In valthur Gas Turbine power station has V 64.3A model ansaldo make GT. It has been tripped on surge protection tripping in many times due to grid
frequencies variation from 50Hz to 49.2Hz. When grid frequency reduced from 49.65Hz to 49.2Hz, the load more than 52MW, the GT got tripped on surge
protection.

As per logic If UP stm compressor of the DP switches 2 out of 3 below set value of 23mbar reached and GT speed above 4560, the GT got tripped on surge
protection tripped occurred. Instrumentation side the following remedial measure has been taken. The above DP switches calibrated and their impulse line
piping cleaned through instrument air, IGV calibrated and mechanical angle, bearing checked and found normal. But suction of the Up steam compr. DP
transmitter value GT running 11.5mbar and compr discharge pr has been reads 1.5 bar. No variation at the time of surge protection tripping. Recently year
2014 6 times tripping has been occurred at the time anti impulsion door cannot opened as per trend shown.

pl explain and trouble shooting procedure and permanent remedial measuring report for avoiding of the above nonsense trip pl.

Report  Like  Reply

CSA #2
Jul 31, 2014

any author,

The first question is:

What does the OEM (Original Equipment Manufacturer: Ansaldo) say about the problem?

The second question is:

Has the OEM made any recommendations or suggestions (other that what you've described)?

The third question is:

Have you implemented any of the OEM's recommendations or suggestions?

The fourth question is:

Have the frequency excursions worsened in the last year or so, either the magnitude of the excursions or the period of the excursions increased? (In other
words, are the low frequency dips more pronounced than in the period prior to the last six or eight months? Is the rate at which the frequency changes (the
"frequency" of the frequency variations) more than in the last six or eight months?

I'm going to guess the OEM is using these sensors and the additional data (including turbine shaft speed) to protect the axial compressor from a stall/surge
condition, which is pretty common for many larger heavy duty gas turbines (protecting against stall/surge conditions which can seriously damage the unit).

Unfortunately, you are most likely going to have to present hard actionable data (graphs; recordings; archival data) of the frequency excursions and the
changes in sensor input the control system is experiencing during these events to the OEM and ask for their help and assistance. They are the ones who would
have the most insight into what the axial compressor is capable of withstanding at or near rated speed, or when the frequency is unstable and less than rated.
They may make changes to parameters, or even to the way in which the sensor data is filtered or used during frequency excursion such as you are
experiencing.

If you believe all of the instrumentation is working correctly, and that sensing/impulse lines are clean and free of obstructions, and that operating parameters
in the Control System are properly set per OEM recommendations, then you are going to have to get the OEM involved in helping to resolve the problem.

I will add just one more thing. I have frequently seen "re-"calibrations of instruments result in even more problems. And, I'm specifically referring to so-called
"SMART" sensors which have been "re-calibrated" soon after commissioning. Often, instrument technicians "erase" all settings in these instruments when re-
calibrating them, including any filters which might have been enabled and set by commissioning personnel causing the instrumentation to be even more
sensitive than previously--even though the setpoints didn't change at all. In the old days, we used to use needle valves in the sensing/impulse lines and would
"throttle" slightly with these valves to smooth the changes which the sensors were monitoring. New-fangled SMART sensors have filtering/smoothing
capabilities built-in.

However, many of the new SMART sensors are rather slow to begin with (response time to "stimuli") so there is some inherent filtering/smoothing just due to
the speed of response.

Again, your best course of action would be to work with the OEM to a resolution. They may have empirical data from other units which can help in the
"relaxation" of the surge control parameters, or they have already dealt with this at another site (or sites) and may have a work-around or solution.

Please write back to let us know how you fare in the resolution of this issue.

Report  Like  Reply

any author #3

A Aug 1, 2014

> The first question is:


> What does the OEM (Original Equipment Manufacturer: Ansaldo) say about the problem?

Air intake filter replaced by OEM filter

>The second question is:


> Has the OEM made any recommendations or suggestions (other that what you've described)?
No

> The third question is:


> Have you implemented any of the OEM's recommendations or suggestions?
No

> The fourth question is:


> Have the frequency excursions worsened in the last year or so, either the
> magnitude of the excursions or the period of the excursions increased? In
> other words, are the low frequency dips more pronounced than in the period prior
> to the last six or eight months? Is the rate at which the frequency changes (the
> "frequency" of the frequency variations) more than in the last six or eight months?
49.97 to 49.02Hz

Report  Like  Reply

                  

Write your reply...

Attach files Post reply Preview

Similar threads Forum Replies Date

T Surge Protection for Axial Compressor Power Generation 1 Dec 27, 2016

B Mark V 125vdc Surge Protection Power Generation 5 Feb 27, 2013

S Gas turbine Surge protection during Grid frequency changes Power Generation 3 Apr 23, 2012

D Current loop surge protection General Communications Chat 0 Dec 27, 2007

G Compressor Surge Protection Process Control 7 Jun 29, 2004

Y O U M AY ALSO L IK E

How to De ne the Tool Introduction to Add-On Red Lion’s Flexedge An Overview of Industrial
Center Point (TCP) on a Instructions Automation Platform Now Level Sensors
Robot Integrates IT & OT
by Damond Goodwin by Dennis Lynch by Alessandro Mascellino by Damond Goodwin

WHO WE ARE PRODUCTS INDUSTRY CONTENT

Circuit Protection Agriculture Company Directory

Connectors Automotive Forums

Control Panel Building Industry White Papers

Control Systems & HMIs Cement News


More about us 
Enclosures, Racks & Cabinets Chemical Technical Articles

IIoT Electronics Textbook

Industrial Controls Food & Beverage Worksheets

CONNECT WITH US Motors Metal

Networking Military/Aerospace

    PLCs & PACs Mining

Pneumatics & Hydraulics Nuclear

Power Oil & Gas

Contact Us Advertise Protocols Medical & Pharmaceutical

Robotics Pulp & Paper


Write For Us Safety Rubber & Plastics

Sensors Utilities

Simulation View All

Test & Measurement


SIGN UP
Vision Systems

Wire & Cable


Enter your email address Register
View All

MORE FROM OUR NETWORK

    

© EETech Media, LLC. All rights reserved Privacy Policy · User Agreement

You might also like