0.7 TCL ( kW ) 0.000 31.90 0.00 0.00 32 kilo-Watts
Power 0.7 0.6 0.5 -------- >> MD ( kW ) 0.00 22.33 0.00 0.00 22
Heating 0.6 0.6 0.55 Result. Dem. Factor #DIV/0! 0.70 #DIV/0! #DIV/0! 0.700
A/C 0.8 0.7 0.6

Updated 05/03/2024 21:08:56


ECG DB / PANELBOARD SCHEDULE Proj.No 1658
According to IEC & Master Spec REV.(0)
NOTE
PANEL NO.: ELP-S-G LOCATION : Ground Floor Notes: 1,4 1- MCCB' s required 6- Led Dimmer Control 10- ELCB, 100 mA required
7- Contactor and PB
2- Isolated Earth Bus 11- ELCB, 30 mA required
Mains Rating Duty Enclosure Dimensions connected to BMS
Fed From : ESMDB-S Main C.B.: 40 A 380 / 220 V SURFACE W mm 3- 200% neutral size 8- Photocell and Timer 12- Split Bus
Cable No. : F-ELP-S-G << TCL : 16 kW 7.48 kA-symm. IP42 D mm 4- Indicating Lamps 9- Two-Section Panel 13- Shunt trip
Cable size: 1 // ( 4x 10 ) mm2 Max.Dem.: 14.3 kW 15.34 kA-peak Form 2 H mm 5-Connected to BMS via lighting control system 14- Metering
SER NO. CCT C.B. WIRE ECC CONNECTED LOAD - No.of points per circuit unit CONNECTED LOAD
N
O 1P-C.B.'s REF SIZE SIZE No. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 Load PER - PHASE
T
ROOM / AREA / SUB PANEL / LOAD DISCRIP.
OR # TL CL/ HID Sing Twin Pwr 3 ph Mot/ W.B/ wind split VAV- @ R Y B
E
WAYS NO. A mm2 mm2 Ltg Exit Ltg S/O S/O S/O S/O Fan HD EWH H.P A/C A/C FCU kW kW kW kW
1 R1 16 3 3 LIGHTING . 8 0.10 0.8
2 Y1 16 3 3 LIGHTING . 8 0.10 0.8
7 3 B1 16 3 3 LIGHTING . 10 0.10 1.0
7 4 R2 16 3 3 LIGHTING . 5 0.10 0.5
7 5 Y2 16 3 3 LIGHTING . 6 0.10 0.6
7 6 B2 16 3 3 LIGHTING . 8 0.10 0.8
10 7 R3 16 3 3 LIGHTING . 7 0.10 0.7
7 8 Y3 16 3 3 LIGHTING . 9 0.10 0.9
9 B3 16 3 3 LIGHTING . 6 0.10 0.6
10 R4 16 3 3 LIGHTING . 5 0.10 0.5
10 11 Y4 16 3 3 LIGHTING . 6 0.10 0.6
7 12 B4 16 3 3 LIGHTING . 6 0.10 0.6
7 13 R5 16 3 3 LIGHTING 12 0.10 1.2
7 14 Y5 16 3 3 LIGHTING . 6 0.10 0.6
7 15 B5 16 3 3 LIGHTING . 12 0.10 1.2
7 16 R6 16 3 3 LIGHTING 12 0.10 1.2
17 Y6 16 3 3 LIGHTING . 12 0.10 1.2
18 B6 20 4 4 JUNCTION BOX FOR CAR PARKING BARRIER . 1 0.50 0.5
19 R7 20 4 4 JUNCTION BOX FOR CAR PARKING BARRIER 1 0.50 0.5
20 Y7 16 3 3 EXIT SIGN 10 0.03 0.3
7 21 B7 16 3 3 LIGHTING 6 0.10 0.6
22 R8 16 3 3 LIGHTING . 5 0.10 0.5
23 Y8 16 SPARE . 0.0
24 B8 16 SPARE . 0.0
Dem. Factor ( DF ) Application SUB - 5.9 5.0 5.3
first 100 Kw next 200 Kw remaining Ltg Power Heating A/C TOTAL 16
Lighting 0.9 0.8 0.7 TCL ( kW ) 15.150 1.00 0.00 0.00 16 kilo-Watts
Power 0.7 0.6 0.5 -------- >> MD ( kW ) 13.64 0.70 0.00 0.00 14
Heating 0.6 0.6 0.55 Result. Dem. Factor 0.90 0.70 #DIV/0! #DIV/0! 0.888
A/C 0.8 0.7 0.6

Updated 05/03/2024 21:08:56


ECG DB / PANELBOARD SCHEDULE Proj.No 1658
According to IEC & Master Spec REV.(0)
NOTE
PANEL NO.: ELP-G-AD1 LOCATION : Ground Floor Notes: 1,4 1- MCCB' s required 6- Led Dimmer Control 10- ELCB, 100 mA required
7- Contactor and PB
2- Isolated Earth Bus 11- ELCB, 30 mA required
Mains Rating Duty Enclosure Dimensions connected to BMS
Fed From : ESMDB-S Main C.B.: 40 A 380 / 220 V SURFACE W mm 3- 200% neutral size 8- Photocell and Timer 12- Split Bus
Cable No. : F-ELP-G-AD1 << TCL : 4 kW 2.18 kA-symm. IP42 D mm 4- Indicating Lamps 9- Two-Section Panel 13- Shunt trip
Cable size: 1 // ( 4x 10 ) mm2 Max.Dem.: 3.83 kW 4.463 kA-peak Form 2 H mm 5-Connected to BMS via lighting control system 14- Metering
SER NO. CCT C.B. WIRE ECC CONNECTED LOAD - No.of points per circuit unit CONNECTED LOAD
N
O 1P-C.B.'s REF SIZE SIZE No. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 Load PER - PHASE
T
ROOM / AREA / SUB PANEL / LOAD DISCRIP.
OR # TL CL/ HID Sing Twin Pwr 3 ph Mot/ W.B/ wind split VAV- @ R Y B
E
WAYS NO. A mm2 mm2 Ltg Exit Ltg S/O S/O S/O S/O Fan HD EWH H.P A/C A/C FCU kW kW kW kW
10 1 R1 16 3 3 LIGHTING . 6 0.10 0.6
7 2 Y1 16 3 3 LIGHTING . 8 0.10 0.8
7 3 B1 16 3 3 LIGHTING . 8 0.10 0.8
7 4 R2 16 3 3 LIGHTING . 6 0.10 0.6
5 Y2 16 3 3 LIGHTING . 2 0.10 0.2
6 B2 16 3 3 EXIT SIGN . 3 0.01 0.0
7 7 R3 16 3 3 LIGHTING . 5 0.10 0.5
10 8 Y3 16 3 3 LIGHTING . 5 0.10 0.5
9 B3 16 3 3 EXIT SIGN . 3 0.01 0.0
10 R4 20 SPARE . 0.0
11 Y4 16 SPARE 0.0
7 12 B4 16 3 3 STAIRS LIGHTING . 2 0.10 0.2
13 R5 16 SPARE 0.0
14 Y5 SPACE . 0.0
15 B5 SPACE . 0.0
16 R6 0.0
17 Y6 . 0.0
18 B6 . 0.0
19 R7 0.0
20 Y7 0.0
21 B7 0.0
22 R8 . 0.0
23 Y8 . 0.0
24 B8 . 0.0
Dem. Factor ( DF ) Application SUB - 1.7 1.5 1.1
first 100 Kw next 200 Kw remaining Ltg Power Heating A/C TOTAL 4
Lighting 0.9 0.8 0.7 TCL ( kW ) 4.260 0.00 0.00 0.00 4 kilo-Watts
Power 0.7 0.6 0.5 -------- >> MD ( kW ) 3.83 0.00 0.00 0.00 4
Heating 0.6 0.6 0.55 Result. Dem. Factor 0.90 #DIV/0! #DIV/0! #DIV/0! 0.900
A/C 0.8 0.7 0.6

Updated 05/03/2024 21:08:56


ECG DB / PANELBOARD SCHEDULE Proj.No 1658
According to IEC & Master Spec REV.(0)
NOTE
PANEL NO.: ELP-G-AD2 LOCATION : Ground Floor Notes: 1,4 1- MCCB' s required 6- Led Dimmer Control 10- ELCB, 100 mA required
7- Contactor and PB
2- Isolated Earth Bus 11- ELCB, 30 mA required
Mains Rating Duty Enclosure Dimensions connected to BMS
Fed From : ESMDB-S Main C.B.: 40 A 380 / 220 V SURFACE W mm 3- 200% neutral size 8- Photocell and Timer 12- Split Bus
Cable No. : F-ELP-G-AD2 << TCL : 3 kW 2.00 kA-symm. IP42 D mm 4- Indicating Lamps 9- Two-Section Panel 13- Shunt trip
Cable size: 1 // ( 4x 10 ) mm2 Max.Dem.: 2.85 kW 4.099 kA-peak Form 2 H mm 5-Connected to BMS via lighting control system 14- Metering
SER NO. CCT C.B. WIRE ECC CONNECTED LOAD - No.of points per circuit unit CONNECTED LOAD
N
O 1P-C.B.'s REF SIZE SIZE No. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 Load PER - PHASE
T
ROOM / AREA / SUB PANEL / LOAD DISCRIP.
OR # TL CL/ HID Sing Twin Pwr 3 ph Mot/ W.B/ wind split VAV- @ R Y B
E
WAYS NO. A mm2 mm2 Ltg Exit Ltg S/O S/O S/O S/O Fan HD EWH H.P A/C A/C FCU kW kW kW kW
10 1 R1 16 3 3 LIGHTING . 5 0.10 0.5
2 Y1 16 3 3 LIGHTING . 5 0.10 0.5
10 3 B1 16 3 3 LIGHTING . 4 0.10 0.4
7 4 R2 16 3 3 LIGHTING . 6 0.10 0.6
5 Y2 16 3 3 LIGHTING . 4 0.10 0.4
6 B2 16 3 3 LIGHTING . 3 0.10 0.3
7 R3 16 3 3 EXIT SIGN . 4 0.01 0.0
8 Y3 16 SPARE . 0.0
9 B3 16 3 3 EXIT SIGN . 3 0.01 0.03
10 R4 20 SPARE . 0.0
11 Y4 20 SPARE . 0.0
7 12 B4 16 3 3 STAIRS LIGHTING . 4 0.10 0.4
13 R5 16 SPARE 0.0
14 Y5 16 SPARE . 0.0
15 B5 16 SPARE . 0.0
16 R6 SPACE 0.0
17 Y6 SPACE . 0.0
18 B6 SPACE . 0.0
19 R7 0.0
20 Y7 0.0
21 B7 0.0
22 R8 . 0.0
23 Y8 . 0.0
24 B8 . 0.0
Dem. Factor ( DF ) Application SUB - 1.1 0.9 1.1
first 100 Kw next 200 Kw remaining Ltg Power Heating A/C TOTAL 3
Lighting 0.9 0.8 0.7 TCL ( kW ) 3.170 0.00 0.00 0.00 3 kilo-Watts
Power 0.7 0.6 0.5 -------- >> MD ( kW ) 2.85 0.00 0.00 0.00 3
Heating 0.6 0.6 0.55 Result. Dem. Factor 0.90 #DIV/0! #DIV/0! #DIV/0! 0.900
A/C 0.8 0.7 0.6

Updated 05/03/2024 21:08:56


ECG DB / PANELBOARD SCHEDULE Proj.No 1658
According to IEC & Master Spec REV.(0)
NOTE
PANEL NO.: ELP-S-M (1-2) LOCATION : Mezzanine Floor Notes: 1,4 1- MCCB' s required 6- Led Dimmer Control 10- ELCB, 100 mA required
7- Contactor and PB
2- Isolated Earth Bus 11- ELCB, 30 mA required
Mains SHEET 1 OF 2 Rating Duty Dimensions connected to BMS
Fed From : ESMDB-S Main C.B.: 63 A 380 / 220 V W mm 3- 200% neutral size 8- Photocell and Timer 12- Split Bus
Cable No. : F-ELP-S-M << TCL : 15 kW 7.66 kA-symm. D mm 4- Indicating Lamps 9- Two-Section Panel 13- Shunt trip
Cable size: 1 // ( 4x 16 ) mm2 Max.Dem.: 13.1 kW 15.71 kA-peak H mm 5-Connected to BMS via lighting control system 14- Metering
SER NO. CCT C.B. WIRE ECC CONNECTED LOAD - No.of points per circuit unit CONNECTED LOAD
N
O 1P-C.B.'s REF SIZE SIZE No. 2 3 4 5 6 7 8 9 10 11 12 13 14 Load PER - PHASE
T
ROOM / AREA / SUB PANEL / LOAD DISCRIP.
OR # CL/ HID Sing Twin Pwr 3 ph Mot/ W.B/ wind split VAV- @ R Y B
E
WAYS NO. A mm2 mm2 Exit Ltg S/O S/O S/O S/O Fan HD EWH H.P A/C A/C FCU kW kW kW kW
10 1 R1 16 3 3 LIGHTING OF (B.H.U) . 0.15 0.4
10 2 Y1 16 3 3 LIGHTING OF (B.H.U) . 0.15 0.6
10 3 B1 16 3 3 LIGHTING OF (B.H.U) . 0.15 0.4
10 4 R2 16 3 3 LIGHTING OF (B.H.U) . 0.15 0.4
5 Y2 16 3 3 LIGHTING . 0.10 0.6
10 6 B2 16 3 3 LIGHTING . 0.10 0.5
7 7 R3 16 3 3 LIGHTING . 0.10 0.9
8 Y3 16 3 3 LIGHTING . 0.10 0.8
9 B3 16 3 3 LIGHTING . 0.10 0.6
10 10 R4 16 3 3 LIGHTING . 0.10 0.5
11 Y4 16 SPARE . 0.0
12 B4 16 3 3 SPARE . 0.0
13 R5 16 3 3 LIGHTING 0.10 0.5
10 14 Y5 16 3 3 LIGHTING . 0.10 0.8
15 B5 16 3 3 LIGHTING . 0.10 0.5
7 16 R6 16 3 3 LIGHTING 0.10 0.4
7 17 Y6 16 3 3 LIGHTING . 0.10 0.4
18 B6 16 3 3 LIGHTING . 0.10 0.7
19 R7 16 3 3 LIGHTING 0.10 1.2
20 Y7 16 3 3 LIGHTING 0.10 0.4
21 B7 16 3 3 LIGHTING 0.10 1.2
22 R8 16 3 3 LIGHTING . 0.10 1.2
23 Y8 16 3 3 LIGHTING . 0.10 0.9
24 B8 16 3 3 LIGHTING . 0.10 0.5
Dem. Factor ( DF ) Application SUB - 5.6 4.5 4.5
first 100 Kw next 200 Kw remaining Ltg Power Heating A/C TOTAL 15
Lighting 0.9 0.8 0.7 TCL ( kW ) 14.550 0.00 0.00 0.00 15 kilo-Watts
Power 0.7 0.6 0.5 -------- >> MD ( kW ) 13.10 0.00 0.00 0.00 13
Heating 0.6 0.6 0.55 Result. Dem. Factor 0.90 #DIV/0! #DIV/0! #DIV/0! 0.900
A/C 0.8 0.7 0.6

Updated 05/03/2024 21:08:56


ECG DB / PANELBOARD SCHEDULE Proj.No 1658
According to IEC & Master Spec REV.(0)
NOTE
PANEL NO.: ELP-S-M (2-2) LOCATION : Mezzanine Floor Notes: 1,4 1- MCCB' s required 6- Led Dimmer Control 10- ELCB, 100 mA required
7- Contactor and PB
2- Isolated Earth Bus 11- ELCB, 30 mA required
Mains SHEET 2 OF 2 Rating Duty Dimensions connected to BMS
Fed From : ESMDB-S Main C.B.: 63 A 380 / 220 V W mm 3- 200% neutral size 8- Photocell and Timer 12- Split Bus
Cable No. : F-ELP-S-M << TCL : 27 kW 7.66 kA-symm. D mm 4- Indicating Lamps 9- Two-Section Panel 13- Shunt trip
Cable size: 1 // ( 4x 16 ) mm2 Max.Dem.: 23.9 kW 15.71 kA-peak H mm 5-Connected to BMS via lighting control system 14- Metering
SER NO. CCT C.B. WIRE ECC CONNECTED LOAD - No.of points per circuit unit CONNECTED LOAD
N
O 1P-C.B.'s REF SIZE SIZE No. 2 3 4 5 6 7 8 9 10 11 12 13 14 Load PER - PHASE
T
ROOM / AREA / SUB PANEL / LOAD DISCRIP.
OR # CL/ HID Sing Twin Pwr 3 ph Mot/ W.B/ wind split VAV- @ R Y B
E
WAYS NO. A mm2 mm2 Exit Ltg S/O S/O S/O S/O Fan HD EWH H.P A/C A/C FCU kW kW kW kW
25 R9 16 3 3 LIGHTING . 0.10 0.8
26 Y9 16 3 3 LIGHTING . 0.10 1.2
27 B9 16 3 3 LIGHTING . 0.10 1.2
28 R10 16 3 3 LIGHTING . 0.10 1.2
29 Y10 16 3 3 LIGHTING . 0.10 1.2
30 B10 16 3 3 LIGHTING . 0.10 1.2
31 R11 16 3 3 LIGHTING . 0.10 1.2
32 Y11 16 3 3 LIGHTING . 0.10 1.2
33 B11 16 3 3 LIGHTING . 0.10 1.2
34 R12 16 3 3 LIGHTING . 0.10 1.2
7 35 Y12 16 3 3 LIGHTING . 0.10 0.3
36 B12 16 3 3 EXIT SIGN . 7 0.01 0.1
37 R13 16 3 3 EXIT SIGN 4 0.01 0.04
38 Y13 20 SPARE . 0.0
39 B13 20 SPARE . 0.0
40 R14 16 SPARE 0.0
41 Y14 16 SPARE . 0.0
42 B14 16 SPARE . 0.0
43 R15 0.0
44 Y15 0.0
45 B15 0.0
46 R16 . 0.0
47 Y16 . 0.0
48 B16 . 0.0
Dem. Factor ( DF ) Application SUB - 10.0 8.4 8.1
first 100 Kw next 200 Kw remaining Ltg Power Heating A/C TOTAL 27
Lighting 0.9 0.8 0.7 TCL ( kW ) 26.560 0.00 0.00 0.00 27 kilo-Watts
Power 0.7 0.6 0.5 -------- >> MD ( kW ) 23.90 0.00 0.00 0.00 24
Heating 0.6 0.6 0.55 Result. Dem. Factor 0.90 #DIV/0! #DIV/0! #DIV/0! 0.900
A/C 0.8 0.7 0.6

Updated 05/03/2024 21:08:56


ECG DB / PANELBOARD SCHEDULE Proj.No 1658
According to IEC & Master Spec REV.(0)
NOTE
PANEL NO.: ELP-S-F LOCATION : First Floor Notes: 1,4 1- MCCB' s required 6- Led Dimmer Control 10- ELCB, 100 mA required
7- Contactor and PB
2- Isolated Earth Bus 11- ELCB, 30 mA required
Mains SHEET 1 OF 2 Rating Duty Enclosure Dimensions connected to BMS
Fed From : ESMDB-S Main C.B.: 63 A 380 / 220 V SURFACE W mm 3- 200% neutral size 8- Photocell and Timer 12- Split Bus
Cable No. : F-ELP-S-F << TCL : 17 kW 6.54 kA-symm. IP42 D mm 4- Indicating Lamps 9- Two-Section Panel 13- Shunt trip
Cable size: 1 // ( 4x 25 ) mm2 Max.Dem.: 15.2 kW 13.4 kA-peak Form 2 H mm 5-Connected to BMS via lighting control system 14- Metering
SER NO. CCT C.B. WIRE ECC CONNECTED LOAD - No.of points per circuit unit CONNECTED LOAD
N
O 1P-C.B.'s REF SIZE SIZE No. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 Load PER - PHASE
T
ROOM / AREA / SUB PANEL / LOAD DISCRIP.
OR # TL CL/ HID Sing Twin Pwr 3 ph Mot/ W.B/ wind split VAV- @ R Y B
E
WAYS NO. A mm2 mm2 Ltg Exit Ltg S/O S/O S/O S/O Fan HD EWH H.P A/C A/C FCU kW kW kW kW
1 R1 16 3 3 LIGHTING . 8 0.10 0.8
2 Y1 16 3 3 LIGHTING . 8 0.10 0.8
3 B1 16 3 3 LIGHTING . 8 0.10 0.8
4 R2 16 3 3 LIGHTING . 8 0.10 0.8
5 Y2 16 3 3 LIGHTING . 8 0.10 0.8
6 B2 16 3 3 LIGHTING . 8 0.10 0.8
7 R3 16 3 3 LIGHTING . 10 0.10 1.0
8 Y3 16 3 3 LIGHTING . 12 0.10 1.2
9 B3 16 3 3 LIGHTING . 5 0.10 0.5
10 10 R4 16 3 3 LIGHTING OF (B.H.U) . 3 0.15 0.4
11 Y4 16 3 3 LIGHTING . 5 0.10 0.5
12 B4 16 3 3 LIGHTING . 10 0.10 1.0
10 13 R5 16 3 3 LIGHTING 5 0.10 0.5
14 Y5 16 3 3 LIGHTING . 10 0.10 1.0
15 B5 16 3 3 LIGHTING . 5 0.10 0.5
7 16 R6 16 3 3 LIGHTING 7 0.10 0.7
17 Y6 16 3 3 LIGHTING . 10 0.10 1.0
18 B6 16 3 3 LIGHTING . 6 0.10 0.6
19 R7 16 3 3 LIGHTING 11 0.10 1.1
20 Y7 16 3 3 LIGHTING 3 0.10 0.3
21 B7 16 3 3 LIGHTING 8 0.10 0.8
22 R8 16 3 3 LIGHTING . 6 0.10 0.6
23 Y8 16 SPARE . 0.0
7 24 B8 16 3 3 LIGHTING . 3 0.10 0.3
Dem. Factor ( DF ) Application SUB - 6.0 5.6 5.3
first 100 Kw next 200 Kw remaining Ltg Power Heating A/C TOTAL 17
Lighting 0.9 0.8 0.7 TCL ( kW ) 16.850 0.00 0.00 0.00 17 kilo-Watts
Power 0.7 0.6 0.5 -------- >> MD ( kW ) 15.17 0.00 0.00 0.00 15
Heating 0.6 0.6 0.55 Result. Dem. Factor 0.90 #DIV/0! #DIV/0! #DIV/0! 0.900
A/C 0.8 0.7 0.6

Updated 05/03/2024 21:08:56


ECG DB / PANELBOARD SCHEDULE Proj.No 1658
According to IEC & Master Spec REV.(0)
NOTE
PANEL NO.: ELP-S-F LOCATION : First Floor Notes: 1,4 1- MCCB' s required 6- Led Dimmer Control 10- ELCB, 100 mA required
7- Contactor and PB
2- Isolated Earth Bus 11- ELCB, 30 mA required
Mains SHEET 2 OF 2 Rating Duty Dimensions connected to BMS
Fed From : ESMDB-S Main C.B.: 63 A 380 / 220 V W mm 3- 200% neutral size 8- Photocell and Timer 12- Split Bus
Cable No. : F-ELP-S-F << TCL : 18 kW 6.54 kA-symm. D mm 4- Indicating Lamps 9- Two-Section Panel 13- Shunt trip
Cable size: 1 // ( 4x 25 ) mm2 Max.Dem.: 16 kW 13.4 kA-peak H mm 5-Connected to BMS via lighting control system 14- Metering
SER NO. CCT C.B. WIRE ECC CONNECTED LOAD - No.of points per circuit unit CONNECTED LOAD
N
O 1P-C.B.'s REF SIZE SIZE No. 2 3 4 5 6 7 8 9 10 11 12 13 14 Load PER - PHASE
T
ROOM / AREA / SUB PANEL / LOAD DISCRIP.
OR # CL/ HID Sing Twin Pwr 3 ph Mot/ W.B/ wind split VAV- @ R Y B
E
WAYS NO. A mm2 mm2 Exit Ltg S/O S/O S/O S/O Fan HD EWH H.P A/C A/C FCU kW kW kW kW
25 R9 16 3 3 EXIT SIGN . 6 0.01 0.1
26 Y9 16 3 3 EXIT SIGN . 9 0.01 0.1
27 B9 16 3 3 EXIT SIGN . 7 0.01 0.1
10 28 R10 16 3 3 LIGHTING OF (B.H.U) . 1 0.15 0.2
10 29 Y10 16 3 3 LIGHTING OF (B.H.U) . 2 0.15 0.3
10 30 B10 16 3 3 LIGHTING OF (B.H.U) . 2 0.15 0.3
31 R11 16 SPARE . 0.0
32 Y11 16 SPARE . 0.0
33 B11 16 SPARE . 0.0
34 R12 16 SPARE . 0.0
35 Y12 16 SPARE . 0.0
36 B12 16 SPARE . 0.0
37 R13 0.0
38 Y13 . 0.0
39 B13 . 0.0
40 R14 0.0
41 Y14 . 0.0
42 B14 . 0.0
43 R15 0.0
44 Y15 0.0
45 B15 0.0
46 R16 . 0.0
47 Y16 . 0.0
48 B16 . 0.0
Dem. Factor ( DF ) Application SUB - 6.2 6.0 5.7
first 100 Kw next 200 Kw remaining Ltg Power Heating A/C TOTAL 18
Lighting 0.9 0.8 0.7 TCL ( kW ) 17.820 0.00 0.00 0.00 18 kilo-Watts
Power 0.7 0.6 0.5 -------- >> MD ( kW ) 16.04 0.00 0.00 0.00 16
Heating 0.6 0.6 0.55 Result. Dem. Factor 0.90 #DIV/0! #DIV/0! #DIV/0! 0.900
A/C 0.8 0.7 0.6

Updated 05/03/2024 21:08:56


ECG DB / PANELBOARD SCHEDULE Proj.No 1658
According to IEC & Master Spec REV.(0)
NOTE
PANEL NO.: ELP-S-2 LOCATION : 2nd Floor Notes: 1,4 1- MCCB' s required 6- Led Dimmer Control 10- ELCB, 100 mA required
7- Contactor and PB
2- Isolated Earth Bus 11- ELCB, 30 mA required
Mains SHEET (1 OF 2) Rating Duty Enclosure Dimensions connected to BMS
Fed From : ESMDB-S Main C.B.: 80 A 380 / 220 V SURFACE W mm 3- 200% neutral size 8- Photocell and Timer 12- Split Bus
Cable No. : F-ELP-S-2 << TCL : 33 kW 7.13 kA-symm. IP42 D mm 4- Indicating Lamps 9- Two-Section Panel 13- Shunt trip
Cable size: 1 // ( 4x 35 ) mm2 Max.Dem.: 29.9 kW 14.62 kA-peak Form 2 H mm 5-Connected to BMS via lighting control system 14- Metering
SER NO. CCT C.B. WIRE ECC CONNECTED LOAD - No.of points per circuit unit CONNECTED LOAD
N
O 1P-C.B.'s REF SIZE SIZE No. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 Load PER - PHASE
T
ROOM / AREA / SUB PANEL / LOAD DISCRIP.
OR # TL CL/ HID Sing Twin Pwr 3 ph Mot/ W.B/ wind split VAV- @ R Y B
E
WAYS NO. A mm2 mm2 Ltg Exit Ltg S/O S/O S/O S/O Fan HD EWH H.P A/C A/C FCU kW kW kW kW
1 R1 16 3 3 LIGHTING . 10 0.10 1.0
2 Y1 16 3 3 LIGHTING . 8 0.10 0.8
3 B1 16 3 3 LIGHTING . 8 0.10 0.8
4 R2 16 3 3 LIGHTING . 8 0.10 0.8
5 Y2 16 3 3 LIGHTING . 8 0.10 0.8
6 B2 16 3 3 LIGHTING . 8 0.10 0.8
7 R3 16 3 3 LIGHTING . 10 0.10 1.0
8 Y3 16 3 3 LIGHTING . 6 0.10 0.6
9 B3 16 3 3 LIGHTING . 8 0.10 0.8
10 R4 16 3 3 EXIT SIGN . 7 0.01 0.1
11 Y4 16 3 3 LIGHTING . 7 0.10 0.7
7 12 B4 16 3 3 LIGHTING . 6 0.10 0.6
13 R5 16 3 3 LIGHTING 4 0.10 0.4
14 Y5 16 SPARE . 0.0
15 B5 16 SPARE . 0.0
16 R6 3.3
17 Y6 40 16 16 ELP-S-3 . 9.07 0.00 0.00 0.00 9.07 2.8
18 B6 . 3.0
19 R7 2.5
20 Y7 40 10 16 ELP-S-4 7.47 0.00 0.00 0.00 7.47 2.7
21 B7 2.3
22 R8 . 2.5
23 Y8 40 10 16 ELP-S-5 . 7.47 0.00 0.00 0.00 7.47 2.7
24 B8 . 2.3
Dem. Factor ( DF ) Application SUB - 11.5 11.1 10.5
first 100 Kw next 200 Kw remaining Ltg Power Heating A/C TOTAL 33
Lighting 0.9 0.8 0.7 TCL ( kW ) 33.180 0.00 0.00 0.00 33 kilo-Watts
Power 0.7 0.6 0.5 -------- >> MD ( kW ) 29.86 0.00 0.00 0.00 30
Heating 0.6 0.6 0.55 Result. Dem. Factor 0.90 #DIV/0! #DIV/0! #DIV/0! 0.900
A/C 0.8 0.7 0.6

Updated 05/03/2024 21:08:56


ECG DB / PANELBOARD SCHEDULE Proj.No 1658
According to IEC & Master Spec REV.(0)
NOTE
PANEL NO.: ELP-S-2 LOCATION : 2nd Floor Notes: 1,4 1- MCCB' s required 6- Led Dimmer Control 10- ELCB, 100 mA required
7- Contactor and PB
2- Isolated Earth Bus 11- ELCB, 30 mA required
Mains SHEET (2 OF 2) Rating Duty Enclosure Dimensions connected to BMS
Fed From : ESMDB-S Main C.B.: 80 A 380 / 220 V SURFACE W mm 3- 200% neutral size 8- Photocell and Timer 12- Split Bus
Cable No. : F-ELP-S-2 << TCL : 39 kW 7.13 kA-symm. IP42 D mm 4- Indicating Lamps 9- Two-Section Panel 13- Shunt trip
Cable size: 1 // ( 4x 35 ) mm2 Max.Dem.: 35 kW 14.62 kA-peak Form 2 H mm 5-Connected to BMS via lighting control system 14- Metering
SER NO. CCT C.B. WIRE ECC CONNECTED LOAD - No.of points per circuit unit CONNECTED LOAD
N
O 1P-C.B.'s REF SIZE SIZE No. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 Load PER - PHASE
T
ROOM / AREA / SUB PANEL / LOAD DISCRIP.
OR # TL CL/ HID Sing Twin Pwr 3 ph Mot/ W.B/ wind split VAV- @ R Y B
E
WAYS NO. A mm2 mm2 Ltg Exit Ltg S/O S/O S/O S/O Fan HD EWH H.P A/C A/C FCU kW kW kW kW
25 R9 . 1.6
26 Y9 40 10 10 ELP-S-6 . 5.67 0.00 0.00 0.00 5.67 2.0
27 B9 . 2.1
28 R10 16 SPARE . 0.0
29 Y10 16 SPARE . 0.0
30 B10 16 SPARE . 0.0
31 R11 . 0.0
32 Y11 . 0.0
33 B11 . 0.0
34 R12 . 0.0
35 Y12 . 0.0
36 B12 . 0.0
37 R13 0.0
38 Y13 . 0.0
39 B13 . 0.0
40 R14 0.0
41 Y14 . 0.0
42 B14 . 0.0
43 R15 0.0
44 Y15 0.0
45 B15 0.0
46 R16 . 0.0
47 Y16 . 0.0
48 B16 . 0.0
Dem. Factor ( DF ) Application SUB - 13.1 13.1 12.6
first 100 Kw next 200 Kw remaining Ltg Power Heating A/C TOTAL 39
Lighting 0.9 0.8 0.7 TCL ( kW ) 38.850 0.00 0.00 0.00 39 kilo-Watts
Power 0.7 0.6 0.5 -------- >> MD ( kW ) 34.97 0.00 0.00 0.00 35
Heating 0.6 0.6 0.55 Result. Dem. Factor 0.90 #DIV/0! #DIV/0! #DIV/0! 0.900
A/C 0.8 0.7 0.6

Updated 05/03/2024 21:08:56


ECG DB / PANELBOARD SCHEDULE Proj.No 1658
According to IEC & Master Spec REV.(0)
NOTE
PANEL NO.: ELP-S-3 LOCATION : 3rd Floor Notes: 1,4 1- MCCB' s required 6- Led Dimmer Control 10- ELCB, 100 mA required
7- Contactor and PB
2- Isolated Earth Bus 11- ELCB, 30 mA required
Mains Rating Duty Enclosure Dimensions connected to BMS
Fed From : ELP-S-2 Main C.B.: 40 A 380 / 220 V SURFACE W mm 3- 200% neutral size 8- Photocell and Timer 12- Split Bus
Cable No. : F-ELP-S-3 << TCL : 9 kW 4.26 kA-symm. IP42 D mm 4- Indicating Lamps 9- Two-Section Panel 13- Shunt trip
Cable size: 1 // ( 4x 16 ) mm2 Max.Dem.: 8.16 kW 8.731 kA-peak Form 2 H mm 5-Connected to BMS via lighting control system 14- Metering
SER NO. CCT C.B. WIRE ECC CONNECTED LOAD - No.of points per circuit unit CONNECTED LOAD
N
O 1P-C.B.'s REF SIZE SIZE No. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 Load PER - PHASE
T
ROOM / AREA / SUB PANEL / LOAD DISCRIP.
OR # TL CL/ HID Sing Twin Pwr 3 ph Mot/ W.B/ wind split VAV- @ R Y B
E
WAYS NO. A mm2 mm2 Ltg Exit Ltg S/O S/O S/O S/O Fan HD EWH H.P A/C A/C FCU kW kW kW kW
1 R1 16 3 3 LIGHTING . 10 0.10 1.0
2 Y1 16 3 3 LIGHTING . 8 0.10 0.8
3 B1 16 3 3 LIGHTING . 8 0.10 0.8
4 R2 16 3 3 LIGHTING . 8 0.10 0.8
5 Y2 16 3 3 LIGHTING . 8 0.10 0.8
6 B2 16 3 3 LIGHTING . 8 0.10 0.8
7 R3 16 3 3 LIGHTING . 10 0.10 1.0
8 Y3 16 3 3 LIGHTING . 5 0.10 0.5
9 B3 16 3 3 LIGHTING . 8 0.10 0.8
10 R4 16 3 3 EXIT SIGN . 7 0.01 0.1
11 Y4 16 3 3 LIGHTING . 7 0.10 0.7
7 12 B4 16 3 3 LIGHTING . 6 0.10 0.6
13 R5 16 3 3 LIGHTING 4 0.10 0.4
14 Y5 16 SPARE . 0.0
15 B5 16 SPARE . 0.0
16 R6 16 SPARE 0.0
17 Y6 16 SPARE . 0.0
18 B6 16 SPARE . 0.0
19 R7 16 SPARE 0.0
20 Y7 SPACE 0.0
21 B7 SPACE 0.0
22 R8 . 0.0
23 Y8 . 0.0
24 B8 . 0.0
Dem. Factor ( DF ) Application SUB - 3.3 2.8 3.0
first 100 Kw next 200 Kw remaining Ltg Power Heating A/C TOTAL 9
Lighting 0.9 0.8 0.7 TCL ( kW ) 9.070 0.00 0.00 0.00 9 kilo-Watts
Power 0.7 0.6 0.5 -------- >> MD ( kW ) 8.16 0.00 0.00 0.00 8
Heating 0.6 0.6 0.55 Result. Dem. Factor 0.90 #DIV/0! #DIV/0! #DIV/0! 0.900
A/C 0.8 0.7 0.6

Updated 05/03/2024 21:08:56


ECG DB / PANELBOARD SCHEDULE Proj.No 1658
According to IEC & Master Spec REV.(0)
NOTE
PANEL NO.: ELP-S-4 LOCATION : 4th Floor Notes: 1,4 1- MCCB' s required 6- Led Dimmer Control 10- ELCB, 100 mA required
7- Contactor and PB
2- Isolated Earth Bus 11- ELCB, 30 mA required
Mains Rating Duty Enclosure Dimensions connected to BMS
Fed From : ELP-S-2 Main C.B.: 40 A 380 / 220 V SURFACE W mm 3- 200% neutral size 8- Photocell and Timer 12- Split Bus
Cable No. : F-ELP-S-4 << TCL : 7 kW 7.48 kA-symm. IP42 D mm 4- Indicating Lamps 9- Two-Section Panel 13- Shunt trip
Cable size: 1 // ( 4x 10 ) mm2 Max.Dem.: 6.72 kW 15.34 kA-peak Form 2 H mm 5-Connected to BMS via lighting control system 14- Metering
SER NO. CCT C.B. WIRE ECC CONNECTED LOAD - No.of points per circuit unit CONNECTED LOAD
N
O 1P-C.B.'s REF SIZE SIZE No. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 Load PER - PHASE
T
ROOM / AREA / SUB PANEL / LOAD DISCRIP.
OR # TL CL/ HID Sing Twin Pwr 3 ph Mot/ W.B/ wind split VAV- @ R Y B
E
WAYS NO. A mm2 mm2 Ltg Exit Ltg S/O S/O S/O S/O Fan HD EWH H.P A/C A/C FCU kW kW kW kW
1 R1 16 3 3 LIGHTING . 5 0.10 0.5
2 Y1 16 3 3 LIGHTING . 5 0.10 0.5
3 B1 16 3 3 LIGHTING . 6 0.10 0.6
4 R2 16 3 3 LIGHTING . 4 0.10 0.4
5 Y2 16 3 3 LIGHTING . 6 0.10 0.6
6 B2 16 3 3 LIGHTING . 8 0.10 0.8
7 R3 16 3 3 LIGHTING . 6 0.10 0.6
8 Y3 16 3 3 LIGHTING . 6 0.10 0.6
9 B3 16 3 3 LIGHTING . 8 0.10 0.8
10 R4 16 3 3 LIGHTING . 6 0.10 0.6
11 Y4 16 3 3 LIGHTING . 6 0.10 0.6
12 B4 16 3 3 EXIT SIGN . 7 0.01 0.1
13 R5 16 3 3 LIGHTING 4 0.10 0.4
14 Y5 16 3 3 LIGHTING . 4 0.10 0.4
15 B5 16 SPARE . 0.0
16 R6 16 SPARE 0.0
17 Y6 16 SPARE . 0.0
18 B6 16 SPARE . 0.0
19 R7 16 SPARE 0.0
20 Y7 SPACE 0.0
21 B7 SPACE 0.0
22 R8 . 0.0
23 Y8 . 0.0
24 B8 . 0.0
Dem. Factor ( DF ) Application SUB - 2.5 2.7 2.3
first 100 Kw next 200 Kw remaining Ltg Power Heating A/C TOTAL 7
Lighting 0.9 0.8 0.7 TCL ( kW ) 7.470 0.00 0.00 0.00 7 kilo-Watts
Power 0.7 0.6 0.5 -------- >> MD ( kW ) 6.72 0.00 0.00 0.00 7
Heating 0.6 0.6 0.55 Result. Dem. Factor 0.90 #DIV/0! #DIV/0! #DIV/0! 0.900
A/C 0.8 0.7 0.6

Updated 05/03/2024 21:08:56


ECG DB / PANELBOARD SCHEDULE Proj.No 1658
According to IEC & Master Spec REV.(0)
NOTE
PANEL NO.: ELP-S-5 LOCATION : 5th Floor Notes: 1,4 1- MCCB' s required 6- Led Dimmer Control 10- ELCB, 100 mA required
7- Contactor and PB
2- Isolated Earth Bus 11- ELCB, 30 mA required
Mains Rating Duty Enclosure Dimensions connected to BMS
Fed From : ELP-S-2 Main C.B.: 40 A 380 / 220 V SURFACE W mm 3- 200% neutral size 8- Photocell and Timer 12- Split Bus
Cable No. : F-ELP-S-5 << TCL : 7 kW 5.73 kA-symm. IP42 D mm 4- Indicating Lamps 9- Two-Section Panel 13- Shunt trip
Cable size: 1 // ( 4x 10 ) mm2 Max.Dem.: 6.72 kW 11.76 kA-peak Form 2 H mm 5-Connected to BMS via lighting control system 14- Metering
SER NO. CCT C.B. WIRE ECC CONNECTED LOAD - No.of points per circuit unit CONNECTED LOAD
N
O 1P-C.B.'s REF SIZE SIZE No. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 Load PER - PHASE
T
ROOM / AREA / SUB PANEL / LOAD DISCRIP.
OR # TL CL/ HID Sing Twin Pwr 3 ph Mot/ W.B/ wind split VAV- @ R Y B
E
WAYS NO. A mm2 mm2 Ltg Exit Ltg S/O S/O S/O S/O Fan HD EWH H.P A/C A/C FCU kW kW kW kW
1 R1 16 3 3 LIGHTING . 5 0.10 0.5
2 Y1 16 3 3 LIGHTING . 5 0.10 0.5
3 B1 16 3 3 LIGHTING . 6 0.10 0.6
4 R2 16 3 3 LIGHTING . 4 0.10 0.4
7 5 Y2 16 3 3 LIGHTING . 6 0.10 0.6
6 B2 16 3 3 LIGHTING . 8 0.10 0.8
7 R3 16 3 3 LIGHTING . 6 0.10 0.6
8 Y3 16 3 3 LIGHTING . 6 0.10 0.6
9 B3 16 3 3 LIGHTING . 8 0.10 0.8
10 R4 16 3 3 LIGHTING . 6 0.10 0.6
11 Y4 16 3 3 LIGHTING . 6 0.10 0.6
12 B4 16 3 3 EXIT SIGN . 7 0.01 0.1
13 R5 16 3 3 LIGHTING 4 0.10 0.4
14 Y5 16 3 3 LIGHTING . 4 0.10 0.4
15 B5 16 SPARE . 0.0
16 R6 16 SPARE 0.0
17 Y6 16 SPARE . 0.0
18 B6 16 SPARE . 0.0
19 R7 16 SPARE 0.0
20 Y7 SPACE 0.0
21 B7 SPACE 0.0
22 R8 . 0.0
23 Y8 . 0.0
24 B8 . 0.0
Dem. Factor ( DF ) Application SUB - 2.5 2.7 2.3
first 100 Kw next 200 Kw remaining Ltg Power Heating A/C TOTAL 7
Lighting 0.9 0.8 0.7 TCL ( kW ) 7.470 0.00 0.00 0.00 7 kilo-Watts
Power 0.7 0.6 0.5 -------- >> MD ( kW ) 6.72 0.00 0.00 0.00 7
Heating 0.6 0.6 0.55 Result. Dem. Factor 0.90 #DIV/0! #DIV/0! #DIV/0! 0.900
A/C 0.8 0.7 0.6

Updated 05/03/2024 21:08:57


ECG DB / PANELBOARD SCHEDULE Proj.No 1658
According to IEC & Master Spec REV.(0)
NOTE
PANEL NO.: ELP-S-6 LOCATION : 6th Floor Notes: 1,4 1- MCCB' s required 6- Led Dimmer Control 10- ELCB, 100 mA required
7- Contactor and PB
2- Isolated Earth Bus 11- ELCB, 30 mA required
Mains Rating Duty Enclosure Dimensions connected to BMS
Fed From : ELP-S-2 Main C.B.: 40 A 380 / 220 V SURFACE W mm 3- 200% neutral size 8- Photocell and Timer 12- Split Bus
Cable No. : F-ELP-S-6 << TCL : 6 kW 4.65 kA-symm. IP42 D mm 4- Indicating Lamps 9- Two-Section Panel 13- Shunt trip
Cable size: 1 // ( 4x 10 ) mm2 Max.Dem.: 5.1 kW 9.531 kA-peak Form 2 H mm 5-Connected to BMS via lighting control system 14- Metering
SER NO. CCT C.B. WIRE ECC CONNECTED LOAD - No.of points per circuit unit CONNECTED LOAD
N
O 1P-C.B.'s REF SIZE SIZE No. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 Load PER - PHASE
T
ROOM / AREA / SUB PANEL / LOAD DISCRIP.
OR # TL CL/ HID Sing Twin Pwr 3 ph Mot/ W.B/ wind split VAV- @ R Y B
E
WAYS NO. A mm2 mm2 Ltg Exit Ltg S/O S/O S/O S/O Fan HD EWH H.P A/C A/C FCU kW kW kW kW
1 R1 16 3 3 LIGHTING . 4 0.10 0.4
2 Y1 16 3 3 LIGHTING . 4 0.10 0.4
3 B1 16 3 3 LIGHTING . 4 0.10 0.4
4 R2 16 3 3 LIGHTING . 4 0.10 0.4
7 5 Y2 16 3 3 LIGHTING . 6 0.10 0.6
6 B2 16 3 3 LIGHTING . 8 0.10 0.8
7 R3 16 3 3 LIGHTING . 4 0.10 0.4
8 Y3 16 3 3 LIGHTING . 6 0.10 0.6
9 B3 16 3 3 LIGHTING . 8 0.10 0.8
10 R4 16 3 3 LIGHTING . 4 0.10 0.4
11 Y4 16 3 3 LIGHTING . 4 0.10 0.4
12 B4 16 3 3 EXIT SIGN . 7 0.01 0.1
13 R5 16 3 3 LIGHTING 4 0.0
14 Y5 16 3 3 LIGHTING . 4 0.0
15 B5 16 SPARE . 0.0
16 R6 16 SPARE 0.0
17 Y6 16 SPARE . 0.0
18 B6 16 SPARE . 0.0
19 R7 0.0
20 Y7 0.0
21 B7 0.0
22 R8 . 0.0
23 Y8 . 0.0
24 B8 . 0.0
Dem. Factor ( DF ) Application SUB - 1.6 2.0 2.1
first 100 Kw next 200 Kw remaining Ltg Power Heating A/C TOTAL 6
Lighting 0.9 0.8 0.7 TCL ( kW ) 5.670 0.00 0.00 0.00 6 kilo-Watts
Power 0.7 0.6 0.5 -------- >> MD ( kW ) 5.10 0.00 0.00 0.00 5
Heating 0.6 0.6 0.55 Result. Dem. Factor 0.90 #DIV/0! #DIV/0! #DIV/0! 0.900
A/C 0.8 0.7 0.6

Updated 05/03/2024 21:08:57


ECG DB / PANELBOARD SCHEDULE Proj.No 1658
According to IEC & Master Spec REV.(0)
NOTE
PANEL NO.: ELP-S-7 LOCATION : 7th Floor Notes: 1,4 1- MCCB' s required 6- Led Dimmer Control 10- ELCB, 100 mA required
7- Contactor and PB
2- Isolated Earth Bus 11- ELCB, 30 mA required
Mains SHEET (1 OF 2) Rating Duty Enclosure Dimensions connected to BMS
Fed From : ESMDB-S Main C.B.: 80 A 380 / 220 V SURFACE W mm 3- 200% neutral size 8- Photocell and Timer 12- Split Bus
Cable No. : F-ELP-S-7 << TCL : 30 kW 4.64 kA-symm. IP42 D mm 4- Indicating Lamps 9- Two-Section Panel 13- Shunt trip
Cable size: 1 // ( 4x 35 ) mm2 Max.Dem.: 26.6 kW 9.508 kA-peak Form 2 H mm 5-Connected to BMS via lighting control system 14- Metering
SER NO. CCT C.B. WIRE ECC CONNECTED LOAD - No.of points per circuit unit CONNECTED LOAD
N
O 1P-C.B.'s REF SIZE SIZE No. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 Load PER - PHASE
T
ROOM / AREA / SUB PANEL / LOAD DISCRIP.
OR # TL CL/ HID Sing Twin Pwr 3 ph Mot/ W.B/ wind split VAV- @ R Y B
E
WAYS NO. A mm2 mm2 Ltg Exit Ltg S/O S/O S/O S/O Fan HD EWH H.P A/C A/C FCU kW kW kW kW
1 R1 16 3 3 LIGHTING . 5 0.10 0.5
2 Y1 16 3 3 LIGHTING . 6 0.10 0.6
3 B1 16 3 3 LIGHTING . 5 0.10 0.5
4 R2 16 3 3 LIGHTING . 4 0.10 0.4
7 5 Y2 16 3 3 LIGHTING . 6 0.10 0.6
6 B2 16 3 3 LIGHTING . 8 0.10 0.8
7 R3 16 3 3 LIGHTING . 5 0.10 0.5
8 Y3 16 3 3 LIGHTING . 6 0.10 0.6
9 B3 16 3 3 LIGHTING . 8 0.10 0.8
10 R4 16 3 3 LIGHTING . 6 0.10 0.6
11 Y4 16 3 3 LIGHTING . 6 0.10 0.6
12 B4 16 3 3 EXIT SIGN . 7 0.01 0.1
13 R5 16 3 3 LIGHTING 4 0.10 0.4
14 Y5 16 SPARE . 0.0
15 B5 16 3 3 LIGHTING . 4 0.10 0.4
16 R6 2.4
17 Y6 40 10 16 ELP-S-8 . 7.37 0.00 0.00 0.00 7.37 2.4
18 B6 . 2.6
19 R7 2.4
20 Y7 40 10 16 ELP-S-9 7.37 0.00 0.00 0.00 7.37 2.4
21 B7 2.6
22 R8 . 2.4
23 Y8 40 10 16 ELP-S-10 . 7.47 0.00 0.00 0.00 7.47 2.4
24 B8 . 2.7
Dem. Factor ( DF ) Application SUB - 9.6 9.6 10.4
first 100 Kw next 200 Kw remaining Ltg Power Heating A/C TOTAL 30
Lighting 0.9 0.8 0.7 TCL ( kW ) 29.580 0.00 0.00 0.00 30 kilo-Watts
Power 0.7 0.6 0.5 -------- >> MD ( kW ) 26.62 0.00 0.00 0.00 27
Heating 0.6 0.6 0.55 Result. Dem. Factor 0.90 #DIV/0! #DIV/0! #DIV/0! 0.900
A/C 0.8 0.7 0.6

Updated 05/03/2024 21:08:57


ECG DB / PANELBOARD SCHEDULE Proj.No 1658
According to IEC & Master Spec REV.(0)
NOTE
PANEL NO.: ELP-S-7 LOCATION : 7th Floor Notes: 1,4 1- MCCB' s required 6- Led Dimmer Control 10- ELCB, 100 mA required
7- Contactor and PB
2- Isolated Earth Bus 11- ELCB, 30 mA required
Mains SHEET (2 OF 2) Rating Duty Enclosure Dimensions connected to BMS
Fed From : ESMDB-S Main C.B.: 80 A 380 / 220 V SURFACE W mm 3- 200% neutral size 8- Photocell and Timer 12- Split Bus
Cable No. : F-ELP-S-7 << TCL : 30 kW 4.64 kA-symm. IP42 D mm 4- Indicating Lamps 9- Two-Section Panel 13- Shunt trip
Cable size: 1 // ( 4x 35 ) mm2 Max.Dem.: 26.6 kW 9.508 kA-peak Form 2 H mm 5-Connected to BMS via lighting control system 14- Metering
SER NO. CCT C.B. WIRE ECC CONNECTED LOAD - No.of points per circuit unit CONNECTED LOAD
N
O 1P-C.B.'s REF SIZE SIZE No. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 Load PER - PHASE
T
ROOM / AREA / SUB PANEL / LOAD DISCRIP.
OR # TL CL/ HID Sing Twin Pwr 3 ph Mot/ W.B/ wind split VAV- @ R Y B
E
WAYS NO. A mm2 mm2 Ltg Exit Ltg S/O S/O S/O S/O Fan HD EWH H.P A/C A/C FCU kW kW kW kW
1 R1 16 SPARE . 0.0
2 Y1 16 SPARE . 0.0
3 B1 16 SPARE . 0.0
4 R2 16 SPARE . 0.0
5 Y2 16 SPARE . 0.0
6 B2 16 SPARE . 0.0
7 R3 16 .
8 Y3 .
9 B3 .
10 R4 .
11 Y4 .
12 B4 .
13 R5
14 Y5 .
15 B5 .
16 R6
17 Y6 .
18 B6 .
19 R7
20 Y7
21 B7
22 R8 .
23 Y8 .
24 B8 .
Dem. Factor ( DF ) Application SUB - 9.6 9.6 10.4
first 100 Kw next 200 Kw remaining Ltg Power Heating A/C TOTAL 30
Lighting 0.9 0.8 0.7 TCL ( kW ) 29.580 0.00 0.00 0.00 30 kilo-Watts
Power 0.7 0.6 0.5 -------- >> MD ( kW ) 26.62 0.00 0.00 0.00 27
Heating 0.6 0.6 0.55 Result. Dem. Factor 0.90 #DIV/0! #DIV/0! #DIV/0! 0.900
A/C 0.8 0.7 0.6

Updated 05/03/2024 21:08:57


ECG DB / PANELBOARD SCHEDULE Proj.No 1658
According to IEC & Master Spec REV.(0)
NOTE
PANEL NO.: ELP-S-8 LOCATION : 8th Floor Notes: 1,4 1- MCCB' s required 6- Led Dimmer Control 10- ELCB, 100 mA required
7- Contactor and PB
2- Isolated Earth Bus 11- ELCB, 30 mA required
Mains Rating Duty Enclosure Dimensions connected to BMS
Fed From : ESMDB-S Main C.B.: 40 A 380 / 220 V SURFACE W mm 3- 200% neutral size 8- Photocell and Timer 12- Split Bus
Cable No. : F-ELP-S-8 << TCL : 7 kW 7.48 kA-symm. IP42 D mm 4- Indicating Lamps 9- Two-Section Panel 13- Shunt trip
Cable size: 1 // ( 4x 10 ) mm2 Max.Dem.: 6.63 kW 15.34 kA-peak Form 2 H mm 5-Connected to BMS via lighting control system 14- Metering
SER NO. CCT C.B. WIRE ECC CONNECTED LOAD - No.of points per circuit unit CONNECTED LOAD
N
O 1P-C.B.'s REF SIZE SIZE No. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 Load PER - PHASE
T
ROOM / AREA / SUB PANEL / LOAD DISCRIP.
OR # TL CL/ HID Sing Twin Pwr 3 ph Mot/ W.B/ wind split VAV- @ R Y B
E
WAYS NO. A mm2 mm2 Ltg Exit Ltg S/O S/O S/O S/O Fan HD EWH H.P A/C A/C FCU kW kW kW kW
1 R1 16 3 3 LIGHTING . 5 0.10 0.5
2 Y1 16 3 3 LIGHTING . 6 0.10 0.6
3 B1 16 3 3 LIGHTING . 5 0.10 0.5
4 R2 16 3 3 LIGHTING . 4 0.10 0.4
7 5 Y2 16 3 3 LIGHTING . 6 0.10 0.6
6 B2 16 3 3 LIGHTING . 8 0.10 0.8
7 R3 16 3 3 LIGHTING . 5 0.10 0.5
8 Y3 16 3 3 LIGHTING . 6 0.10 0.6
9 B3 16 3 3 LIGHTING . 8 0.10 0.8
10 R4 16 3 3 LIGHTING . 6 0.10 0.6
11 Y4 16 3 3 LIGHTING . 6 0.10 0.6
12 B4 16 3 3 EXIT SIGN . 7 0.01 0.1
13 R5 16 3 3 LIGHTING 4 0.10 0.4
14 Y5 16 SPARE . 0.0
15 B5 16 3 3 LIGHTING . 4 0.10 0.4
16 R6 16 SPARE 0.0
17 Y6 16 SPARE . 0.0
18 B6 16 SPARE . 0.0
19 R7 16 SPARE 0.0
20 Y7 SPACE 0.0
21 B7 SPACE 0.0
22 R8 . 0.0
23 Y8 . 0.0
24 B8 . 0.0
Dem. Factor ( DF ) Application SUB - 2.4 2.4 2.6
first 100 Kw next 200 Kw remaining Ltg Power Heating A/C TOTAL 7
Lighting 0.9 0.8 0.7 TCL ( kW ) 7.370 0.00 0.00 0.00 7 kilo-Watts
Power 0.7 0.6 0.5 -------- >> MD ( kW ) 6.63 0.00 0.00 0.00 7
Heating 0.6 0.6 0.55 Result. Dem. Factor 0.90 #DIV/0! #DIV/0! #DIV/0! 0.900
A/C 0.8 0.7 0.6

Updated 05/03/2024 21:08:57


ECG DB / PANELBOARD SCHEDULE Proj.No 1658
According to IEC & Master Spec REV.(0)
NOTE
PANEL NO.: ELP-S-9 LOCATION : 9th Floor Notes: 1,4 1- MCCB' s required 6- Led Dimmer Control 10- ELCB, 100 mA required
7- Contactor and PB
2- Isolated Earth Bus 11- ELCB, 30 mA required
Mains Rating Duty Enclosure Dimensions connected to BMS
Fed From : ESMDB-S Main C.B.: 40 A 380 / 220 V SURFACE W mm 3- 200% neutral size 8- Photocell and Timer 12- Split Bus
Cable No. : F-ELP-S-9 << TCL : 7 kW 5.73 kA-symm. IP42 D mm 4- Indicating Lamps 9- Two-Section Panel 13- Shunt trip
Cable size: 1 // ( 4x 10 ) mm2 Max.Dem.: 6.63 kW 11.76 kA-peak Form 2 H mm 5-Connected to BMS via lighting control system 14- Metering
SER NO. CCT C.B. WIRE ECC CONNECTED LOAD - No.of points per circuit unit CONNECTED LOAD
N
O 1P-C.B.'s REF SIZE SIZE No. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 Load PER - PHASE
T
ROOM / AREA / SUB PANEL / LOAD DISCRIP.
OR # TL CL/ HID Sing Twin Pwr 3 ph Mot/ W.B/ wind split VAV- @ R Y B
E
WAYS NO. A mm2 mm2 Ltg Exit Ltg S/O S/O S/O S/O Fan HD EWH H.P A/C A/C FCU kW kW kW kW
1 R1 16 3 3 LIGHTING . 5 0.10 0.5
2 Y1 16 3 3 LIGHTING . 6 0.10 0.6
3 B1 16 3 3 LIGHTING . 5 0.10 0.5
4 R2 16 3 3 LIGHTING . 4 0.10 0.4
7 5 Y2 16 3 3 LIGHTING . 6 0.10 0.6
6 B2 16 3 3 LIGHTING . 8 0.10 0.8
7 R3 16 3 3 LIGHTING . 5 0.10 0.5
8 Y3 16 3 3 LIGHTING . 6 0.10 0.6
9 B3 16 3 3 LIGHTING . 8 0.10 0.8
10 R4 16 3 3 LIGHTING . 6 0.10 0.6
11 Y4 16 3 3 LIGHTING . 6 0.10 0.6
12 B4 16 3 3 EXIT SIGN . 7 0.01 0.1
13 R5 16 3 3 LIGHTING 4 0.10 0.4
14 Y5 16 SPARE . 0.0
15 B5 16 3 3 LIGHTING . 4 0.10 0.4
16 R6 16 SPARE 0.0
17 Y6 16 SPARE . 0.0
18 B6 16 SPARE . 0.0
19 R7 0.0
20 Y7 0.0
21 B7 0.0
22 R8 . 0.0
23 Y8 . 0.0
24 B8 . 0.0
Dem. Factor ( DF ) Application SUB - 2.4 2.4 2.6
first 100 Kw next 200 Kw remaining Ltg Power Heating A/C TOTAL 7
Lighting 0.9 0.8 0.7 TCL ( kW ) 7.370 0.00 0.00 0.00 7 kilo-Watts
Power 0.7 0.6 0.5 -------- >> MD ( kW ) 6.63 0.00 0.00 0.00 7
Heating 0.6 0.6 0.55 Result. Dem. Factor 0.90 #DIV/0! #DIV/0! #DIV/0! 0.900
A/C 0.8 0.7 0.6

Updated 05/03/2024 21:08:57


ECG DB / PANELBOARD SCHEDULE Proj.No 1658
According to IEC & Master Spec REV.(0)
NOTE
PANEL NO.: ELP-S-10 LOCATION : 10th Floor Notes: 1,4 1- MCCB' s required 6- Led Dimmer Control 10- ELCB, 100 mA required
7- Contactor and PB
2- Isolated Earth Bus 11- ELCB, 30 mA required
Mains Rating Duty Enclosure Dimensions connected to BMS
Fed From : ESMDB-S Main C.B.: 40 A 380 / 220 V SURFACE W mm 3- 200% neutral size 8- Photocell and Timer 12- Split Bus
Cable No. : F-ELP-S-10 << TCL : 7 kW 4.65 kA-symm. IP42 D mm 4- Indicating Lamps 9- Two-Section Panel 13- Shunt trip
Cable size: 1 // ( 4x 10 ) mm2 Max.Dem.: 6.72 kW 9.531 kA-peak Form 2 H mm 5-Connected to BMS via lighting control system 14- Metering
SER NO. CCT C.B. WIRE ECC CONNECTED LOAD - No.of points per circuit unit CONNECTED LOAD
N
O 1P-C.B.'s REF SIZE SIZE No. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 Load PER - PHASE
T
ROOM / AREA / SUB PANEL / LOAD DISCRIP.
OR # TL CL/ HID Sing Twin Pwr 3 ph Mot/ W.B/ wind split VAV- @ R Y B
E
WAYS NO. A mm2 mm2 Ltg Exit Ltg S/O S/O S/O S/O Fan HD EWH H.P A/C A/C FCU kW kW kW kW
1 R1 16 3 3 LIGHTING . 5 0.10 0.5
2 Y1 16 3 3 LIGHTING . 6 0.10 0.6
3 B1 16 3 3 LIGHTING . 5 0.10 0.5
4 R2 16 3 3 LIGHTING . 4 0.10 0.4
5 Y2 16 3 3 LIGHTING . 6 0.10 0.6
7 6 B2 16 3 3 LIGHTING . 8 0.10 0.8
7 R3 16 3 3 LIGHTING . 5 0.10 0.5
8 Y3 16 3 3 LIGHTING . 6 0.10 0.6
9 B3 16 3 3 LIGHTING . 8 0.10 0.8
10 R4 16 3 3 LIGHTING . 6 0.10 0.6
11 Y4 16 3 3 LIGHTING . 6 0.10 0.6
12 B4 16 3 3 EXIT SIGN . 7 0.01 0.1
13 R5 16 3 3 LIGHTING 4 0.10 0.4
14 Y5 16 SPARE . 0.0
15 B5 16 3 3 LIGHTING . 5 0.10 0.5
16 R6 16 SPARE 0.0
17 Y6 16 SPARE . 0.0
18 B6 16 SPARE . 0.0
19 R7 0.0
20 Y7 0.0
21 B7 0.0
22 R8 . 0.0
23 Y8 . 0.0
24 B8 . 0.0
Dem. Factor ( DF ) Application SUB - 2.4 2.4 2.7
first 100 Kw next 200 Kw remaining Ltg Power Heating A/C TOTAL 7
Lighting 0.9 0.8 0.7 TCL ( kW ) 7.470 0.00 0.00 0.00 7 kilo-Watts
Power 0.7 0.6 0.5 -------- >> MD ( kW ) 6.72 0.00 0.00 0.00 7
Heating 0.6 0.6 0.55 Result. Dem. Factor 0.90 #DIV/0! #DIV/0! #DIV/0! 0.900
A/C 0.8 0.7 0.6

Updated 05/03/2024 21:08:57


ECG DB / PANELBOARD SCHEDULE Proj.No 1658
According to IEC & Master Spec REV.(0)
NOTE
PANEL NO.: UDB-S LOCATION : Basement Floor Notes: 1,12,4 1- MCCB' s required 6- Led Dimmer Control 10- ELCB, 100 mA required
7- Contactor and PB
2- Isolated Earth Bus 11- ELCB, 30 mA required
Mains Rating Duty Enclosure Dimensions connected to BMS
Fed From : UPS-S Main C.B.: 630 A 380 / 220 V SURFACE W mm 3- 200% neutral size 8- Photocell and Timer 12- over&under voltage
Cable No. : F-UDB-S << TCL : 204 kW 14 kA-symm. IP42 D mm 4- Indicating Lamps 9- Two-Section Panel 13- Shunt trip
Cable size: 2 // ( 4 x 185 ) mm2 Max.Dem.: 132.22 kW 28 kA-peak Form 2 H mm 5-Connected to BMS via lighting control system 14- Metering
SER NO.CCT C.B. WIRE ECC CONNECTED LOAD - No.of points per circuit unit CONNECTED LOAD
N
O 1P-C.B.'sREF SIZE SIZE No. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 Load PER - PHASE
T
ROOM / AREA / SUB PANEL / LOAD DISCRIP.
OR # TL CL/ HID Sing Twin Pwr 3 ph Mot/ W.B/ wind split VAV- @ R Y B
E
WAYS NO. A mm2 mm2 Ltg Exit Ltg S/O S/O S/O S/O Fan HD EWH H.P A/C A/C FCU kW kW kW kW
1 R1 12.3
2 Y1 63 35 16 UP-S-G . 0.00 35.00 0.00 0.00 35.00 10.3
3 B1 12.4
4 R2 3.3
5 Y2 40 16 16 UP-S-F . 0.00 12.30 0.00 0.00 12.30 4.5
6 B2 4.5
7 R3 9.8
8 Y3 100 50 25 UP-S-2 . 0.00 37.10 0.00 0.00 37.10 13.1
9 B3 14.2
10 R4 14.3
11 Y4 100 50 25 UP-S-3 . 0.00 37.10 0.00 0.00 37.10 13.1
12 B4 9.7
13 R5 16.8
14 Y5 125 70 35 UP-S-4 . 0.00 46.40 0.00 0.00 46.40 15.6
15 B5 14.0
16 R6 11.9
17 Y6 100 70 35 UP-S-7 . 0.00 35.80 0.00 0.00 35.80 11.6
18 B6 12.3
19 R7
20 Y7 40 SPARE .
21 B7
22 R8
23 Y8 100 SPARE .
24 B8
Dem. Factor ( DF ) Application SUB - 68.4 68.2 67.1
first 100 Kw next 200 Kw remaining Ltg Power Heating A/C TOTAL 204
Lighting 0.9 0.8 0.7 TCL ( kW ) 0 203.70 0.00 0.00 204 kilo-Watts
Power 0.7 0.6 0.5 -------- >> MD ( kW ) 0.00 132.22 0.00 0.00 132
Heating 0.6 0.6 0.55 Result. Dem. Factor #DIV/0! 0.65 #DIV/0! #DIV/0! 0.649
A/C 0.8 0.7 0.6

Updated 05/03/2024 21:08:57


ECG DB / PANELBOARD SCHEDULE Proj.No 1658
According to IEC & Master Spec REV.(0)
NOTE
PANEL NO.: UP-S-G LOCATION : Ground Floor Notes: 1,4 1- MCCB' s required 6- Led Dimmer Control 10- ELCB, 100 mA required
7- Contactor and PB
2- Isolated Earth Bus 11- ELCB, 30 mA required
Mains Rating Duty Enclosure Dimensions connected to BMS
Fed From : UDB-S Main C.B.: 63 A 380 / 220 V SURFACE W mm 3- 200% neutral size 8- Photocell and Timer 12- Split Bus
Cable No. : F-UP-S-G << TCL : 35 kW 8.69 kA-symm. IP42 D mm 4- Indicating Lamps 9- Two-Section Panel 13- Shunt trip
Cable size: 1 // ( 4x 35 ) mm2 Max.Dem.: 24.5 kW 17.81 kA-peak Form 2 H mm 5-Connected to BMS via lighting control system 14- Metering
SER NO. CCT C.B. WIRE ECC CONNECTED LOAD - No.of points per circuit unit CONNECTED LOAD
N
O 1P-C.B.'s REF SIZE SIZE No. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 Load PER - PHASE
T
ROOM / AREA / SUB PANEL / LOAD DISCRIP.
OR # TL CL/ HID Sing Twin Pwr 3 ph Mot/ W.B/ wind split VAV- @ R Y B
E
WAYS NO. A mm2 mm2 Ltg Exit Ltg S/O S/O S/O S/O Fan HD EWH H.P A/C A/C FCU kW kW kW kW
1 R1 20 4 4 CAMERA . 3 0.10 0.3
2 Y1 20 4 4 CAMERA . 3 0.10 0.3
3 B1 20 4 4 CAMERA . 4 0.10 0.4
4 R2 20 4 4 CAMERA . 3 0.10 0.3
5 Y2 20 4 4 CAMERA . 4 0.10 0.4
6 B2 20 4 4 CAMERA . 3 0.10 0.3
7 R3 20 4 4 WI FI + CAMERA . 4 0.10 0.4
8 Y3 20 4 4 SOCKET OUTLET . 4 0.20 0.8
9 B3 20 4 4 SOCKET OUTLET . 4 0.20 0.8
10 R4 20 SPARE . 0.0
11 Y4 20 SPARE . 0.0
12 B4 20 SPARE . 0.0
13 R5 20 SPARE 0.0
14 Y5 20 4 4 WATER LEAK PANEL . 1 0.50 0.5
15 B5 20 4 4 BASEMENT FLOOR CAMERAS . 6 0.10 0.6
16 R6 32 6 6 IT RACK 1 3.00 3.0
17 Y6 20 SPARE . 0.0
18 B6 32 6 6 IT RACK . 1 3.00 3.0
19 R7 8.3
20 Y7 40 25 16 UP-S-M 1 23.90 8.3
21 B7 7.3
22 R8 . 0.0
23 Y8 . 0.0
24 B8 . 0.0
Dem. Factor ( DF ) Application SUB - 12.3 10.3 12.4
first 100 Kw next 200 Kw remaining Ltg Power Heating A/C TOTAL 35
Lighting 0.9 0.8 0.7 TCL ( kW ) 0.000 35.00 0.00 0.00 35 kilo-Watts
Power 0.7 0.6 0.5 -------- >> MD ( kW ) 0.00 24.50 0.00 0.00 25
Heating 0.6 0.6 0.55 Result. Dem. Factor #DIV/0! 0.70 #DIV/0! #DIV/0! 0.700
A/C 0.8 0.7 0.6

Updated 05/03/2024 21:08:57


ECG DB / PANELBOARD SCHEDULE Proj.No 1658
According to IEC & Master Spec REV.(0)
NOTE
PANEL NO.: UP-S-M LOCATION : Mezzanine Floor Notes: 1,4 1- MCCB' s required 6- Led Dimmer Control 10- ELCB, 100 mA required
7- Contactor and PB
2- Isolated Earth Bus 11- ELCB, 30 mA required
Mains SHEET (1 OF 2) Rating Duty Enclosure Dimensions connected to BMS
Fed From : UP-S-G Main C.B.: 40 A 380 / 220 V SURFACE W mm 3- 200% neutral size 8- Photocell and Timer 12- Split Bus
Cable No. : F-UP-S-M << TCL : 15 kW 6.04 kA-symm. IP42 D mm 4- Indicating Lamps 9- Two-Section Panel 13- Shunt trip
Cable size: 1 // ( 4x 25 ) mm2 Max.Dem.: 10.5 kW 12.39 kA-peak Form 2 H mm 5-Connected to BMS via lighting control system 14- Metering
SER NO. CCT C.B. WIRE ECC CONNECTED LOAD - No.of points per circuit unit CONNECTED LOAD
N
O 1P-C.B.'s REF SIZE SIZE No. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 Load PER - PHASE
T
ROOM / AREA / SUB PANEL / LOAD DISCRIP.
OR # TL CL/ HID Sing Twin Pwr 3 ph Mot/ W.B/ wind split VAV- @ R Y B
E
WAYS NO. A mm2 mm2 Ltg Exit Ltg S/O S/O S/O S/O Fan HD EWH H.P A/C A/C FCU kW kW kW kW
1 R1 20 4 4 CAMERA . 2 0.10 0.2
2 Y1 20 SPARE . 0.20 0.0
3 B1 20 4 4 WI FI + CAMERA + CLOCK . 4 0.10 0.4
11 4 R2 20 4 4 SOCKET OUTLET . 1 3 0.20 0.8
11 5 Y2 20 4 4 SOCKET OUTLET . 1 3 0.20 0.8
11 6 B2 20 4 4 SOCKET OUTLET . 1 3 0.20 0.8
11 7 R3 20 4 4 SOCKET OUTLET . 1 3 0.20 0.8
11 8 Y3 20 4 4 SOCKET OUTLET . 1 3 0.20 0.8
11 9 B3 20 4 4 SOCKET OUTLET . 1 3 0.20 0.8
11 10 R4 20 4 4 SOCKET OUTLET . 1 3 0.20 0.8
11 11 Y4 20 4 4 SOCKET OUTLET . 1 3 0.20 0.8
11 12 B4 20 4 4 SOCKET OUTLET . 1 3 0.20 0.8
11 13 R5 20 4 4 SOCKET OUTLET 1 3 0.20 0.8
11 14 Y5 20 4 4 SOCKET OUTLET . 1 3 0.20 0.8
11 15 B5 20 4 4 SOCKET OUTLET . 1 3 0.20 0.8
11 16 R6 20 4 4 SOCKET OUTLET 4 0.20 0.8
17 Y6 20 SPARE . 0.0
11 18 B6 20 4 4 SOCKET OUTLET . 3 0.20 0.6
11 19 R7 20 4 4 SOCKET OUTLET 2 0.20 0.4
11 20 Y7 20 4 4 B.H.U 3 0.20 0.6
11 21 B7 20 4 4 SOCKET OUTLET 2 0.20 0.4
11 22 R8 20 4 4 B.H.U . 3 0.20 0.6
11 23 Y8 20 4 4 B.H.U . 4 0.20 0.8
11 24 B8 20 4 4 B.H.U . 3 0.20 0.6
Dem. Factor ( DF ) Application SUB - 5.2 4.6 5.2
first 100 Kw next 200 Kw remaining Ltg Power Heating A/C TOTAL 15
Lighting 0.9 0.8 0.7 TCL ( kW ) 0.000 15.00 0.00 0.00 15 kilo-Watts
Power 0.7 0.6 0.5 -------- >> MD ( kW ) 0.00 10.50 0.00 0.00 11
Heating 0.6 0.6 0.55 Result. Dem. Factor #DIV/0! 0.70 #DIV/0! #DIV/0! 0.700
A/C 0.8 0.7 0.6

Updated 05/03/2024 21:08:57


ECG DB / PANELBOARD SCHEDULE Proj.No 1658
According to IEC & Master Spec REV.(0)
NOTE
PANEL NO.: UP-S-M LOCATION : Mezzanine Floor Notes: 1,4 1- MCCB' s required 6- Led Dimmer Control 10- ELCB, 100 mA required
7- Contactor and PB
2- Isolated Earth Bus 11- ELCB, 30 mA required
Mains SHEET (2 OF 2) Rating Duty Enclosure Dimensions connected to BMS
Fed From : UP-S-G Main C.B.: 40 A 380 / 220 V SURFACE W mm 3- 200% neutral size 8- Photocell and Timer 12- Split Bus
Cable No. : F-UP-S-M << TCL : 24 kW 6.04 kA-symm. IP42 D mm 4- Indicating Lamps 9- Two-Section Panel 13- Shunt trip
Cable size: 1 // ( 4x 25 ) mm2 Max.Dem.: 16.7 kW 12.39 kA-peak Form 2 H mm 5-Connected to BMS via lighting control system 14- Metering
SER NO. CCT C.B. WIRE ECC CONNECTED LOAD - No.of points per circuit unit CONNECTED LOAD
N
O 1P-C.B.'s REF SIZE SIZE No. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 Load PER - PHASE
T
ROOM / AREA / SUB PANEL / LOAD DISCRIP.
OR # TL CL/ HID Sing Twin Pwr 3 ph Mot/ W.B/ wind split VAV- @ R Y B
E
WAYS NO. A mm2 mm2 Ltg Exit Ltg S/O S/O S/O S/O Fan HD EWH H.P A/C A/C FCU kW kW kW kW
25 R9 20 SPARE . 0.0
26 Y9 20 SPARE . 0.10 0.0
27 B9 20 4 4 CAMERA . 3 0.10 0.3
28 R10 20 4 4 WI FI . 1 0.10 0.1
29 Y10 20 4 4 DIGITAL CLOCK SOCKET . 1 0.10 0.1
30 B10 20 4 4 DOOR CONTROLLER SOCKET OUTLET . 2 0.20 0.4
31 R11 32 6 6 IT RACK . 1 3.00 3.0
32 Y11 32 6 6 IT RACK . 1 3.00 3.0
33 B11 20 4 4 CAMERA . 8 0.10 0.8
34 R12 20 SPARE . 0.0
11 35 Y12 20 4 4 B.H.U . 3 0.20 0.6
36 B12 20 4 4 SOCKET OUTLET . 3 0.20 0.6
37 R13 0.0
38 Y13 . 0.0
39 B13 . 0.0
40 R14 0.0
41 Y14 . 0.0
42 B14 . 0.0
43 R15 0.0
44 Y15 0.0
45 B15 0.0
46 R16 . 0.0
47 Y16 . 0.0
48 B16 . 0.0
Dem. Factor ( DF ) Application SUB - 8.3 8.3 7.3
first 100 Kw next 200 Kw remaining Ltg Power Heating A/C TOTAL 24
Lighting 0.9 0.8 0.7 TCL ( kW ) 0.000 23.90 0.00 0.00 24 kilo-Watts
Power 0.7 0.6 0.5 -------- >> MD ( kW ) 0.00 16.73 0.00 0.00 17
Heating 0.6 0.6 0.55 Result. Dem. Factor #DIV/0! 0.70 #DIV/0! #DIV/0! 0.700
A/C 0.8 0.7 0.6

Updated 05/03/2024 21:08:57


ECG DB / PANELBOARD SCHEDULE Proj.No 1658
According to IEC & Master Spec REV.(0)
NOTE
PANEL NO.: UP-S-F LOCATION : First Floor Notes: 1,4 1- MCCB' s required 6- Led Dimmer Control 10- ELCB, 100 mA required
7- Contactor and PB
2- Isolated Earth Bus 11- ELCB, 30 mA required
Mains Rating Duty Enclosure Dimensions connected to BMS
Fed From : UDB-S Main C.B.: 40 A 380 / 220 V SURFACE W mm 3- 200% neutral size 8- Photocell and Timer 12- Split Bus
Cable No. : F-UP-S-F << TCL : 12 kW 3.48 kA-symm. IP42 D mm 4- Indicating Lamps 9- Two-Section Panel 13- Shunt trip
Cable size: 1 // ( 4x 16 ) mm2 Max.Dem.: 8.61 kW 7.144 kA-peak Form 2 H mm 5-Connected to BMS via lighting control system 14- Metering
SER NO. CCT C.B. WIRE ECC CONNECTED LOAD - No.of points per circuit unit CONNECTED LOAD
N
O 1P-C.B.'s REF SIZE SIZE No. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 Load PER - PHASE
T
ROOM / AREA / SUB PANEL / LOAD DISCRIP.
OR # TL CL/ HID Sing Twin Pwr 3 ph Mot/ W.B/ wind split VAV- @ R Y B
E
WAYS NO. A mm2 mm2 Ltg Exit Ltg S/O S/O S/O S/O Fan HD EWH H.P A/C A/C FCU kW kW kW kW
11 1 R1 20 4 4 B.H.U . 3 0.20 0.6
11 2 Y1 20 4 4 B.H.U . 2 0.20 0.4
11 3 B1 20 4 4 B.H.U . 2 0.20 0.4
11 4 R2 20 4 4 B.H.U . 2 0.20 0.4
5 Y2 32 6 6 IT RACK . 1 3.00 3.0
6 B2 32 6 6 IT RACK . 1 3.00 3.0
7 R3 20 4 4 SFACP . 1 1.00 1.0
8 Y3 20 4 4 CAMERA . 5 0.10 0.5
9 B3 20 4 4 CAMERA . 3 0.10 0.3
10 R4 20 4 4 CAMERA 7 0.10 0.7
11 Y4 20 4 4 SOCKET OUTLET . 3 0.20 0.6
12 B4 20 4 4 SOCKET OUTLET . 1 3 0.20 0.8
13 R5 20 4 4 SOCKET OUTLET . 3 0.20 0.6
14 Y5 20 SPARE . 0.0
15 B5 20 SPARE 0.0
16 R6 20 4 4 SOCKET OUTLET 5 0.20 0.0
17 Y6 20 SPARE 0.0
18 B6 20 SPARE 0.0
19 R7 20 SPARE 0.0
20 Y7 SPACE 0.0
21 B7 SPACE 0.0
22 R8 0.0
23 Y8 0.0
24 B8 0.0
Dem. Factor ( DF ) Application SUB - 3.3 4.5 4.5
first 100 Kw next 200 Kw remaining Ltg Power Heating A/C TOTAL 12
Lighting 0.9 0.8 0.7 TCL ( kW ) 0.000 12.30 0.00 0.00 12 kilo-Watts
Power 0.7 0.6 0.5 -------- >> MD ( kW ) 0.00 8.61 0.00 0.00 9
Heating 0.6 0.6 0.55 Result. Dem. Factor #DIV/0! 0.70 #DIV/0! #DIV/0! 0.700
A/C 0.8 0.7 0.6

Updated 05/03/2024 21:08:57


ECG DB / PANELBOARD SCHEDULE Proj.No 1658
According to IEC & Master Spec REV.(0)
NOTE
PANEL NO.: UP-S-2 LOCATION : 2nd Floor Notes: 1,4 1- MCCB' s required 6- Led Dimmer Control 10- ELCB, 100 mA required
7- Contactor and PB
2- Isolated Earth Bus 11- ELCB, 30 mA required
Mains SHEET (1 OF 2) Rating Duty Enclosure Dimensions connected to BMS
Fed From : UDB-S Main C.B.: 100 A 380 / 220 V SURFACE W mm 3- 200% neutral size 8- Photocell and Timer 12- Split Bus
Cable No. : F-UP-S-2 << TCL : 37 kW 6.83 kA-symm. IP42 D mm 4- Indicating Lamps 9- Two-Section Panel 13- Shunt trip
Cable size: 1 // ( 4x 50 ) mm2 Max.Dem.: 26 kW 14 kA-peak Form 2 H mm 5-Connected to BMS via lighting control system 14- Metering
SER NO. CCT C.B. WIRE ECC CONNECTED LOAD - No.of points per circuit unit CONNECTED LOAD
N
O 1P-C.B.'s REF SIZE SIZE No. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 Load PER - PHASE
T
ROOM / AREA / SUB PANEL / LOAD DISCRIP.
OR # TL CL/ HID Sing Twin Pwr 3 ph Mot/ W.B/ wind split VAV- @ R Y B
E
WAYS NO. A mm2 mm2 Ltg Exit Ltg S/O S/O S/O S/O Fan HD EWH H.P A/C A/C FCU kW kW kW kW
11 1 R1 20 4 4 B.H.U . 2 0.20 0.4
2 Y1 20 4 4 SOCKET OUTLET . 5 0.20 1.0
3 B1 20 4 4 CAMERAS . 6 0.10 0.6
4 R2 20 4 4 WI FI . 3 0.10 0.3
5 Y2 32 6 6 IT RACK 1 3.00 3.0
6 B2 20 SPARE . 0.0
7 R3 20 16 16 IPP-2-3 . 1 9.10 9.1
8 Y3 20 16 16 IPP-2-1 . 1 9.10 9.1
9 B3 20 16 16 IPP-2-2 . 1 9.10 9.1
10 R4 20 SPARE 0.0
11 Y4 20 SPARE 0.0
12 B4 20 16 16 IPP-2-4 1 4.50 4.5
13 R5 0.0
14 Y5 0.0
15 B5 0.0
16 R6 0.0
17 Y6 0.0
18 B6 0.0
19 R7 0.0
20 Y7 0.0
21 B7 0.0
22 R8
23 Y8
24 B8
Dem. Factor ( DF ) Application SUB - 9.8 13.1 14.2
first 100 Kw next 200 Kw remaining Ltg Power Heating A/C TOTAL 37
Lighting 0.9 0.8 0.7 TCL ( kW ) 0.000 37.10 0.00 0.00 37 kilo-Watts
Power 0.7 0.6 0.5 -------- >> MD ( kW ) 0.00 25.97 0.00 0.00 26
Heating 0.6 0.6 0.55 Result. Dem. Factor #DIV/0! 0.70 #DIV/0! #DIV/0! 0.700
A/C 0.8 0.7 0.6

Updated 05/03/2024 21:08:57


ECG DB / PANELBOARD SCHEDULE Proj.No 1658
According to IEC & Master Spec REV.(0)
NOTE
PANEL NO.: UP-S-3 LOCATION : 3rd Floor Notes: 1,4 1- MCCB' s required 6- Led Dimmer Control 10- ELCB, 100 mA required
7- Contactor and PB
2- Isolated Earth Bus 11- ELCB, 30 mA required
Mains Rating Duty Enclosure Dimensions connected to BMS
Fed From : UDB-S Main C.B.: 100 A 380 / 220 V SURFACE W mm 3- 200% neutral size 8- Photocell and Timer 12- Split Bus
Cable No. : F-UP-S-3 << TCL : 37 kW 8.47 kA-symm. IP42 D mm 4- Indicating Lamps 9- Two-Section Panel 13- Shunt trip
Cable size: 1 // ( 4x 50 ) mm2 Max.Dem.: 26 kW 17.36 kA-peak Form 2 H mm 5-Connected to BMS via lighting control system 14- Metering
SER NO. CCT C.B. WIRE ECC CONNECTED LOAD - No.of points per circuit unit CONNECTED LOAD
N
O 1P-C.B.'s REF SIZE SIZE No. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 Load PER - PHASE
T
ROOM / AREA / SUB PANEL / LOAD DISCRIP.
OR # TL CL/ HID Sing Twin Pwr 3 ph Mot/ W.B/ wind split VAV- @ R Y B
E
WAYS NO. A mm2 mm2 Ltg Exit Ltg S/O S/O S/O S/O Fan HD EWH H.P A/C A/C FCU kW kW kW kW
11 1 R1 20 4 4 B.H.U . 2 0.20 0.4
2 Y1 20 4 4 SOCKET OUTLET . 5 0.20 1.0
3 B1 20 4 4 CAMERAS . 6 0.10 0.6
4 R2 20 4 4 WI FI . 3 0.10 0.3
5 Y2 32 6 6 IT RACK 1 3.00 3.0
6 B2 20 SPARE . 0.0
7 R3 20 16 16 IPP-3-3 . 1 9.10 9.1
8 Y3 20 16 16 IPP-3-1 . 1 9.10 9.1
9 B3 20 16 16 IPP-3-2 . 1 9.10 9.1
10 R4 20 16 16 IPP-3-4 1 4.50 4.5
11 Y4 20 SPARE 0.0
12 B4 SPACE 0.0
13 R5 0.0
14 Y5 0.0
15 B5 0.0
16 R6 0.0
17 Y6 0.0
18 B6 0.0
19 R7 0.0
20 Y7 0.0
21 B7 0.0
22 R8 . 0.0
23 Y8 . 0.0
24 B8 . 0.0
Dem. Factor ( DF ) Application SUB - 14.3 13.1 9.7
first 100 Kw next 200 Kw remaining Ltg Power Heating A/C TOTAL 37
Lighting 0.9 0.8 0.7 TCL ( kW ) 0.000 37.10 0.00 0.00 37 kilo-Watts
Power 0.7 0.6 0.5 -------- >> MD ( kW ) 0.00 25.97 0.00 0.00 26
Heating 0.6 0.6 0.55 Result. Dem. Factor #DIV/0! 0.70 #DIV/0! #DIV/0! 0.700
A/C 0.8 0.7 0.6

Updated 05/03/2024 21:08:57


ECG DB / PANELBOARD SCHEDULE Proj.No 1658
According to IEC & Master Spec REV.(0)
NOTE
PANEL NO.: UP-S-4 LOCATION : 4th Floor Notes: 1,4 1- MCCB' s required 6- Led Dimmer Control 10- ELCB, 100 mA required
7- Contactor and PB
2- Isolated Earth Bus 11- ELCB, 30 mA required
Mains SHEET (1 OF 2) Rating Duty Enclosure Dimensions connected to BMS
Fed From : UDB-S Main C.B.: 125 A 380 / 220 V SURFACE W mm 3- 200% neutral size 8- Photocell and Timer 12- Split Bus
Cable No. : F-UP-S-4 << TCL : 34 kW 7.44 kA-symm. IP42 D mm 4- Indicating Lamps 9- Two-Section Panel 13- Shunt trip
Cable size: 1 // ( 4x 70 ) mm2 Max.Dem.: 23.7 kW 15.26 kA-peak Form 2 H mm 5-Connected to BMS via lighting control system 14- Metering
SER NO. CCT C.B. WIRE ECC CONNECTED LOAD - No.of points per circuit unit CONNECTED LOAD
N
O 1P-C.B.'s REF SIZE SIZE No. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 Load PER - PHASE
T
ROOM / AREA / SUB PANEL / LOAD DISCRIP.
OR # TL CL/ HID Sing Twin Pwr 3 ph Mot/ W.B/ wind split VAV- @ R Y B
E
WAYS NO. A mm2 mm2 Ltg Exit Ltg S/O S/O S/O S/O Fan HD EWH H.P A/C A/C FCU kW kW kW kW
11 1 R1 20 4 4 B.H.U . 6 0.20 1.2
11 2 Y1 20 4 4 B.H.U . 4 0.20 0.8
11 3 B1 20 4 4 B.H.U . 4 0.20 0.8
11 4 R2 20 4 4 B.H.U . 4 0.20 0.8
11 5 Y2 20 4 4 B.H.U . 4 0.20 0.8
11 6 B2 20 4 4 B.H.U . 4 0.20 0.8
11 7 R3 20 4 4 B.H.U . 6 0.20 1.2
11 8 Y3 20 4 4 B.H.U . 6 0.20 1.2
11 9 B3 20 4 4 B.H.U . 4 0.20 0.8
11 10 R4 20 4 4 B.H.U . 4 0.20 0.8
11 11 Y4 20 4 4 B.H.U . 4 0.20 0.8
11 12 B4 20 4 4 B.H.U . 4 0.20 0.8
11 13 R5 20 4 4 B.H.U 4 0.20 0.8
11 14 Y5 20 4 4 B.H.U . 2 0.20 0.4
15 B5 20 4 4 SOCKET OUTLET . 5 0.20 1.0
16 R6 20 SPARE 0.0
17 Y6 20 4 4 CAMERAS . 8 0.10 0.8
18 B6 20 4 4 WI FI . 1 0.10 0.1
19 R7 20 SPARE 0.0
20 Y7 20 SPARE 0.0
21 B7 32 6 6 IT RACK 1 3.00 3.0
22 R8 7.8
23 Y8 40 50 25 UP-S-5 . 0 16.90 0.00 0.00 16.90 4.8
24 B8 4.3
Dem. Factor ( DF ) Application SUB - 12.6 9.6 11.6
first 100 Kw next 200 Kw remaining Ltg Power Heating A/C TOTAL 34
Lighting 0.9 0.8 0.7 TCL ( kW ) 0.000 33.80 0.00 0.00 34 kilo-Watts
Power 0.7 0.6 0.5 -------- >> MD ( kW ) 0.00 23.66 0.00 0.00 24
Heating 0.6 0.6 0.55 Result. Dem. Factor #DIV/0! 0.70 #DIV/0! #DIV/0! 0.700
A/C 0.8 0.7 0.6

Updated 05/03/2024 21:08:57


ECG DB / PANELBOARD SCHEDULE Proj.No 1658
According to IEC & Master Spec REV.(0)
NOTE
PANEL NO.: UP-S-4 LOCATION : 4th Floor Notes: 1,4 1- MCCB' s required 6- Led Dimmer Control 10- ELCB, 100 mA required
7- Contactor and PB
2- Isolated Earth Bus 11- ELCB, 30 mA required
Mains SHEET (2 OF 2) Rating Duty Enclosure Dimensions connected to BMS
Fed From : UDB-S Main C.B.: 125 A 380 / 220 V SURFACE W mm 3- 200% neutral size 8- Photocell and Timer 12- Split Bus
Cable No. : F-UP-S-4 << TCL : 46 kW 7.44 kA-symm. IP42 D mm 4- Indicating Lamps 9- Two-Section Panel 13- Shunt trip
Cable size: 1 // ( 4x 70 ) mm2 Max.Dem.: 32.5 kW 15.26 kA-peak Form 2 H mm 5-Connected to BMS via lighting control system 14- Metering
SER NO. CCT C.B. WIRE ECC CONNECTED LOAD - No.of points per circuit unit CONNECTED LOAD
N
O 1P-C.B.'s REF SIZE SIZE No. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 Load PER - PHASE
T
ROOM / AREA / SUB PANEL / LOAD DISCRIP.
OR # TL CL/ HID Sing Twin Pwr 3 ph Mot/ W.B/ wind split VAV- @ R Y B
E
WAYS NO. A mm2 mm2 Ltg Exit Ltg S/O S/O S/O S/O Fan HD EWH H.P A/C A/C FCU kW kW kW kW
25 R9 4.2
26 Y9 40 50 25 UP-S-6 . 0 12.60 0.00 0.00 12.60 6.0
27 B9 2.4
28 R10 20 SPARE
29 Y10 20 SPARE
30 B10 20 SPARE
31 R11
32 Y11 40 SPARE .
33 B11
34 R12 .
35 Y12 .
36 B12 .
37 R13
38 Y13 .
39 B13 .
40 R14
41 Y14 .
42 B14 .
43 R15
44 Y15
45 B15
46 R16 .
47 Y16 .
48 B16 .
Dem. Factor ( DF ) Application SUB - 16.8 15.6 14.0
first 100 Kw next 200 Kw remaining Ltg Power Heating A/C TOTAL 46
Lighting 0.9 0.8 0.7 TCL ( kW ) 0.000 46.40 0.00 0.00 46 kilo-Watts
Power 0.7 0.6 0.5 -------- >> MD ( kW ) 0.00 32.48 0.00 0.00 32
Heating 0.6 0.6 0.55 Result. Dem. Factor #DIV/0! 0.70 #DIV/0! #DIV/0! 0.700
A/C 0.8 0.7 0.6

Updated 05/03/2024 21:08:57


ECG DB / PANELBOARD SCHEDULE Proj.No 1658
According to IEC & Master Spec REV.(0)
NOTE
PANEL NO.: UP-S-5 LOCATION : 5th Floor Notes: 1,4 1- MCCB' s required 6- Led Dimmer Control 10- ELCB, 100 mA required
7- Contactor and PB
2- Isolated Earth Bus 11- ELCB, 30 mA required
Mains Rating Duty Enclosure Dimensions connected to BMS
Fed From : UP-S-4 Main C.B.: 40 A 380 / 220 V SURFACE W mm 3- 200% neutral size 8- Photocell and Timer 12- Split Bus
Cable No. : F-UP-S-5 << TCL : 17 kW 14.07 kA-symm. IP42 D mm 4- Indicating Lamps 9- Two-Section Panel 13- Shunt trip
Cable size: 1 // ( 4x 50 ) mm2 Max.Dem.: 11.8 kW 28.85 kA-peak Form 2 H mm 5-Connected to BMS via lighting control system 14- Metering
SER NO. CCT C.B. WIRE ECC CONNECTED LOAD - No.of points per circuit unit CONNECTED LOAD
N
O 1P-C.B.'s REF SIZE SIZE No. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 Load PER - PHASE
T
ROOM / AREA / SUB PANEL / LOAD DISCRIP.
OR # TL CL/ HID Sing Twin Pwr 3 ph Mot/ W.B/ wind split VAV- @ R Y B
E
WAYS NO. A mm2 mm2 Ltg Exit Ltg S/O S/O S/O S/O Fan HD EWH H.P A/C A/C FCU kW kW kW kW
11 1 R1 20 4 4 B.H.U . 6 0.20 1.2
11 2 Y1 20 4 4 B.H.U . 4 0.20 0.8
11 3 B1 20 4 4 B.H.U . 4 0.20 0.8
11 4 R2 20 4 4 B.H.U . 4 0.20 0.8
11 5 Y2 20 4 4 B.H.U . 4 0.20 0.8
11 6 B2 20 4 4 B.H.U . 4 0.20 0.8
11 7 R3 20 4 4 B.H.U . 6 0.20 1.2
11 8 Y3 20 4 4 B.H.U . 6 0.20 1.2
11 9 B3 20 4 4 B.H.U . 4 0.20 0.8
11 10 R4 20 4 4 B.H.U . 4 0.20 0.8
11 11 Y4 20 4 4 B.H.U . 4 0.20 0.8
11 12 B4 20 4 4 B.H.U . 4 0.20 0.8
11 13 R5 20 4 4 B.H.U 4 0.20 0.8
11 14 Y5 20 4 4 B.H.U . 2 0.20 0.4
15 B5 20 4 4 SOCKET OUTLET . 5 0.20 1.0
16 R6 20 SPARE 0.0
17 Y6 20 4 4 CAMERAS . 8 0.10 0.8
18 B6 20 4 4 WI FI . 1 0.10 0.1
19 R7 32 6 6 IT RACK 1 3.00 3.0
20 Y7 0.0
21 B7 0.0
22 R8 . 0.0
23 Y8 . 0.0
24 B8 . 0.0
Dem. Factor ( DF ) Application SUB - 7.8 4.8 4.3
first 100 Kw next 200 Kw remaining Ltg Power Heating A/C TOTAL 17
Lighting 0.9 0.8 0.7 TCL ( kW ) 0.000 16.90 0.00 0.00 17 kilo-Watts
Power 0.7 0.6 0.5 -------- >> MD ( kW ) 0.00 11.83 0.00 0.00 12
Heating 0.6 0.6 0.55 Result. Dem. Factor #DIV/0! 0.70 #DIV/0! #DIV/0! 0.700
A/C 0.8 0.7 0.6

Updated 05/03/2024 21:08:57


ECG DB / PANELBOARD SCHEDULE Proj.No 1658
According to IEC & Master Spec REV.(0)
NOTE
PANEL NO.: UP-S-6 LOCATION : 6th Floor Notes: 1,4 1- MCCB' s required 6- Led Dimmer Control 10- ELCB, 100 mA required
7- Contactor and PB
2- Isolated Earth Bus 11- ELCB, 30 mA required
Mains Rating Duty Enclosure Dimensions connected to BMS
Fed From : UP-S-4 Main C.B.: 40 A 380 / 220 V SURFACE W mm 3- 200% neutral size 8- Photocell and Timer 12- Split Bus
Cable No. : F-UP-S-6 << TCL : 13 kW 12.43 kA-symm. IP42 D mm 4- Indicating Lamps 9- Two-Section Panel 13- Shunt trip
Cable size: 1 // ( 4x 50 ) mm2 Max.Dem.: 8.82 kW 25.47 kA-peak Form 2 H mm 5-Connected to BMS via lighting control system 14- Metering
SER NO. CCT C.B. WIRE ECC CONNECTED LOAD - No.of points per circuit unit CONNECTED LOAD
N
O 1P-C.B.'s REF SIZE SIZE No. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 Load PER - PHASE
T
ROOM / AREA / SUB PANEL / LOAD DISCRIP.
OR # TL CL/ HID Sing Twin Pwr 3 ph Mot/ W.B/ wind split VAV- @ R Y B
E
WAYS NO. A mm2 mm2 Ltg Exit Ltg S/O S/O S/O S/O Fan HD EWH H.P A/C A/C FCU kW kW kW kW
11 1 R1 20 4 4 B.H.U . 4 0.20 0.8
11 2 Y1 20 4 4 B.H.U . 4 0.20 0.8
11 3 B1 20 4 4 B.H.U . 4 0.20 0.8
11 4 R2 20 4 4 B.H.U . 4 0.20 0.8
11 5 Y2 20 4 4 B.H.U . 4 0.20 0.8
11 6 B2 20 4 4 B.H.U . 4 0.20 0.8
11 7 R3 20 4 4 B.H.U . 4 0.20 0.8
11 8 Y3 20 4 4 B.H.U . 2 0.20 0.4
11 9 B3 20 4 4 B.H.U . 4 0.20 0.8
10 R4 20 4 4 CAMERAS . 8 0.20 1.6
11 Y4 20 4 4 SOCKET OUTLET . 5 0.20 1.0
12 B4 20 SPARE . 0.20 0.0
13 R5 20 4 4 WIFI 1 0.20 0.2
14 Y5 32 6 6 IT RACK . 1 3.00 3.0
15 B5 20 SPARE . 0.0
16 R6 20 SPARE 0.0
17 Y6 20 SPARE . 0.0
18 B6 SPACE . 0.0
19 R7 0.0
20 Y7 0.0
21 B7 0.0
22 R8 . 0.0
23 Y8 . 0.0
24 B8 . 0.0
Dem. Factor ( DF ) Application SUB - 4.2 6.0 2.4
first 100 Kw next 200 Kw remaining Ltg Power Heating A/C TOTAL 13
Lighting 0.9 0.8 0.7 TCL ( kW ) 0.000 12.60 0.00 0.00 13 kilo-Watts
Power 0.7 0.6 0.5 -------- >> MD ( kW ) 0.00 8.82 0.00 0.00 9
Heating 0.6 0.6 0.55 Result. Dem. Factor #DIV/0! 0.70 #DIV/0! #DIV/0! 0.700
A/C 0.8 0.7 0.6

Updated 05/03/2024 21:08:57


ECG DB / PANELBOARD SCHEDULE Proj.No 1658
According to IEC & Master Spec REV.(0)
NOTE
PANEL NO.: UP-S-7 LOCATION : 7th Floor Notes: 1,4 1- MCCB' s required 6- Led Dimmer Control 10- ELCB, 100 mA required
7- Contactor and PB
2- Isolated Earth Bus 11- ELCB, 30 mA required
Mains SHEET 1 OF 2 Rating Duty Enclosure Dimensions connected to BMS
Fed From : UDB-S Main C.B.: 100 A 380 / 220 V SURFACE W mm 3- 200% neutral size 8- Photocell and Timer 12- Split Bus
Cable No. : F-UP-S-7 << TCL : 36 kW 6.46 kA-symm. IP42 D mm 4- Indicating Lamps 9- Two-Section Panel 13- Shunt trip
Cable size: 1 // ( 4x 70 ) mm2 Max.Dem.: 25.1 kW 13.24 kA-peak Form 2 H mm 5-Connected to BMS via lighting control system 14- Metering
SER NO. CCT C.B. WIRE ECC CONNECTED LOAD - No.of points per circuit unit CONNECTED LOAD
N
O 1P-C.B.'s REF SIZE SIZE No. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 Load PER - PHASE
T
ROOM / AREA / SUB PANEL / LOAD DISCRIP.
OR # TL CL/ HID Sing Twin Pwr 3 ph Mot/ W.B/ wind split VAV- @ R Y B
E
WAYS NO. A mm2 mm2 Ltg Exit Ltg S/O S/O S/O S/O Fan HD EWH H.P A/C A/C FCU kW kW kW kW
11 1 R1 20 4 4 B.H.U . 4 0.20 0.8
11 2 Y1 20 4 4 B.H.U . 4 0.20 0.8
11 3 B1 20 4 4 B.H.U . 4 0.20 0.8
11 4 R2 20 4 4 B.H.U . 4 0.20 0.8
11 5 Y2 20 4 4 B.H.U . 4 0.20 0.8
11 6 B2 20 4 4 B.H.U . 4 0.20 0.8
11 7 R3 20 4 4 B.H.U . 4 0.20 0.8
11 8 Y3 20 4 4 B.H.U . 2 0.20 0.4
11 9 B3 20 4 4 PANEL DEVICE . 4 0.20 0.8
10 R4 20 4 4 CAMERAS . 7 0.10 0.7
11 Y4 20 4 4 SOCKET OUTLET . 3 0.20 0.6
12 B4 20 SPARE . 0.0
13 R5 20 4 4 WI FI 1 0.10 0.1
14 Y5 32 6 6 IT RACK . 1 3.00 3.0
15 B5 . 0.0
16 R6 4.9
17 Y6 40 10 10 UP-S-8 . 1 8.20 2.0
18 B6 . 1.3
19 R7 1.9
20 Y7 40 10 10 UP-S-9 1 8.20 2.0
21 B7 4.3
22 R8 . 1.9
23 Y8 40 25 16 UP-S-10 . 1 8.20 2.0
24 B8 . 4.3
Dem. Factor ( DF ) Application SUB - 11.9 11.6 12.3
first 100 Kw next 200 Kw remaining Ltg Power Heating A/C TOTAL 36
Lighting 0.9 0.8 0.7 TCL ( kW ) 0.000 35.80 0.00 0.00 36 kilo-Watts
Power 0.7 0.6 0.5 -------- >> MD ( kW ) 0.00 25.06 0.00 0.00 25
Heating 0.6 0.6 0.55 Result. Dem. Factor #DIV/0! 0.70 #DIV/0! #DIV/0! 0.700
A/C 0.8 0.7 0.6

Updated 05/03/2024 21:08:57


ECG DB / PANELBOARD SCHEDULE Proj.No 1658
According to IEC & Master Spec REV.(0)
NOTE
PANEL NO.: UP-S-7 LOCATION : 7th Floor Notes: 1,4 1- MCCB' s required 6- Led Dimmer Control 10- ELCB, 100 mA required
7- Contactor and PB
2- Isolated Earth Bus 11- ELCB, 30 mA required
Mains SHEET 2 OF 2 Rating Duty Enclosure Dimensions connected to BMS
Fed From : UDB-S Main C.B.: 100 A 380 / 220 V SURFACE W mm 3- 200% neutral size 8- Photocell and Timer 12- Split Bus
Cable No. : F-UP-S-7 << TCL : 36 kW 6.46 kA-symm. IP42 D mm 4- Indicating Lamps 9- Two-Section Panel 13- Shunt trip
Cable size: 1 // ( 4x 70 ) mm2 Max.Dem.: 25.1 kW 13.24 kA-peak Form 2 H mm 5-Connected to BMS via lighting control system 14- Metering
SER NO. CCT C.B. WIRE ECC CONNECTED LOAD - No.of points per circuit unit CONNECTED LOAD
N
O 1P-C.B.'s REF SIZE SIZE No. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 Load PER - PHASE
T
ROOM / AREA / SUB PANEL / LOAD DISCRIP.
OR # TL CL/ HID Sing Twin Pwr 3 ph Mot/ W.B/ wind split VAV- @ R Y B
E
WAYS NO. A mm2 mm2 Ltg Exit Ltg S/O S/O S/O S/O Fan HD EWH H.P A/C A/C FCU kW kW kW kW
25 R9 20 SPARE .
26 Y9 20 SPARE .
27 B9 20 SPARE .
28 R10 20 .
29 Y10 20 .
30 B10 20 .
31 R11 20 .
32 Y11 20 .
33 B11 20 .
34 R12 20 .
35 Y12 20 .
36 B12 20 .
37 R13 20
38 Y13 20 .
39 B13 20 .
40 R14 20
41 Y14 20 .
42 B14 20 .
43 R15 20
44 Y15 20
45 B15 20
46 R16 20 .
47 Y16 20 .
48 B16 20 .
Dem. Factor ( DF ) Application SUB - 11.9 11.6 12.3
first 100 Kw next 200 Kw remaining Ltg Power Heating A/C TOTAL 36
Lighting 0.9 0.8 0.7 TCL ( kW ) 0.000 35.80 0.00 0.00 36 kilo-Watts
Power 0.7 0.6 0.5 -------- >> MD ( kW ) 0.00 25.06 0.00 0.00 25
Heating 0.6 0.6 0.55 Result. Dem. Factor #DIV/0! 0.70 #DIV/0! #DIV/0! 0.700
A/C 0.8 0.7 0.6

Updated 05/03/2024 21:08:57


ECG DB / PANELBOARD SCHEDULE Proj.No 1658
According to IEC & Master Spec REV.(0)
NOTE
PANEL NO.: UP-S-8 LOCATION : 8th Floor Notes: 1,4 1- MCCB' s required 6- Led Dimmer Control 10- ELCB, 100 mA required
7- Contactor and PB
2- Isolated Earth Bus 11- ELCB, 30 mA required
Mains Rating Duty Enclosure Dimensions connected to BMS
Fed From : UP-S-7 Main C.B.: 40 A 380 / 220 V SURFACE W mm 3- 200% neutral size 8- Photocell and Timer 12- Split Bus
Cable No. : F-UP-S-8 << TCL : 8 kW 7.48 kA-symm. IP42 D mm 4- Indicating Lamps 9- Two-Section Panel 13- Shunt trip
Cable size: 1 // ( 4x 10 ) mm2 Max.Dem.: 5.74 kW 15.34 kA-peak Form 2 H mm 5-Connected to BMS via lighting control system 14- Metering
SER NO. CCT C.B. WIRE ECC CONNECTED LOAD - No.of points per circuit unit CONNECTED LOAD
N
O 1P-C.B.'s REF SIZE SIZE No. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 Load PER - PHASE
T
ROOM / AREA / SUB PANEL / LOAD DISCRIP.
OR # TL CL/ HID Sing Twin Pwr 3 ph Mot/ W.B/ wind split VAV- @ R Y B
E
WAYS NO. A mm2 mm2 Ltg Exit Ltg S/O S/O S/O S/O Fan HD EWH H.P A/C A/C FCU kW kW kW kW
11 1 R1 20 4 4 B.H.U . 2 0.20 0.4
11 2 Y1 20 4 4 B.H.U . 2 0.20 0.4
11 3 B1 20 4 4 B.H.U . 2 0.20 0.4
11 4 R2 20 4 4 B.H.U . 2 0.20 0.4
11 5 Y2 20 4 4 B.H.U . 2 0.20 0.4
11 6 B2 20 4 4 B.H.U . 2 0.20 0.4
11 7 R3 20 4 4 B.H.U . 2 0.20 0.4
11 8 Y3 20 4 4 B.H.U . 1 0.20 0.2
11 9 B3 20 4 4 B.H.U . 2 0.20 0.4
10 R4 20 4 4 CAMERAS . 7 0.10 0.7
11 Y4 20 4 4 SOCKET OUTLET . 5 0.20 1.0
12 B4 20 4 4 WIFI . 1 0.10 0.1
13 R5 32 6 6 IT-RACK 1 3.00 3.0
14 Y5 20 SPARE . 0.0
15 B5 20 SPARE . 0.0
16 R6 20 SPARE 0.0
17 Y6 20 SPARE . 0.0
18 B6 SPACE . 0.0
19 R7 0.0
20 Y7 0.0
21 B7 0.0
22 R8 . 0.0
23 Y8 . 0.0
24 B8 . 0.0
Dem. Factor ( DF ) Application SUB - 4.9 2.0 1.3
first 100 Kw next 200 Kw remaining Ltg Power Heating A/C TOTAL 8
Lighting 0.9 0.8 0.7 TCL ( kW ) 0.000 8.20 0.00 0.00 8 kilo-Watts
Power 0.7 0.6 0.5 -------- >> MD ( kW ) 0.00 5.74 0.00 0.00 6
Heating 0.6 0.6 0.55 Result. Dem. Factor #DIV/0! 0.70 #DIV/0! #DIV/0! 0.700
A/C 0.8 0.7 0.6

Updated 05/03/2024 21:08:57


ECG DB / PANELBOARD SCHEDULE Proj.No 1658
According to IEC & Master Spec REV.(0)
NOTE
PANEL NO.: UP-S-9 LOCATION : 9th Floor Notes: 1,4 1- MCCB' s required 6- Led Dimmer Control 10- ELCB, 100 mA required
7- Contactor and PB
2- Isolated Earth Bus 11- ELCB, 30 mA required
Mains Rating Duty Enclosure Dimensions connected to BMS
Fed From : UP-S-7 Main C.B.: 40 A 380 / 220 V SURFACE W mm 3- 200% neutral size 8- Photocell and Timer 12- Split Bus
Cable No. : F-UP-S-9 << TCL : 8 kW 7.66 kA-symm. IP42 D mm 4- Indicating Lamps 9- Two-Section Panel 13- Shunt trip
Cable size: 1 // ( 4x 16 ) mm2 Max.Dem.: 5.74 kW 15.71 kA-peak Form 2 H mm 5-Connected to BMS via lighting control system 14- Metering
SER NO. CCT C.B. WIRE ECC CONNECTED LOAD - No.of points per circuit unit CONNECTED LOAD
N
O 1P-C.B.'s REF SIZE SIZE No. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 Load PER - PHASE
T
ROOM / AREA / SUB PANEL / LOAD DISCRIP.
OR # TL CL/ HID Sing Twin Pwr 3 ph Mot/ W.B/ wind split VAV- @ R Y B
E
WAYS NO. A mm2 mm2 Ltg Exit Ltg S/O S/O S/O S/O Fan HD EWH H.P A/C A/C FCU kW kW kW kW
11 1 R1 20 4 4 B.H.U . 2 0.20 0.4
11 2 Y1 20 4 4 B.H.U . 2 0.20 0.4
11 3 B1 20 4 4 B.H.U . 2 0.20 0.4
11 4 R2 20 4 4 B.H.U . 2 0.20 0.4
11 5 Y2 20 4 4 B.H.U . 2 0.20 0.4
11 6 B2 20 4 4 B.H.U . 2 0.20 0.4
11 7 R3 20 4 4 B.H.U . 2 0.20 0.4
11 8 Y3 20 4 4 B.H.U . 1 0.20 0.2
11 9 B3 20 4 4 B.H.U . 2 0.20 0.4
10 R4 20 4 4 CAMERAS . 7 0.10 0.7
11 Y4 20 4 4 SOCKET OUTLET . 5 0.20 1.0
12 B4 20 4 4 WIFI . 1 0.10 0.1
13 R5 20 SPARE 0.0
14 Y5 20 SPARE . 0.0
15 B5 32 6 6 IT-RACK . 1 3.00 3.0
16 R6 20 SPARE 0.0
17 Y6 20 SPARE . 0.0
18 B6 SPACE . 0.0
19 R7 0.0
20 Y7 0.0
21 B7 0.0
22 R8 . 0.0
23 Y8 . 0.0
24 B8 . 0.0
Dem. Factor ( DF ) Application SUB - 1.9 2.0 4.3
first 100 Kw next 200 Kw remaining Ltg Power Heating A/C TOTAL 8
Lighting 0.9 0.8 0.7 TCL ( kW ) 0.000 8.20 0.00 0.00 8 kilo-Watts
Power 0.7 0.6 0.5 -------- >> MD ( kW ) 0.00 5.74 0.00 0.00 6
Heating 0.6 0.6 0.55 Result. Dem. Factor #DIV/0! 0.70 #DIV/0! #DIV/0! 0.700
A/C 0.8 0.7 0.6

Updated 05/03/2024 21:08:57


ECG DB / PANELBOARD SCHEDULE Proj.No 1658
According to IEC & Master Spec REV.(0)
NOTE
PANEL NO.: UP-S-10 LOCATION : 10th Floor Notes: 1,4 1- MCCB' s required 6- Led Dimmer Control 10- ELCB, 100 mA required
7- Contactor and PB
2- Isolated Earth Bus 11- ELCB, 30 mA required
Mains Rating Duty Enclosure Dimensions connected to BMS
Fed From : UP-S-7 Main C.B.: 40 A 380 / 220 V SURFACE W mm 3- 200% neutral size 8- Photocell and Timer 12- Split Bus
Cable No. : F-UP-S-10 << TCL : 8 kW 8.37 kA-symm. IP42 D mm 4- Indicating Lamps 9- Two-Section Panel 13- Shunt trip
Cable size: 1 // ( 4x 25 ) mm2 Max.Dem.: 5.74 kW 17.17 kA-peak Form 2 H mm 5-Connected to BMS via lighting control system 14- Metering
SER NO. CCT C.B. WIRE ECC CONNECTED LOAD - No.of points per circuit unit CONNECTED LOAD
N
O 1P-C.B.'s REF SIZE SIZE No. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 Load PER - PHASE
T
ROOM / AREA / SUB PANEL / LOAD DISCRIP.
OR # TL CL/ HID Sing Twin Pwr 3 ph Mot/ W.B/ wind split VAV- @ R Y B
E
WAYS NO. A mm2 mm2 Ltg Exit Ltg S/O S/O S/O S/O Fan HD EWH H.P A/C A/C FCU kW kW kW kW
11 1 R1 20 4 4 B.H.U . 2 0.20 0.4
11 2 Y1 20 4 4 B.H.U . 2 0.20 0.4
11 3 B1 20 4 4 B.H.U . 2 0.20 0.4
11 4 R2 20 4 4 B.H.U . 2 0.20 0.4
11 5 Y2 20 4 4 B.H.U . 2 0.20 0.4
11 6 B2 20 4 4 B.H.U . 2 0.20 0.4
11 7 R3 20 4 4 B.H.U . 2 0.20 0.4
11 8 Y3 20 4 4 B.H.U . 1 0.20 0.2
11 9 B3 20 4 4 B.H.U . 2 0.20 0.4
10 R4 20 4 4 CAMERAS . 7 0.10 0.7
11 Y4 20 4 4 SOCKET OUTLET . 5 0.20 1.0
12 B4 20 4 4 WIFI . 1 0.10 0.1
13 R5 20 SPARE 0.0
14 Y5 20 SPARE . 0.0
15 B5 32 6 6 IT-RACK . 1 3.00 3.0
16 R6 20 SPARE 0.0
17 Y6 20 SPARE . 0.0
18 B6 SPACE . 0.0
19 R7 0.0
20 Y7 0.0
21 B7 0.0
22 R8 . 0.0
23 Y8 . 0.0
24 B8 . 0.0
Dem. Factor ( DF ) Application SUB - 1.9 2.0 4.3
first 100 Kw next 200 Kw remaining Ltg Power Heating A/C TOTAL 8
Lighting 0.9 0.8 0.7 TCL ( kW ) 0.000 8.20 0.00 0.00 8 kilo-Watts
Power 0.7 0.6 0.5 -------- >> MD ( kW ) 0.00 5.74 0.00 0.00 6
Heating 0.6 0.6 0.55 Result. Dem. Factor #DIV/0! 0.70 #DIV/0! #DIV/0! 0.700
A/C 0.8 0.7 0.6